Default Re: GFCI won't trip by tester

It would be possible for Randy's 3 light tester to show a properly grounded gfci, yet still not trip it with the button if it was a bootleg ground.
Reply With Quote
  #17  
Old 3/22/08, 1:06 AM
gporter's Avatar
gporter gporter is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Orlando, fl
Posts: 3,283
Default Re: GFCI won't trip by tester

Had the samething today also. So it should be written up?



Gary Porter

GLP's Home and Mold Inspections
321-239-0621

Certified Commercial Mold Inspector

Serving Orlando, Kissimmee, Winter Park, Winter Springs, Oviedo, Titusville, Celebration, Harmony, Avalon, Windermere, Deltona, Debary, Sanford
Orange County, Seminole County, Volusia County, Osceola County

www.homeandmoldinspections.com
Reply With Quote
  #18  
Old 3/22/08, 1:19 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,948
Default Re: GFCI won't trip by tester

Product Safety Tips:

GFCIs -- A SMALL INVESTMENT, A BIG LIFESAVER
UL Recommends Regular Testing of GFCIs


December 20, 2003: Underwriters Laboratories periodically revises requirements in its Standards for Safety to harmonize with international requirements, address code and safety issues, and accommodate new product developments as applicable. UL has adopted new and revised requirements for Ground-Fault Circuit-Interrupters (GFCIs) that become effective January 1, 2003. Among others, these requirements include enhanced requirements for immunity to voltage surges, resistance to moisture and corrosion, reverse line-load miswiring, and resistance to environmental noise. Though products meeting these revised requirements will soon enter the marketplace, they are not required to have any special markings to distinguish them from models made prior to January 1, 2003. Models of GFCIs Listed by UL that were manufactured and labeled prior to January 1, 2003 still may appear in the marketplace after January 1, 2003, and until such time as old stocks of GFCIs become exhausted.
Ground fault circuit interrupters (GFCI) can help prevent electrocution inside and outside the home. GFCIs are an effective means of protecting against electrical shock, however, they must be tested regularly -- UL recommends once a month -- to verify they are working properly.
"Ground faults" are often the result of damaged appliance cords or consumers who use electrical products in wet environments, such as bathrooms or swimming pool decks. By installing GFCIs in every home in the United States, the U.S. Product Safety Commission (CPSC) estimates that more than two-thirds of the approximately 300 electrocutions occurring each year could be prevented. The advantage of using GFCIs is that they detect even those amounts of electricity too small for your fuse or circuit breaker to activate and shut off the circuit.
Like all products, GFCIs can be damaged. GFCIs damaged by lightning or electrical surges may fail to provide adequate protection. A simple test once a month and after any violent thunderstorm should be conducted.
To properly test GFCI receptacles in your home:
  • Push the "Reset" button located on the GFCI receptacle, first to assure normal GFCI operation.
  • Plug a nightlight (with an "ON/OFF" switch) or other product (such as a lamp) into the GFCI receptacle and turn the product "ON."
  • Push the "Test" button located on the GFCI receptacle. The nightlight or other product should go "OFF."
  • Push the "Reset" button, again. The light or other product should go "ON" again.
If the light or other product remains "ON" when the "Test" button is pushed, the GFCI is not working properly or has been incorrectly installed (miswired). If your GFCI is not working properly, call a qualified, certified electrician who can assess the situation, rewire the GFCI if necessary or replace the device.
"GFCIs are proven lifesavers, however, consumers need to take a few minutes each month to do this simple test. By taking action, you can help protect your family from the risk of electric shock," says John Drengenberg, UL Consumer Affairs Manager.
Several types of GFCIs may be installed in/around your home. Look for the UL Mark on GFCIs when purchasing them or when specifying the product to your electrician.
Wall Receptacle GFCI -- This type of GFCI -- the most widely used -- fits into a standard outlet and protects against ground faults whenever an electrical product is plugged into the outlet. Wall receptacle GFCIs are most often installed in kitchens, bath and laundry rooms, and out-of-doors where water and electricity are most likely to be in close proximity.
Circuit Breaker GFCI -- In homes equipped with circuit breakers, this type of GFCI may be installed in a panel box to give protection to selected circuits. Circuit breaker GFCIs should also be checked monthly. Keep in mind that the test will disconnect power to all lights and appliances on the circuit.
Portable GFCI -- A portable GFCI requires no special knowledge or equipment to install. One type contains the GFCI circuitry in a self-contained enclosure with plug blades in the back and receptacle slots in the front. It can then be plugged into a receptacle, and the electrical products are plugged into the GFCI. Another type of portable GFCI is an extension cord combined with a GFCI. It adds flexibility in using receptacles that are not protected by GFCIs. Portable GFCIs should only be used on a temporary basis and should be tested prior to every use.
Underwriters Laboratories Inc. (UL) is an independent, not-for-profit product safety certification organization that has been testing products for more than a century. More than 16 billion products bearing the UL Mark enter the marketplace every year.


I bet the a large % never get tested .
...Cookie



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #19  
Old 3/22/08, 8:03 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI won't trip by tester

Quote:
Originally Posted by rcooke
I bet the a large % never get tested .
...Cookie
I have seen " monthly test charts" left by the electrician with only the first installed month checked off and this is years after installation.

About 7 years ago, I added this to my Electrical Appendix section on GFCI's:

"In our lengthy inspection experience, we have seen many cases (especially with outdoor GFCI’s) where the receptacle was supplying power but the safety breaker mechanism was seized in place due to corrosion. We now recommend that when using an exterior GFCI protected receptacle: Trip and reset the breaker twice to ensure that the safety feature is functional"
Reply With Quote
  #20  
Old 3/22/08, 1:17 PM
dmcauley's Avatar
dmcauley dmcauley is offline
Active Poster
 
Join Date: Jan 2006
Location: Hoffman Estates, IL
Posts: 855
Please Note: dmcauley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCI won't trip by tester

I agree with Mark on this as this is the way I test GFCIs. I use the tester when down field from the GFCI.
Reply With Quote
  #21  
Old 3/22/08, 9:04 PM
Randy D. Stufflebeem's Avatar
Randy D. Stufflebeem Randy D. Stufflebeem is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Galesburg, IL
Posts: 3,278
Default Re: GFCI won't trip by tester

Just got a call from the actual seller from the same home. I recommended GFCI for an outside recepticle and an electrician told him no need because it was grandfathered in and not the rule at the time of install. I told him I am okay with that but I am still recommending GFCI as safety is key to my reports as I actually care for my clients best interest. Right or Wrong...Play stands! Any thoughts?
By the way he started asking me a ton of questions about my inspection service which who knows he may now call on me.
Reply With Quote
  #22  
Old 3/22/08, 9:09 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,948
Default Re: GFCI won't trip by tester

Quote:
Originally Posted by rstufflebeem
Just got a call from the actual seller from the same home. I recommended GFCI for an outside recepticle and an electrician told him no need because it was grandfathered in and not the rule at the time of install. I told him I am okay with that but I am still recommending GFCI as safety is key to my reports as I actually care for my clients best interest. Right or Wrong...Play stands! Any thoughts?
By the way he started asking me a ton of questions about my inspection service which who knows he may now call on me.
Me too it is a safety item Decks also if incorrect ( example climbing hazard ).
Some kid breaks a elbow they where warned .
I call it CRA ( Cover Roys *****) they all laugh but do not forget.
...Cookie



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #23  
Old 3/22/08, 9:10 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: GFCI won't trip by tester

Recommendations are just that.

It's up to the buyer to make it an issue for negotiation or not.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 2 1/8/11 8:04 PM
More GFCI info from U/L Greg Fretwell Electrical Inspections 9 12/4/07 9:33 PM
GFCI Safety Notice rcooke Electrical Inspections 1 10/30/07 1:29 PM
Gfci cwillick1 Electrical Inspections 5 5/5/07 2:10 AM