Default GFCI won't trip by tester

GFCI trips at outlet but will not trip by my tester. Been so long since I had this issue I cant remember how to describe it. I use a basic 3-light tester (9$). Faster getting the answer here than looking it up. What is the correct explanation for the issue.
Thanks in advance,
Reply With Quote
  #2  
Old 3/20/08, 4:57 PM
rbrady's Avatar
rbrady rbrady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI won't trip by tester

Could it have an open ground? That would do it.
Reply With Quote
  #3  
Old 3/20/08, 5:09 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: GFCI won't trip by tester

Ungrounded outlets will trip by pushing the actual "TEST" button, but will not trip with the GFCI tester.

You have an ungrounded outlet that should be labeled "GFCI protected / NO Equipment ground".
Reply With Quote
  #4  
Old 3/20/08, 5:14 PM
Randy D. Stufflebeem's Avatar
Randy D. Stufflebeem Randy D. Stufflebeem is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Galesburg, IL
Posts: 3,277
Default Re: GFCI won't trip by tester

[quote=dvalley]Ungrounded outlets will trip by pushing the actual "TEST" button, but will not trip with the GFCI tester.

You have an ungrounded outlet that should be labeled "GFCI protected / NO Equipment ground".[/quote]

That's the one

Last edited by rstufflebeem; 3/20/08 at 5:27 PM..
Reply With Quote
  #5  
Old 3/20/08, 5:51 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI won't trip by tester

I would be very surprised if home inspectors ever see those stickers for GFCI receptacles. Scraping them off is usually one of the first things the housewife does because they look tacky.
Reply With Quote
  #6  
Old 3/21/08, 7:15 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: GFCI won't trip by tester

Quote:
Originally Posted by Greg Fretwell
I would be very surprised if home inspectors ever see those stickers for GFCI receptacles. Scraping them off is usually one of the first things the housewife does because they look tacky.
True, but I'm simply stating code.

ooops...Did I just say CODE?

Oh-oh, please don't cyber attack...I'm innocent.
Reply With Quote
  #7  
Old 3/21/08, 9:23 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI won't trip by tester

Quote:
Originally Posted by rbrady
Could it have an open ground? That would do it.
That should show on his tester when he plugged it in.
If it showed an intact, operational ground, it should trip by the tester switch.

My feeling on this situation is that:

The GFCI function is not tripping as it should when the first current leakage to ground is about 10 milliamps or so. I don't know what the self-test trip mechanism/operation is but......if it's not tripping at the lower amperage, replace it. They're only $15 or so......cheap protection.
Reply With Quote
  #8  
Old 3/21/08, 9:28 AM
msylvester's Avatar
msylvester msylvester is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Batavia, IL
Posts: 672
Send a message via AIM to msylvester
Default Re: GFCI won't trip by tester

I believe the only true way to test these outlets is by the test button on the outlet. The manufactures state this in there installation papers.



Mark Sylvester
P.I. Home Inspection Services
www.pihomeinspection.com
mark@pihomeinspection.com
Reply With Quote
  #9  
Old 3/21/08, 9:42 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,485
Default Re: GFCI won't trip by tester

In a bathroom at an apartment complex, I came across a GFCI that would not trip with my tester or with the tester button. I recommended that it be replaced.

While I was still on the property, an electrician was sent over to the apartment to affect the repair. I went back to the apartment and it was working perfectly. I asked if he replaced it and he said "no", and that all he did was flip the breaker off and back on.

How can this be? BTW, it was not a GFCI breaker.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.

Reply With Quote
  #10  
Old 3/21/08, 10:08 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI won't trip by tester

Was the GFCI energized when you tested it? If the breaker was tripped the GFCI would not "test".
Reply With Quote
  #11  
Old 3/21/08, 10:13 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI won't trip by tester

Brian. What kind of tester are you using? If it is something like a Suretest that puts a load on the ground you can trust the grounding connection but a neon tester might show a good ground with a connection that would not pass 6ma.
Reply With Quote
  #12  
Old 3/21/08, 10:21 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,485
Default Re: GFCI won't trip by tester

Quote:
Originally Posted by Greg Fretwell
Was the GFCI energized when you tested it? If the breaker was tripped the GFCI would not "test".
It was energized and, according to my tester, properly grounded.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.

Reply With Quote
  #13  
Old 3/21/08, 10:41 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI won't trip by tester

Sounds like a bad GFCI to me
Reply With Quote
  #14  
Old 3/21/08, 10:58 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI won't trip by tester

Quote:
Originally Posted by Greg Fretwell
Brian. What kind of tester are you using? If it is something like a Suretest that puts a load on the ground you can trust the grounding connection but a neon tester might show a good ground with a connection that would not pass 6ma.
23 year old "dinosaur" Suretest. It won't fail so I can justify buying a new one!!! Do carry 2 cheaper backups with me but when I think I may have a problem with the Suretest.....it's always correct!
Reply With Quote
  #15  
Old 3/21/08, 2:22 PM
John Evans John Evans is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Bel Air, MD
Posts: 848
Default Re: GFCI won't trip by tester

Since many standard recpetacles are wired "downstream" from a GFCI, the trip button on the tester must be used to identify the existance of GFCI circuits in required areas. A few days ago, I tripped a GFCI located on the opposite side of the kitched from my test location and the GFCI test button actually broke loose and flew a few feet. You never know!!!




[Maryland Home Inspections
www.aimhomeinspection.com
Infraspection Certified Level 1 No. 7801
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 2 1/8/11 8:04 PM
More GFCI info from U/L Greg Fretwell Electrical Inspections 9 12/4/07 9:33 PM
GFCI Safety Notice rcooke Electrical Inspections 1 10/30/07 1:29 PM
Gfci cwillick1 Electrical Inspections 5 5/5/07 2:10 AM
GFCI trip or not to trip abishop Electrical Inspections 11 5/24/06 7:43 PM


All times are GMT -4. The time now is 11:18 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts