GFCI trips at outlet but will not trip by my tester. Been so long since I had this issue I cant remember how to describe it. I use a basic 3-light tester (9$). Faster getting the answer here than looking it up. What is the correct explanation for the issue.
Thanks in advance, |
|
#2
|
||||
|
||||
|
Please Note:
rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Could it have an open ground? That would do it.
|
|
#3
|
||||
|
||||
|
Ungrounded outlets will trip by pushing the actual "TEST" button, but will not trip with the GFCI tester.
You have an ungrounded outlet that should be labeled "GFCI protected / NO Equipment ground". |
|
#4
|
||||
|
||||
|
[quote=dvalley]Ungrounded outlets will trip by pushing the actual "TEST" button, but will not trip with the GFCI tester.
You have an ungrounded outlet that should be labeled "GFCI protected / NO Equipment ground".[/quote] That's the one Last edited by rstufflebeem; 3/20/08 at 5:27 PM.. |
|
#5
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
I would be very surprised if home inspectors ever see those stickers for GFCI receptacles. Scraping them off is usually one of the first things the housewife does because they look tacky.
|
|
#6
|
||||
|
||||
|
Quote:
ooops...Did I just say CODE? Oh-oh, please don't cyber attack...I'm innocent. |
|
#7
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
If it showed an intact, operational ground, it should trip by the tester switch. My feeling on this situation is that: The GFCI function is not tripping as it should when the first current leakage to ground is about 10 milliamps or so. I don't know what the self-test trip mechanism/operation is but......if it's not tripping at the lower amperage, replace it. They're only $15 or so......cheap protection. |
|
#8
|
||||
|
||||
|
I believe the only true way to test these outlets is by the test button on the outlet. The manufactures state this in there installation papers.
|
|
#9
|
||||
|
||||
|
In a bathroom at an apartment complex, I came across a GFCI that would not trip with my tester or with the tester button. I recommended that it be replaced.
While I was still on the property, an electrician was sent over to the apartment to affect the repair. I went back to the apartment and it was working perfectly. I asked if he replaced it and he said "no", and that all he did was flip the breaker off and back on. How can this be? BTW, it was not a GFCI breaker. James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas. |
|
#10
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Was the GFCI energized when you tested it? If the breaker was tripped the GFCI would not "test".
|
|
#11
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Brian. What kind of tester are you using? If it is something like a Suretest that puts a load on the ground you can trust the grounding connection but a neon tester might show a good ground with a connection that would not pass 6ma.
|
|
#12
|
||||
|
||||
|
Quote:
James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas. |
|
#13
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Sounds like a bad GFCI to me
|
|
#14
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#15
|
|||
|
|||
|
Since many standard recpetacles are wired "downstream" from a GFCI, the trip button on the tester must be used to identify the existance of GFCI circuits in required areas. A few days ago, I tripped a GFCI located on the opposite side of the kitched from my test location and the GFCI test button actually broke loose and flew a few feet. You never know!!!
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 2 | 1/8/11 8:04 PM |
| More GFCI info from U/L | Greg Fretwell | Electrical Inspections | 9 | 12/4/07 9:33 PM |
| GFCI Safety Notice | rcooke | Electrical Inspections | 1 | 10/30/07 1:29 PM |
| Gfci | cwillick1 | Electrical Inspections | 5 | 5/5/07 2:10 AM |
| GFCI trip or not to trip | abishop | Electrical Inspections | 11 | 5/24/06 7:43 PM |