Default GFCI Testers

I did an inspection yesterday on a home with Arc Fault Circuit breakers installed on the bedroom circuits. I don't do many newer homes working mostly in Boston, so I don't usually run into them but my GFCI tester tripped the Arc Fault Circuit breaker. I don't remember having this happen in the past. Is a GFCI circuit tester supposed to trip the Arc Fault Circuit Breaker. Thanks
John
Reply With Quote
  #2  
Old 4/13/08, 12:25 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Testers

Arc Fault breakers also have a GFI component. They trip under a ground fault of 30 milliamperes and over. The regular GFCI's that protect people (like around sinks and such) trip at 5 milliamperes.

A couple things might have happened in your case:
  • Your GFCI tester is simulating a short of much greater than 5 milliamperes, and needs replaced
  • The AFCI breaker is too sensitive
  • A ground fault of a magnitude less than 30 milliamperes presently exists on the circuit, and the extra 6 or 8 milliamperes you added with your tester brought it over the 30 milliamp threshold that it took to trip the AFCI.

In my experience, the last option in my list is the likely culprit. I really don't know how to advise you on how or what to write about this in your report. One of your other home inspector colleagues probably has a good idea.
Reply With Quote
  #3  
Old 4/13/08, 12:33 PM
GARY L. RUSK GARY L. RUSK is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: FT. JENNINGS, OH
Posts: 189
Default Re: GFCI Testers

It was probably a combination AFCI / GFCI breaker.



Gary
Reply With Quote
  #4  
Old 4/13/08, 12:43 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,842
Default Re: GFCI Testers

If the AFCI responded properly to it's test button and no other "defect" was noted I would note what occurred while "other GFCI testing" was being performed and have evaluated by electrician.
Once occupied by your client and the circuit is loaded, nuisance tripping may occur that was not disclosed and guess who they'll want to pay for the "defect"

This is what I'm using when AFCI is not present, maybe some part may help you or your client

Safety enhancement upgrade: Arc Fault Circuit Interrupter (AFCI) is now required, depending on local adoption of these new standards. All 120-volt, single phase, 15-20-ampere branch circuits supplying outlets installed in a dwelling unit family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sun rooms, hallways, recreation rooms, closets, similar rooms or areas shall be protected by a listed arc fault interrupter combination-type, installed to provide protection of the branch circuit.



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #5  
Old 4/13/08, 12:59 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Testers

Quote:
Originally Posted by grusk
It was probably a combination AFCI / GFCI breaker.
That's one I hadn't considered, but while they certainly exist, it would be pretty rare to run into one in the field. Certainly possible, but rare. Of course, we're dealing with sort of a rare situation here (GFCI tester tripping an AFCI), so who knows? Not really something a home inspector rightfully needs to sort out. I wouldn't want to automatically assume that he was dealing with the combination AFCI/GFCI breaker and dismiss the issue, only to have it be a genuine problem.
Reply With Quote
  #6  
Old 4/13/08, 1:05 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Testers

I think C/H has the AFCI/GFCI
Reply With Quote
  #7  
Old 4/13/08, 1:35 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: GFCI Testers

If you were using a SureTest, you would know exactly how may mA were applied to the circuit, and for what duration.

The standard three-light testers are pretty useless for any type of circuit analysis.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 4/13/08, 1:46 PM
Justin Watts Justin Watts is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Rancho Santa Margarita, CA
Posts: 771
Default Re: GFCI Testers

AFCI question.............

I have been recommending AFCI upgrades for bedroom circuits, do you guys recommend them now per the 2005 NEC for all ROOMS. (other than GFCI locations)

I am sure Realtors love this recommendation.... since AFCI's are fairly a new requirement. I get questions just for the bedroom recommendations...

Do you recommend all Circuits????? I am sure I will start...
Let me know.
Reply With Quote
  #9  
Old 4/13/08, 1:49 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Testers

Quote:
Originally Posted by jwatts1
AFCI question.............

I have been recommending AFCI upgrades for bedroom circuits, do you guys recommend them now per the 2005 NEC for all ROOMS. (other than GFCI locations)

I am sure Realtors love this recommendation.... since AFCI's are fairly a new requirement. I get questions just for the bedroom recommendations...

Do you recommend all Circuits????? I am sure I will start...
Let me know.
That's actually a brand-new 2008 requirement. Speaking as an electrician, yes!, please recommend that they be added to all 120 volt circuits.
Reply With Quote
  #10  
Old 4/13/08, 2:30 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Testers

Quote:
Originally Posted by Greg Fretwell
I think C/H has the AFCI/GFCI
They do, but as Marc said, they are extremely rare.

Too many folks are under the misconception that the new "combination" AFCIs are combination AFCI/GFCI, when in fact they are NOT. They are simply combination AFCI breakers.
Reply With Quote
  #11  
Old 4/14/08, 12:25 AM
Bruce Erny Bruce Erny is offline
New User
 
Join Date: Apr 2008
Location: SW Florida
Posts: 18
Please Note: Bruce Erny is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Testers

Quote:
Originally Posted by jwatts1
AFCI question.............

I have been recommending AFCI upgrades for bedroom circuits, do you guys recommend them now per the 2005 NEC for all ROOMS. (other than GFCI locations)

I am sure Realtors love this recommendation.... since AFCI's are fairly a new requirement. I get questions just for the bedroom recommendations...

Do you recommend all Circuits????? I am sure I will start...
Let me know.
You can open up a can of worms doing that. If the bedroom is wired on mwbc the afc breaker will not work and the homeowner will think he has an electric wiring problem when he does not.
Reply With Quote
  #12  
Old 4/14/08, 12:35 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Testers

Quote:
Originally Posted by Bruce Erny
If the bedroom is wired on mwbc the afc breaker will not work and the homeowner will think he has an electric wiring problem when he does not.
WHAT???????

If the circuit is a MWBC, the ONLY way it would work with an AFCI is if it is a two-pole breaker.
A MWBC would not work at all if two SP AFCIs were used.
Reply With Quote
  #13  
Old 4/14/08, 12:58 AM
Bruce Erny Bruce Erny is offline
New User
 
Join Date: Apr 2008
Location: SW Florida
Posts: 18
Please Note: Bruce Erny is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Testers

Quote:
Originally Posted by Greg Fretwell
I think C/H has the AFCI/GFCI
That would be GE with the white rocker switches. One side GFC one side AFC

Last edited by Bruce Erny; 4/14/08 at 1:27 AM..
Reply With Quote
  #14  
Old 4/14/08, 3:05 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Testers

Quote:
Originally Posted by Bruce Erny
That would be GE with the white rocker switches. One side GFC one side AFC
I highly suggest you cease giving out electrical advise of any sort.
Reply With Quote
  #15  
Old 4/14/08, 10:50 AM
Bruce Erny Bruce Erny is offline
New User
 
Join Date: Apr 2008
Location: SW Florida
Posts: 18
Please Note: Bruce Erny is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI Testers

Quote:
Originally Posted by Marc D. Shunk
I highly suggest you cease giving out electrical advise of any sort.
Marc, If you will please read my post again, I think you will see I did not give any electric advice. I very simply stated that what he saw MAY have been the GE AFCI breaker that has the white rocker test switch on it. If you look close, you will see that on one side of the switch it says AFCI on the other side it says GFCI. I gave no advice to use the device or made any statement of it effectiveness.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 2 1/8/11 8:04 PM
More GFCI info from U/L Greg Fretwell Electrical Inspections 9 12/4/07 9:33 PM
GFCI Safety Notice rcooke Electrical Inspections 1 10/30/07 1:29 PM
The question asked on the new HI Study test here? jtedesco1 Electrical Inspections 28 10/4/06 10:31 AM
UL Information about Testing of GFCIs jtedesco1 Electrical Inspections 0 2/5/06 5:38 PM


All times are GMT -4. The time now is 3:07 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts