Default GFI question

In an older home with a two wire non grounded system.
Can a GFI be installed without being grounded to water system or some other means of grounding the outlet? I am unclear as the NEC make two specific notations about this type of system.
Thanks for the input.



www.alertinspector.com
Texas Professional Inspector
TREC # 8726
Reply With Quote
Find an InterNACHI certified Missouri Home Inspector (and anywhere else in North America)
  #2  
Old 10/15/09, 9:35 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: GFI question

Quote:
Originally Posted by rwooten View Post
In an older home with a two wire non grounded system.
Can a GFI be installed without being grounded to water system or some other means of grounding the outlet? I am unclear as the NEC make two specific notations about this type of system.
Thanks for the input.
Yes...

See:
http://www.mikeholt.com/mojonewsarch...1~20020102.htm



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #3  
Old 10/15/09, 9:39 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,697
Default Re: GFI question

Yes, but you must become the grounding conductor!

Care to give it a try?!



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #4  
Old 10/16/09, 12:09 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2009
Location: Chicago
Posts: 1,049
Default Re: GFI question

No issue.
Reply With Quote
  #5  
Old 10/16/09, 12:24 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,637
Default Re: GFI question

Two-wire systems are grounded, are safe, and are still code compliant. GFI's will work.
Reply With Quote
  #6  
Old 10/16/09, 1:26 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 690
Default Re: GFI question

Quote:
Originally Posted by jbushart View Post
Two-wire systems are grounded, are safe, and are still code compliant. GFI's will work.

However, it will not work with your standard 3 light tester (due to the way the tester works). Use the test button on the GFCI device itself to test.
Reply With Quote
  #7  
Old 10/16/09, 3:23 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,637
Default Re: GFI question

Quote:
Originally Posted by cevans View Post
However, it will not work with your standard 3 light tester (due to the way the tester works). Use the test button on the GFCI device itself to test.
If I am not mistaken, the only method that is authorized by the NEC to test the GFI is with the button on the device, anyway.
Reply With Quote
  #8  
Old 10/16/09, 10:52 AM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 610
Default Re: GFI question

An ungrounded GFCI should be labeled as such. There is typically a label in the original packaging to use.



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr

"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold


Eureka, Fortuna & Arcata, CA
Reply With Quote
  #9  
Old 10/16/09, 10:59 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,697
Default Re: GFI question

Quote:
Originally Posted by jbushart View Post
If I am not mistaken, the only method that is authorized by the NEC to test the GFI is with the button on the device, anyway.
But how many devices have you found that test internally but fail to test externally or are wired wrong downstream and don't test?



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #10  
Old 10/16/09, 11:10 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Cassville, MO
Posts: 13,637
Default Re: GFI question

Quote:
Originally Posted by dandersen View Post
But how many devices have you found that test internally but fail to test externally or are wired wrong downstream and don't test?
I don't understand your point.

While I am not totally certain, I'm reasonably sure that the NEC recognizes the fact that some indications of "pass" or "fail" could be from faulty test equipment as well as faulty GFI's. Accordingly, it officially allows and recognizes the test button on the receptacle, itself, as the test that counts.
Reply With Quote
  #11  
Old 10/16/09, 11:29 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,697
Default Re: GFI question

My point is your point...

Quote:
it officially allows and recognizes the test button on the receptacle, itself, as the test that counts.
My question (or point) is that it can be as incorrect as any test device.
Does "as the test that counts" mean that it is the only acceptable test procedure that they recognize?

If so, I have dozens of cases where the device tested OK, but was not.



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #12  
Old 10/16/09, 11:42 AM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 610
Default Re: GFI question

Quote:
Originally Posted by dandersen View Post
If so, I have dozens of cases where the device tested OK, but was not.
It came up in a recent thread, that sometimes when you press the test button, the GFCI will trip but not disable power to the receptacle.
It is my understanding that a GFCI can be wired to do exactly that. It will protect whatever is downstream, without disabling the power at the receptacle itself. If it should be disabling the power, then I write it up as "mis-wired".



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr

"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold


Eureka, Fortuna & Arcata, CA
Reply With Quote
  #13  
Old 10/17/09, 6:32 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 690
Default Re: GFI question

Quote:
Originally Posted by jbushart View Post
If I am not mistaken, the only method that is authorized by the NEC to test the GFI is with the button on the device, anyway.
I'm not sure about NEC, but the test button is the manufacturer's approved test method, which probably makes it the NEC approved method too.

I added the original comment to clarify for folks so they didn't write ungrounded GFCI devices as defective because they did not trip with their three light tester. I do, however, use my three light tester to test the downstream protected outlets on grounded systems.
Reply With Quote
Find an InterNACHI certified Missouri Home Inspector (and anywhere else in North America)
  #14  
Old 10/18/09, 11:58 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 505
Default Re: GFI question

Quote:
Originally Posted by cevans View Post
I'm not sure about NEC, but the test button is the manufacturer's approved test method, which probably makes it the NEC approved method too.

I added the original comment to clarify for folks so they didn't write ungrounded GFCI devices as defective because they did not trip with their three light tester. I do, however, use my three light tester to test the downstream protected outlets on grounded systems.
I always test GFCIs both ways and frequently find miswired downstream receptacles using the 3 wire tester. Actually, that is about the only way to test the downstrea, devices - no test button on them !



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sump Pit/Pump Question Joey D'Adamo Plumbing 4 11/26/08 2:04 PM
Question for all... Bob Hopton-Jones General Inspection Discussion 9 4/6/07 8:43 AM
Basement Bathroom Venting Question Sean M. Jeric Plumbing 4 3/21/07 12:56 AM


All times are GMT -4. The time now is 9:48 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts