Default GFCIs on 2 wire circuits

I was taking the NACHI electrical inspection online course today and under the topic "GFCIs on 2 wire circuits" it states "There is a common misconception that GFCIs only work on grounded circuits. This is not entirely the case." My question is when would a GFCI work on a 2 wire circuit?
Reply With Quote
Find an InterNACHI certified Wyoming Home Inspector (and anywhere else in North America)
  #2  
Old 3/29/09, 10:43 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: GFCIs on 2 wire circuits

Quote:
Originally Posted by dscott2 View Post
I was taking the NACHI electrical inspection online course today and under the topic "GFCIs on 2 wire circuits" it states "There is a common misconception that GFCIs only work on grounded circuits. This is not entirely the case." My question is when would a GFCI work on a 2 wire circuit?
The GFCI does not rrequire a ground to function as it is sensing the current in both the supply and return leg is within 5 mA of each other.

If not it opesns the circut.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 3/29/09, 10:49 PM
dscott2 dscott2 is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Louisburg, KS
Posts: 6
Default Re: GFCIs on 2 wire circuits

So it's ok to install a GFCI on a 2 wire circuit. Thanks Michael
Reply With Quote
  #4  
Old 3/29/09, 11:16 PM
Terry Clayton Terry Clayton is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Arnold, MO
Posts: 246
Default Re: GFCIs on 2 wire circuits

If the AHJ will allow it
Reply With Quote
  #5  
Old 3/29/09, 11:19 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: GFCIs on 2 wire circuits

Quote:
Originally Posted by dscott2 View Post
So it's ok to install a GFCI on a 2 wire circuit. Thanks Michael
Yes but the outlets have to be labeled as not providing a safety ground.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #6  
Old 3/29/09, 11:24 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,956
Default Re: GFCIs on 2 wire circuits

Quote:
Originally Posted by tclayton View Post
If the AHJ will allow it
St. Louis County still uses 2005 NEC and does not modify this rule in their own code. All St. Louis municipalities, likewise....but get a hold of the actual code for the City of St. Louis. They write their own electrical code and this may not be allowed in it.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Reply With Quote
  #7  
Old 3/29/09, 11:24 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: GFCIs on 2 wire circuits

...and receptacles for certain applilcations are required to have a ground, so getting around the three wire requirement with a GFCI has only limited opportunity.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #8  
Old 3/29/09, 11:29 PM
dscott2 dscott2 is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Louisburg, KS
Posts: 6
Default Re: GFCIs on 2 wire circuits

Where I usually find this condition is at kitchen counter outlets and bathroom sink outlets.
Reply With Quote
  #9  
Old 3/29/09, 11:47 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: GFCIs on 2 wire circuits

GFCI works fine on a 2-wire circuit, it's just your typical tester that won't work. The tester needs a ground to be able to simulate a leak to cause it to trip. It will still trip if there is an actual current leak or if you use the device test button which does not require a ground to work. I believe that the on-board test button uses a resistor to simulate a leak.

Most all of the GFCI outlets I have ever purchased come with two sets of labels "GFCI Protected Outlet" for downstream outlets and "No Equipment Ground" for when they are used to provide a 3-prong outlet on an ungrounded system.

NEC allows use on ungrounded systems, but local codes may not.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #10  
Old 3/30/09, 12:02 AM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: GFCIs on 2 wire circuits

Replacing Receptacles to Meet the NEC

The NEC requires receptacles installed on 15 and 20 ampere branch circuits to be of the grounding-type and it requires the grounding contacts of those receptacles to be effectively grounded to the branch circuit equipment grounding conductor [210-7]. However, the Code allows the installation of any of the following installations when replacing a 2-wire nongrounding-type receptacle where no ground exists in the outlet box [210-7(d)(3)], Figure 9/10:

(a) Replace the 2-wire receptacle with another 2-wire receptacle.

(b) Replace the 2-wire receptacle with a GFCI-type receptacle and marked the receptacle with the words “No Equipment Ground.”

(c) Replace the 2-wire receptacle with a grounding-type receptacle where protected by a GFCI protection device (circuit breaker or receptacle). Since the grounding terminals for the receptacles are not grounded, the receptacles must be marked with the words “GFCI Protected” and “No Equipment Ground.”


Author’s Comment: The equipment grounding conductor serves no purpose in the operation of a GFCI protection device, and therefore it has no effect on the function of the GFCI test-button.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!

Last edited by ccurrins; 3/30/09 at 12:05 AM..
Reply With Quote
  #11  
Old 4/4/09, 2:41 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: GFCIs on 2 wire circuits

Yep, lets not forget the structure of the NEC and other documents. Even the "Codeists" like myself need to remember...USBC, IBC,IRC.....then NEC....the NEC is simply a standard to which is referenced so at the end of the day....your statewide building code comes first, then the international codes and then our little NEC.

While the NEC may allow something, the IRC, IBC or the USBC may not.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 5 3/25/07 10:41 PM
UL Information about Testing of GFCIs jtedesco1 Electrical Inspections 0 2/5/06 4:38 PM


All times are GMT -4. The time now is 9:49 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts