  #16  
Old 5/18/09, 6:57 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 746
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCIs for garbage disposals?

As Mr. Pope has said there is no need for a GFI for the disposal from a NEC standpoint.
Reply With Quote
Find an InterNACHI certified Washington Home Inspector (and anywhere else in North America)
  #17  
Old 5/18/09, 9:42 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: GFCIs for garbage disposals?

Those who desire to recommend GFCIs were they are not called for may wish to reconsider their take on this issue as there is little added safety in providing a GFCI for a garbage disposal.

A direct wire or grounded receptacle are more than sufficient.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #18  
Old 5/19/09, 10:00 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: GFCIs for garbage disposals?

Quote:
Originally Posted by rlondon View Post
So I'm trying to find out if garbage disposals should be connected to GFCIs. It seems from a quick internet search that the answer is no, but take a look at the NEC code:


"All receptacles serving kitchen counter tops or within 6 feet of any sink shall have GFCI
rotection. 2002 NEC 210.8"Isn't that a firm, "yes"? Unless, of course, your disposal is more than six feet from the sink.

Cheers

Rob

Think here.......

Is the Garbage Disposal receptacle serving the countertop?- NO
Is the receptacle more than 12" down from the countertop surface? - Probably Yes

Now since you are using the 2002 NEC, Where exactly does it say serving the "Kitchen" countertops. Let's look at the NEC 2002 Mind You )

210.8(A)(6) Kitchens
where the receptacles are installed to serve
the countertop surfaces.

Sorry as I dont see anything about the 6' in that section. Maybe you are refering to wet bars, lets look....

210.8(A)(7) Wet bar sinks
where the receptacles are installed to
serve the countertop surfaces and are located within 1.8
m (6 ft) of the outside edge of the wet bar sink.

So since you said nothing about wet bars we wont use 210.8(A)(7) at all and since the garage disposal is not serving any countertop at all then the answer is NO to your question.




Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #19  
Old 5/20/09, 1:25 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is online now
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 29,299
Default Re: GFCIs for garbage disposals?

Michale writes:
Quote:
We used to have electricians come by and answer this type of question but alas no more since moderation happened
Huh?

This message board isn't moderated. Where did you hear that?

Members aren't moderated at all.
Registered non-members who post for a while have their posts go right up as if they were members.
Electricians answering this type of question aren't moderated.

The only small, unique group that could possibly be considered to be moderated would be a non-member who attempts to post something so offensive that none of the moderators (who have no control over members and no control over each other and do not include a single staffer) ALL agree unanimously to prevent the post from being seen. That's not moderation.

The number of posts that fall in that rare latter category constitute 0.01% (1/10,000th) of all posts.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17

Last edited by gromicko; 5/20/09 at 1:33 AM..
Reply With Quote
  #20  
Old 5/20/09, 1:29 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: GFCIs for garbage disposals?

Quote:
Originally Posted by gromicko View Post
Michale writes:

Huh?

This message board isn't moderated. Where did you hear that?

Members aren't moderated at all. Technically impossible.
Registered non-members who post for a while aren't moderated.
Electricians answering this type of question aren't moderated.

The only small, unique group that could possibly be considered to be moderated would be a non-member who attempts to post something so offensive that none of the message board moderators (who have no control over non-members and no control over each other) ALL agree unanimously to prevent the post from going up.
Yes it is moderated in that posts from non members must be approved by a moderator.

Very few non members visit here anymore and some have expressed why. The delay in getting their post approved is only part of the problem.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #21  
Old 5/20/09, 2:00 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is online now
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 29,299
Default Re: GFCIs for garbage disposals?

The few non-members who won't post because they initially have to wait a bit for their posts to become visible apparently has helped the message board. Posts per day are way up since the new message board rules took effect, and I can prove it if you want me to.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17

Last edited by gromicko; 5/20/09 at 2:12 AM..
Reply With Quote
  #22  
Old 5/20/09, 2:21 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: GFCIs for garbage disposals?

Quote:
Most users ever online was 1,315, 6/20/07 at 6:41 PM
Have at it Nick
Reply With Quote
  #23  
Old 5/20/09, 8:46 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 746
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCIs for garbage disposals?

Quote:
Originally Posted by gromicko View Post
Michale writes: Huh?

This message board isn't moderated. Where did you hear that?

Members aren't moderated at all.
Registered non-members who post for a while have their posts go right up as if they were members.
Electricians answering this type of question aren't moderated.

.
Got to disagree with this Nick,

I have been here for months and still have to wait until my posts are approved. I have asked Chris several times for access and not heard anything back. Marcel was also going to check into this and I have not heard from him either.

Since the moderation of non-members has started the only other electrician I know from other forums that contributes here is Paul A. I have not seen MDShunk here is quite a while.
Reply With Quote
  #24  
Old 5/20/09, 8:51 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 746
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFCIs for garbage disposals?

Nick,

I need to correct something in my last post about being a member here for months. It should be changed to years. My join date was July 07.
Reply With Quote
  #25  
Old 5/20/09, 10:19 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: GFCIs for garbage disposals?

Currently Active Users: 45 (45 registered users and 0 guests)



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #26  
Old 5/20/09, 2:26 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,585
Default Re: GFCIs for garbage disposals?

I think it is the thin mountain air that makes Nick have these delusional episodes, Michael. Heck, he did not realize NACHI gets slandered, except in his home state of Pennsylvania, until it happened on his mountain in Denver. I have a lot of respect for Nick but he needs to climb off that mountain and realize what is going on. The declining visits to the message board is just the tip of the iceberg. Sad but true.
Reply With Quote
  #27  
Old 5/20/09, 3:25 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is online now
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 29,299
Default Re: GFCIs for garbage disposals?

Oh I don't think I have data for visits. All I know is # of posts per day have been way up this year and hits have been way up (I have that data). I struggle to imagine how #of posts per day can be up and hits can be up, but # of visitors could be down. Visitors on the bottom of the message board = registered visitors, not viewers/readers. The technical forums are way up.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
GFCI won't trip by tester rstufflebeem Electrical Inspections 22 3/22/08 9:10 PM
Inspection Pointers Here jtedesco1 Electrical Inspections 3 3/15/08 10:19 AM
The question asked on the new HI Study test here? jtedesco1 Electrical Inspections 28 10/4/06 10:31 AM
UL Information about Testing of GFCIs jtedesco1 Electrical Inspections 0 2/5/06 5:38 PM