Default GFCI tester question

Today I completed an inspection and when plugging the gfci tester into a 3 prong outlet all three lights were lit? The center light was the brightest, and the outer lights were glowing noticably. There is not code on the tester explaining what the hell this means, reverse polarity, open ground and open nuetral? Has anyone ever seen this? George
Reply With Quote
Find an InterNACHI certified Oklahoma Home Inspector (and anywhere else in North America)
  #2  
Old 6/3/09, 8:40 AM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: Scottville, Mi
Posts: 930
Default Re: GFCI tester question

Testers vary from model to model. If I came across this, I would have gotten out my testing meter, possibly something funky with the voltage?
Reply With Quote
  #3  
Old 6/3/09, 10:16 AM
Mark A. Timpani's Avatar
Mark A. Timpani Mark A. Timpani is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 1,613
Default Re: GFCI tester question

I have seen this in Tucson also. Don't know the answer.




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #4  
Old 6/3/09, 1:08 PM
Mark Thorman Mark Thorman is offline
Active Poster
 
Join Date: Mar 2008
Posts: 166
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI tester question

I found this once. Someone removed the 240v outlet for an a/c and installed a 120v rated outlet but still wired it 240v.

www.MauiHomeInspections.com
Reply With Quote
  #5  
Old 6/3/09, 2:47 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI tester question

Thats why it pays to carry a standard voltage tester and multi meter.
Reply With Quote
  #6  
Old 6/3/09, 5:45 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,219
Default Re: GFCI tester question

The only way to get all 3 lights to light is with voltage on the neutral.

Could be 120V from neutral to ground and 240V from neutral to hot.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207
Reply With Quote
  #7  
Old 6/3/09, 5:56 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: GFCI tester question

Quote:
Originally Posted by bking View Post
The only way to get all 3 lights to light is with voltage on the neutral.

Could be 120V from neutral to ground and 240V from neutral to hot.
That's what I've found, too.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #8  
Old 6/3/09, 5:58 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: GFCI tester question

Whatever it is, it's not right.
Reply With Quote
  #9  
Old 6/3/09, 6:52 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Broadview Hts., OH
Posts: 1,465
Default Re: GFCI tester question

Brings back memories of a recent inspection.

Open ground, Open ground, Reverse polarity, Reverse Polarity, False Ground,

BBBBBBZZZZZZZTTTTTT. Dead Ideal Sure Tester. Glad they stand behind there warranties.
Reply With Quote
  #10  
Old 6/3/09, 7:57 PM
William Thacker's Avatar
William Thacker William Thacker is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Pennsylvania
Posts: 354
Default Re: GFCI tester question

was it on a dimmer? I have seen this before. I plug in a lamp if there is one available and see if the outlet behaves as expected. It does not take much to get that condition and the neutral is supposed to carry current back to the panel. If no dimmer, a poor neutral connection may exhibit unusual indications.

Last edited by wthacker; 6/3/09 at 8:08 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Inspection Pointers Here jtedesco1 Electrical 3 3/15/08 10:19 AM
Installing GFCI in garage with no ground cyezza Electrical 53 11/30/07 6:05 PM
GFCI Safety Notice rcooke Electrical 1 10/30/07 1:29 PM
GFCI Question jvogan Electrical 4 8/25/07 3:28 PM
Adequate service size....oh, and a GFCI question ksherstobetoff Electrical 13 2/8/07 2:18 PM


All times are GMT -4. The time now is 8:43 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts