I know this has been dicussed on this board before, if you can direct me to the thread or give a quick answer it would be appreciated.
What are the requirements on a sump being on a GFCI? Would or could the sump trip the GFCI? Thanks |
|
#2
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
There is no exception for sump pumps in unfinished basements and crawl spaces as far as GFI protection goes. See 210.8(A)(4)&(5)
That said most inspectors are lenient as far as sump pumps are concerned if intent is shown. IE: Single receptacles, etc. Yes, any motor load can cause a nuisance trip. With most newer motors and GFIs this is less of an issue. |
|
#3
|
||||
|
||||
|
Well said......could not have added anything too Peter's statement...Most Excellent.
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
![]() |