Default GFCI under Kitchen Sink????

Should the outlet under the kitchen sink be a GFCI? From what I understand all outlets within 6' of water should be GFCI protected.
Attached Thumbnails
gfci-under-kitchen-sink-dscf3183.jpg  
Reply With Quote
Find an InterNACHI certified Washington Home Inspector (and anywhere else in North America)
  #2  
Old 6/21/09, 8:35 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by acassady View Post
Should the outlet under the kitchen sink be a GFCI? From what I understand all outlets within 6' of water should be GFCI protected.
It is not required by code as the outlet does not serve the counter top.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #3  
Old 6/21/09, 8:55 PM
Anthony A. Cassady's Avatar
Anthony A. Cassady Anthony A. Cassady is offline
InterNACHI Member
 
Join Date: Feb 2009
Location: Waynesville, MO
Posts: 118
Default Re: GFCI under Kitchen Sink????

What about the outlets in the laundry room do they need to be GFCI?
Reply With Quote
  #4  
Old 6/21/09, 8:58 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by acassady View Post
What about the outlets in the laundry room do they need to be GFCI?
Only the outlets within 6 feet of the sink (if equipped).

If they supply the washer, they do not need to be GFCI'ed.
Reply With Quote
  #5  
Old 6/21/09, 9:12 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,374
Default Re: GFCI under Kitchen Sink????

No, but could someone fire the Carpenter that butchered that cabinet around that outlet.




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #6  
Old 6/21/09, 9:19 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by mcyr View Post
No, but could someone fire the Carpenter that butchered that cabinet around that outlet.

If they did that, then 85% of the Carpenters wouldn't be working.

This is a typical mess for a kitchen cabinet.
Reply With Quote
  #7  
Old 6/21/09, 9:32 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,374
Default Re: GFCI under Kitchen Sink????

You got a point there David.




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #8  
Old 6/21/09, 9:47 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by dvalley View Post
Only the outlets within 6 feet of the sink (if equipped).

If they supply the washer, they do not need to be GFCI'ed.
Remember now......if the washer receptacle is within 6' of the edge of the sink. It would indeed require the receptacle to be GFCI protected. Nothing in the NEC would allow the washer receptacle IF in that 6' area to not be GFCI protected.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #9  
Old 6/21/09, 9:49 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,744
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by pabernathy View Post
Remember now......if the washer receptacle is within 6' of the edge of the sink. It would indeed require the receptacle to be GFCI protected. Nothing in the NEC would allow the washer receptacle IF in that 6' area to not be GFCI protected.

Even a dedicated cicuit?



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #10  
Old 6/21/09, 9:49 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by pabernathy View Post
Remember now......if the washer receptacle is within 6' of the edge of the sink. It would indeed require the receptacle to be GFCI protected. Nothing in the NEC would allow the washer receptacle IF in that 6' area to not be GFCI protected.

Good point...
Reply With Quote
  #11  
Old 6/21/09, 9:51 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,374
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by pabernathy View Post
Remember now......if the washer receptacle is within 6' of the edge of the sink. It would indeed require the receptacle to be GFCI protected. Nothing in the NEC would allow the washer receptacle IF in that 6' area to not be GFCI protected.

Paul, can you elaborate on what that means?




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
  #12  
Old 6/21/09, 9:53 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by mcyr View Post
Paul, can you elaborate on what that means?
He's stating that if the washer is plugged into an outlet and this outlet is within 6 feet of a sink, it should be GFCI'ed

I don't really make a big deal out of this situation.
Reply With Quote
  #13  
Old 6/21/09, 10:04 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,374
Default Re: GFCI under Kitchen Sink????

Most dishwashers I see share the same receptacle under the counter cabinet with the pig, that is what is confusing, it is within 6' of the sink.




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
Find an InterNACHI certified Washington Home Inspector (and anywhere else in North America)
  #14  
Old 6/21/09, 10:09 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by mcyr View Post
Most dishwashers I see share the same receptacle under the counter cabinet with the pig, that is what is confusing, it is within 6' of the sink.
Ya, but a homeowner would more likely plug into an outlet behind a washer (at a convenient stomach height) verses an outlet located in a lower cabinet where they have to crawl into to get access to the concealed outlet.
Reply With Quote
  #15  
Old 6/22/09, 9:18 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by lkage View Post
Even a dedicated cicuit?

Yes......makes no difference.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Composite granite kitchen sink ... good choice? Bill Featherstone Plumbing 6 1/9/08 12:03 AM
More GFCI info from U/L Greg Fretwell Electrical 9 12/4/07 9:33 PM
Outlet under kitchen sink adooley Electrical 3 2/13/07 3:50 PM
venting the kitchen sink kblair1 Plumbing 57 12/8/06 4:37 PM
No GFCI in Kitchen rnewland Electrical 6 9/19/06 8:51 AM


All times are GMT -4. The time now is 1:59 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts