Default Re: GFCI tripping

Quote:
Originally Posted by kshepard
So how did you finally write it up, Will?
1) There was only one regular receptacle downstream of the two GFCIs in the kitchen. This was a one bedroom condo in a 59 unit apartment condo conversion building.

2) "GFCI protected receptacles in bathroom and over counter in kitchen tripped upon insertion the a simple tester unit. This is most likely cause by defective GFCI receptacles, use of defective GFCI receptacles or improper installation. It should be noted that there are various signs of less-than-professional electrical work in the subject unit, including improperly secured receptacles, broken receptacles and sloppy wiring in the distribution panel.

Recommend evaluation by an independent licensed and insured electrical contractor and obtaining written documentation of the evaluation (on letterhead, with license number and insurance certification) before the close of escrow."

Hope this helps.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #17  
Old 12/29/06, 10:38 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: GFCI tripping

Bump....



Paul W. Abernathy
Reply With Quote
  #18  
Old 12/29/06, 6:16 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI tripping

If your "traffic light" tester was left in the truck and was able to draw damp, it may have enough leakage between conductors to nuisance trip some of the more sensitive models of GFCI's. At one point in time, AMP made this style of tester that was totally potted to avoid that issue. I have found, over time, that some GFCI's are just more sensitive and prone to nuisance trip. The 'Eagle' brand, in particular. At one point in time, Slater made a GFCI tester that you could "dial in" the amount of test leakage and see exactly at what point the GFCI trips. It also had a feed-though feature to plug in a suspected leaky appliance (such as your tester) to read the leakage current. If I remember, I'll try to post a picture of that meter one day.
Reply With Quote
  #19  
Old 12/29/06, 8:09 PM
bandag bandag is offline
Active Poster
 
Join Date: Sep 2006
Posts: 137
Please Note: bandag is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI tripping

Maybe it would be a good idea to carry a small electrical appliance with you like an electric drill or a mixer just as a additional way to check this problem.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
Inspection Pointers Here jtedesco1 Electrical Inspections 3 3/15/08 9:19 AM
GFCI Safety Notice rcooke Electrical Inspections 1 10/30/07 12:29 PM
The question asked on the new HI Study test here? jtedesco1 Electrical Inspections 28 10/4/06 9:31 AM
UL Information about Testing of GFCIs jtedesco1 Electrical Inspections 0 2/5/06 4:38 PM