Default GFCIs for garbage disposals?

So I'm trying to find out if garbage disposals should be connected to GFCIs. It seems from a quick internet search that the answer is no, but take a look at the NEC code:


"All receptacles serving kitchen counter tops or within 6 feet of any sink shall have GFCI
rotection. 2002 NEC 210.8"Isn't that a firm, "yes"? Unless, of course, your disposal is more than six feet from the sink.

Cheers

Rob
Reply With Quote
Find an InterNACHI certified Alabama Home Inspector (and anywhere else in North America)
  #2  
Old 5/18/09, 2:29 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: GFCIs for garbage disposals?

We used to have electricians come by and answer this type of question but alas no more since moderation happened.

http://www.nachi.org/forum/f19/garba...al-gfci-31343/



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #3  
Old 5/18/09, 2:47 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,647
Default Re: GFCIs for garbage disposals?

If the disposal is NOT hardwired, I recommend a GFCI, knowing that I am not dependent upon the code and what is written will back me up, in a pinch.

Carl Brown and Dale Duffy's board gets quite a few visitors. You can probably get an electrician to respond to you right away.
Reply With Quote
  #4  
Old 5/18/09, 2:55 PM
Rob London Rob London is offline
InterNACHI Member
 
Join Date: May 2009
Posts: 66
Default Re: GFCIs for garbage disposals?

Quote:
Originally Posted by mlarson View Post
We used to have electricians come by and answer this type of question but alas no more since moderation happened.

http://www.nachi.org/forum/f19/garba...al-gfci-31343/
I read that thread thoroughly before I started this one. People seem to think that the code does not require GFCIs for garbage disposals because they are not on sink level, but they don't seem to notice that there is an "or" in the code, not an "and". Kitchen appliances on sink level OR are within six feet of the sink must be protected by a GFCI. As the disposal is underneath the sink I'd say it qualifies. The NEC says nothing specifically about disposals or exemptions from what I can tell.
Reply With Quote
  #5  
Old 5/18/09, 3:16 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,647
Default Re: GFCIs for garbage disposals?

The beauty of being a home inspector is that I can recommend things based upon observation and common sense and am not restricted by the code books.
Reply With Quote
  #6  
Old 5/18/09, 3:18 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: GFCIs for garbage disposals?

Where did you get that reference? Here is the exact text from the 2002 NEC


210.8 Ground-Fault Circuit-Interrupter Protection for Personnel.

(6) Kitchens — where the receptacles are installed to serve the countertop surfaces

(7) Wet bar sinks — where the receptacles are installed to serve the countertop surfaces and are located within 1.8 m (6 ft) of the outside edge of the wet bar sink.

The answer is "no." There is no (nor has there ever been a) requirement for GFCI protection at an under-counter disposal.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #7  
Old 5/18/09, 3:18 PM
Mark E. Northrup's Avatar
Mark E. Northrup Mark E. Northrup is offline
InterNACHI Member
 
Join Date: Dec 2008
Location: Oregon
Posts: 215
Default Re: GFCIs for garbage disposals?

Is this not a problem in it's self. If a motor is pluged into a GFCI the start voltage can sometimes trip the gfci as in the case of a freezer being pluged into one and tripping after you reset it. Leaving the food to get a little warm if not noticed.
Reply With Quote
  #8  
Old 5/18/09, 3:26 PM
Rob London Rob London is offline
InterNACHI Member
 
Join Date: May 2009
Posts: 66
Default Re: GFCIs for garbage disposals?

James - Point taken

Jeffery - I got that reference from here: http://74.125.45.132/search?q=cache:...ient=firefox-a

It's possible that it was altered. I'll go with your reference, thanks. If anyone has any further input I'd like to hear it.
Reply With Quote
  #9  
Old 5/18/09, 4:04 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,647
Default Re: GFCIs for garbage disposals?

Quote:
Originally Posted by jpope View Post
Where did you get that reference? Here is the exact text from the 2002 NEC


210.8 Ground-Fault Circuit-Interrupter Protection for Personnel.

(6) Kitchens — where the receptacles are installed to serve the countertop surfaces

(7) Wet bar sinks — where the receptacles are installed to serve the countertop surfaces and are located within 1.8 m (6 ft) of the outside edge of the wet bar sink.

The answer is "no." There is no (nor has there ever been a) requirement for GFCI protection at an under-counter disposal.

To me, it is common sense to use the GFCI, and I recommend it.

Maybe it is just us old guys, but when I open the doors underneath the sink to poke my head in....the hand that is supporting my weight often has a grip on the wet area countertop, above. As I balance myself with my left hand at the top of the sink, and reach underneath with my right.....I would take comfort in knowing that I was protected by a GFCI.
Reply With Quote
  #10  
Old 5/18/09, 4:19 PM
Rick Maday's Avatar
Rick Maday Rick Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 4,591
Default Re: GFCIs for garbage disposals?

Quote:
Originally Posted by jbushart View Post
To me, it is common sense to use the GFCI, and I recommend it.

Maybe it is just us old guys, but when I open the doors underneath the sink to poke my head in....the hand that is supporting my weight often has a grip on the wet area countertop, above. As I balance myself with my left hand at the top of the sink, and reach underneath with my right.....I would take comfort in knowing that I was protected by a GFCI.
Recmmend visual observation of undersink area prior to inserting right hand.



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #11  
Old 5/18/09, 4:49 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 2,736
Send a message via MSN to bwiley
Default Re: GFCIs for garbage disposals?

I can't think of a reason for the disposal receptacle to be GFCI protected, hard wired or not.

The disposals are not hard wired here, and a GFCI is not required. Nor is one required for the dishwasher, which is also a plug in appliance.



If the opposite of pro is con, the opposite of progress must be...

www.qualityhomeinspectionsfl.com
Reply With Quote
  #12  
Old 5/18/09, 5:02 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: GFCIs for garbage disposals?

Quote:
Originally Posted by jbushart View Post
To me, it is common sense to use the GFCI, and I recommend it.
I'm not sure I understand how you consider it to be "common sense" anymore than many other locations in the home, but that's neither here nor there.

The OP asked for an opinion based on an imaginary code, to which I responded - there is no such requirement.

I support the right of every inspector to make recommendations for "safety upgrades," however, I think there should be something "code based" or "reality based" to make those recommendations on.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #13  
Old 5/18/09, 5:06 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,647
Default Re: GFCIs for garbage disposals?

Quote:
Originally Posted by jpope View Post
I'm not sure I understand how you consider it to be "common sense" anymore than many other locations in the home, but that's neither here nor there.

The OP asked for an opinion based on an imaginary code, to which I responded - there is no such requirement.

I support the right of every inspector to make recommendations for "safety upgrades," however, I think there should be something "code based" or "reality based" to make those recommendations on.
Would you reconsider is the GD was plugged in to a double receptacle(as most are), leaving another receptacle open for use directly beneath the kitchen sink?
Reply With Quote
Find an InterNACHI certified Alabama Home Inspector (and anywhere else in North America)
  #14  
Old 5/18/09, 5:17 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: GFCIs for garbage disposals?

In my mind, that would make no difference. The receptacle is not "readily accessible," so it would rarely (if ever) be used except for a fixed appliance - i.e. water heater, dishwasher, trash compactor, etc.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #15  
Old 5/18/09, 5:17 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,516
Default Re: GFCIs for garbage disposals?

Absolutely agree, otherwise this is exactly how we end up with all kinds of bogus "rule of thumb" theories and personal preferences expressed by many different Inspectors that get passed around / along until these become "fact" or "normal" criteria. This is often how errors get incorporated and evolve into a standard with no basis in reality or accepted practice. I would personally like for every home I inspect to be 100% safe, have no discrepancies, be cleaned prior to the inspection and be provided with a long list of upgrades and known issues but I don't think that is going to happen any time soon. My preferences are not at issue here. I don't think we should be code inspectors but I do think we should be knowledgeable of codes enough to know where the boundaries are and recognize legitimate "unsafe" conditions, but not make up new ones on my own.



Doug Edwards, CMI








Last edited by dedwards; 5/18/09 at 6:55 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
GFCI won't trip by tester rstufflebeem Electrical 22 3/22/08 9:10 PM
Inspection Pointers Here jtedesco1 Electrical 3 3/15/08 10:19 AM
The question asked on the new HI Study test here? jtedesco1 Electrical 28 10/4/06 10:31 AM
UL Information about Testing of GFCIs jtedesco1 Electrical 0 2/5/06 5:38 PM


All times are GMT -4. The time now is 6:12 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts