Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by relliott View Post
Thats why I always start phrases in my reports with the words recommend and suggest.

I make exceptions only for State code on smoke and carbon monoxide detectors which requires them with in 15 feet of bedrooms in my area though I use that only to declare that I recommend them in bedrooms.

AHJ's do not like competition they say.
That's actually State Law for CO and smoke alarms.

Last edited by rmaday; 6/24/09 at 10:20 AM..
Reply With Quote
Find an InterNACHI certified Montana Home Inspector (and anywhere else in North America)
  #32  
Old 6/24/09, 10:20 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by rmaday View Post
That's actually State Law fot CO alarms. Not sure if the smokes are written into law.
Smoke was first with Co added 2006 Jan 1st.

My point was that it is clear cut.(on smoke,though notice the slight loophole with Co)

Safety is always big.

Section 20. Exemptions. The following residential units shall not require carbon monoxide detectors:
(1) A residential unit in a building that: (i) does not rely on combustion of fossil fuel for heat, ventilation, or hot water; (ii) is not connected in any way to a garage; and (iii) is not sufficiently close to any ventilated source of carbon monoxide, as determined by the local building commissioner, to receive carbon monoxide from that source.
Reply With Quote
  #33  
Old 6/24/09, 10:22 AM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by relliott View Post
Smoke was first with Co added 2006 Jan 1st.

Section 20. Exemptions. The following residential units shall not require carbon monoxide detectors:
(1) A residential unit in a building that: (i) does not rely on combustion of fossil fuel for heat, ventilation, or hot water; (ii) is not connected in any way to a garage; and (iii) is not sufficiently close to any ventilated source of carbon monoxide, as determined by the local building commissioner, to receive carbon monoxide from that source.
Yeah, edited my previous post.

http://www.state.il.us/osfm/News/Smo...SavesLives.pdf
Reply With Quote
  #34  
Old 6/24/09, 10:22 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by relliott View Post
Why must you draw a line?

It is all opinion ,and that is his.
I asked the question because the claim was made to recommend installation of a GFCI for safety.

We all could recommend improvements for safeties sake but where do you stop?

Yes, it is an opinion and we all have them.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #35  
Old 6/24/09, 10:24 AM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by relliott View Post
.

My point was that it is clear cut.(on smoke,though notice the slight loophole with Co)

Safety is always big.
Agreed.

My point is Law and code are two different standards.
Reply With Quote
  #36  
Old 6/24/09, 10:25 AM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by mlarson View Post
I asked the question because the claim was made to recommend installation of a GFCI for safety.

We all could recommend improvements for safeties sake but where do you stop?

Yes, it is an opinion and we all have them.
GFCI on all receptacles, then. They all have the potential for electrocution.
Reply With Quote
  #37  
Old 6/24/09, 10:26 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,488
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by mlarson View Post
So do 3-wire electrical systems Jim.

Where do you draw the line?

Do you also recommend upgrading 2-wire electrical systems for safety reasons?
No, I do not recommend replacing a perfectly operating 2-wire system that is not defective....with a 3-wire system that is not defective. That is silly.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.

Reply With Quote
  #38  
Old 6/24/09, 10:28 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by jbushart View Post
No, I do not recommend replacing a perfectly operating 2-wire system that is not defective....with a 3-wire system that is not defective. That is silly.
And IMHO about as silly as recommending a GFCI under the sink.

It just seems inconsistent to me.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #39  
Old 6/24/09, 10:28 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI under Kitchen Sink????

As far as a 2 wire home goes that might seem ok to you ,but not around here .

Yeah ,Yeah you can run dedicated circuits to computers etc and that's just what everyone in today's modern society wants.(right)

Being forced to have things in one location

Recommend upgrade.
If I do not the next Inspector will when they are selling.
Reply With Quote
  #40  
Old 6/24/09, 10:31 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,488
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by mlarson View Post
And IMHO about as silly as recommending a GFCI under the sink.

It just seems inconsistent to me.
Not inconsistent at all. GFCI's are as effective with 2-wire systems and are much less expensive to replace.

I recognize no danger in a non-defective 2-wire electrical system. Neither does the NEC.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.

Reply With Quote
  #41  
Old 6/24/09, 10:35 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by jbushart View Post
Not inconsistent at all. GFCI's are as effective with 2-wire systems and are much less expensive to replace.
Separate issue.
Where do yo draw the line on cost before recommending safety upgrades?

Quote:
Originally Posted by jbushart View Post
I recognize no danger in a non-defective 2-wire electrical system. Neither does the NEC.
They also see no danger in an outlet under the sink without a GFCI.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #42  
Old 6/24/09, 10:38 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,488
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by mlarson View Post
Separate issue.
Where do yo draw the line on cost before recommending safety upgrades?

They also see no danger in an outlet under the sink without a GFCI.

I see a potential danger in an under-the-sink outlet, and recommend accordingly.

I see no potential danger in a perfectly operating 2-wire electrical system.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.

Reply With Quote
  #43  
Old 6/24/09, 10:40 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by jbushart View Post
I see a potential danger in an under-the-sink outlet, and recommend accordingly.

I see no potential danger in a perfectly operating 2-wire electrical system.
If there is no danger in perfectly operating 2-wire system, why are they not permitted in hospitals.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
Find an InterNACHI certified Montana Home Inspector (and anywhere else in North America)
  #44  
Old 6/24/09, 10:43 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,488
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by mlarson View Post
If there is no danger in perfectly operating 2-wire system, why are they not permitted in hospitals.
Certainly you are not suggesting that the building requirements for hospitals are relevant to one and two family residential dwellings.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.

Reply With Quote
  #45  
Old 6/24/09, 10:53 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: GFCI under Kitchen Sink????

Quote:
Originally Posted by jbushart View Post
Certainly you are not suggesting that the building requirements for hospitals are relevant to one and two family residential dwellings.
No I am not.

But it is evident that the NEC must considers 2-wire systems a possible hazard in some locations.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Composite granite kitchen sink ... good choice? Bill Featherstone Plumbing Inspections 6 1/9/08 12:03 AM
More GFCI info from U/L Greg Fretwell Electrical Inspections 9 12/4/07 9:33 PM
Outlet under kitchen sink adooley Electrical Inspections 3 2/13/07 3:50 PM
venting the kitchen sink kblair1 Plumbing Inspections 57 12/8/06 4:37 PM
No GFCI in Kitchen rnewland Electrical Inspections 6 9/19/06 8:51 AM


All times are GMT -4. The time now is 5:18 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts