Question GFI not grounded

Older house with all two prong receptacles with the kitchen and baths being changed to GFI, but not ground. Any issues with GFI not grounded?
Reply With Quote
  #2  
Old 3/4/07, 6:19 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFI not grounded

No special issues. If there is any code that would apply to such installations, it would be the International Existing Building Code. It is mute on that matter.

That said, there is nothing in the "law" that would require a person to ground existing ungrounded circuits. Adding a GFCI to ungrounded bath and kitchen receptacles is an excellent idea. The GFCI will function perfectly fine, and offer an enhancement to safety in these locations. Your plug-in type "traffic light" tester will not trip these GFCI's that are ungrounded, so you'll have to use the test button on the device itself.
Reply With Quote
  #3  
Old 3/4/07, 6:29 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFI not grounded

They are required to be labeled "non-grounded".
Reply With Quote
  #4  
Old 3/4/07, 6:33 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: GFI not grounded

The Instructions with a typical GFCI explains the necessary labeling, and usually include a sticker.

tom
Reply With Quote
  #5  
Old 3/4/07, 6:41 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFI not grounded

Regarding the stickers, there are a couple of realistic conclusions....
1) The stickers are of such poor quality, they can be expected to last only a short period of time. -and-
2) The presence of or lack of the sticker will not change the way the consumer uses the receptacle, in all likelihood.

I'm not so sure I'd get too torn up about this little sticker.
Reply With Quote
  #6  
Old 3/4/07, 6:44 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: GFI not grounded

Marc, Marc, Marc.

I'm guessing you are one of my local inspectors. I have one that doesn't allow for anything other than 2-prong receptacles unless you can verify a ground present. Gfci's on ungrounded circuits is a failure.

tom
Reply With Quote
  #7  
Old 3/4/07, 6:45 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFI not grounded

Quote:
Originally Posted by tdietrich1
Marc, Marc, Marc.

I'm guessing you are one of my local inspectors. I have one that doesn't allow for anything other than 2-prong receptacles unless you can verify a ground present. Gfci's on ungrounded circuits is a failure.

tom
No. I'm saying that GFCI's on existing ungrounded circuits are fine. Not sure how you took it otherwise. Would you like the code citation?
Reply With Quote
  #8  
Old 3/4/07, 6:56 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: GFI not grounded

Quote:
Originally Posted by Marc D. Shunk
No. I'm saying that GFCI's on existing ungrounded circuits are fine. Not sure how you took it otherwise. Would you like the code citation?
ha ha ha, just kidding. I don't like bright red stickers.

tom
Reply With Quote
  #9  
Old 3/4/07, 7:11 PM
Russell Truluck Russell Truluck is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Travelers Rest, SC
Posts: 22
Default Re: GFI not grounded

Tom, so are you saying gfci's on ungrounded circits is wrong?
Reply With Quote
  #10  
Old 3/4/07, 7:12 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: GFI not grounded

Quote:
Originally Posted by rtruluck
Tom, so are you saying gfci's on ungrounded circits is wrong?
NO, NO, NO!

I'm saying that per the NEC it's ok, just that you have to check with your AHJ.

Where I live, I fall under the ICC and NEC, but I drive a few mins north, next city over, I am under the ICC, NEC and the will of the local enforcement inspectors.

tom
Reply With Quote
  #11  
Old 3/4/07, 10:44 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFI not grounded

Quote:
Originally Posted by tdietrich1
.....and the will of the local enforcement inspectors.
This is the part that is complete B-S! How can you "interpret" this section of the code any differently???
If you are under the NEC then a 3-prong GFI is absolutely legal on an ungrounded circuit. And as Marc said, it DOES work and does provide an elevated level of protection.
If an inspector tried to pull that crap on me I'd find another inspector who knows the code.
Reply With Quote
  #12  
Old 3/5/07, 12:09 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: GFI not grounded

Quote:
Originally Posted by Speedy Petey
If an inspector tried to pull that crap on me I'd find another inspector who knows the code.
Few things:

1. This is the only inspector. He is employed by the city.
2. It is code. NEC 90.4

tom
Reply With Quote
  #13  
Old 3/5/07, 7:03 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFI not grounded

Quote:
Originally Posted by tdietrich1
1. This is the only inspector. He is employed by the city.
2. It is code. NEC 90.4
1) That sucks. He is on a power trip and should be reported.
I guess I am lucky, I have choices.

2) "The authority having jurisdiction for enforcement of the Code has the responsibility for making interpretations of the rules, for deciding on the approval of equipment and materials, and for granting the special permission contemplated in a number of the rules."

Interpretation of the rules! NOT making up his own rules.
If he is telling you that he does not "want" GFI replacements on ungrounded circuits that is misinterpretation and abuse of power.

I hear all the time about what some inspectors "want", without any reference to a code section. They just want it.
Sorry, that don't fly!
Reply With Quote
  #14  
Old 3/5/07, 10:15 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFI not grounded

The fact remains there is always a lot of varience in interpretation, no matter what the code says. Florida has a statewide unified code, no local exceptions but they still don't build the same house from county to county, AHJ to AHJ. I have even seen cases where different inspectors in the same building department disagreed what the code says.
Wrong but still true.
Reply With Quote
  #15  
Old 3/7/07, 11:02 PM
Jack R. Robnett Jack R. Robnett is offline
InterNACHI Member
 
Join Date: May 2004
Location: Lubbock, TX
Posts: 65
Default Re: GFI not grounded

From codecheck.com

The GFCI operates by sensing the difference between the currents in the Hot and Neutral conductors. Under normal conditions, these should be equal. However, if someone touches the Hot and a Ground such as a plumbing fixture or they are standing in water, these currents will not be equal as the path is to Ground - a ground fault - and not to the Neutral. This might occur if a short circuit developed inside an ungrounded appliance or if someone was working on a live circuit and accidentally touched a live wire.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Need a clarification kmcmahon Electrical Inspections 15 8/12/07 1:56 PM
So...Do you think THIS panel is Grounded? pabernathy Electrical Inspections 3 1/22/07 7:52 PM
opinions on GFCI outlets for non grounded oputlets jmerritt1 Electrical Inspections 23 5/11/06 7:22 PM
Electrical Inspection Training for Home Inspectors jtedesco1 Inspection Education & Training 6 4/27/06 10:43 PM


All times are GMT -4. The time now is 9:55 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts