Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 216
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default GFCI -water softener

Found a usual double outlet in the garage next to the water softener LOOP. There was no softener in place. The outlet was not GFCI protected although you can tell it was put there for a softener to be plugged into to. My question is, since it's a double outlet, it would not be deemed as a dedicated outlet for the softener (if one were ever to be installed) and since it is in accessible range, shouldn't it be gfci protected? What are some thoughts?
Reply With Quote
  #2  
Old 6/21/07, 2:43 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: GFCI -water softener

Depends on the year the home was built, but generally speaking, yes - it should be GFCI protected. A water softening system doesn't qualify for the exception in most cases.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 6/21/07, 2:48 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI -water softener

There is no rational reason for a water softener to be exempted from GFCI protection. It is not a critical application and there is no hardware reason for it to trip a GFCI other than a shorted motor.

Even if you do choose to exploit 210.8(A)(2)ex2 that only exempts the receptacle in the "dedicated space" that the fixed in place equipment is plugged into. It does not exempt a second hole in a duplex and if the softener is gone the exception goes away with it.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 6:58 PM
Need Help On Chimney Liners Nick Scibetta Exterior Inspections 10 1/11/06 10:53 PM


All times are GMT -4. The time now is 4:43 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts