Angry GFI's

Is there any written rule and if there is where can i find it. I have a customer that claims that her GFI that is located next to her FEDERAL PACIFIC breaker panel is all she needs.

From my understanding a homeowner needs a Gfi in the kitchen and one in each bathroom. Unless they are all wired downstream.

I need to find info on this !!!

HELP
Reply With Quote
Find an InterNACHI certified Michigan Home Inspector (and anywhere else in North America)
  #2  
Old 12/9/09, 7:32 PM
staylor5's Avatar
staylor5 staylor5 is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Freehold, NJ
Posts: 108
Default Re: GFI's

Why argue with her. Tell her she is wrong and move on. If this is for a home inspection you should be using a code book anyway.
Reply With Quote
  #3  
Old 12/9/09, 7:35 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFI's

Given the age based on the panel brand I doubt that any GFI protection was required when the house was built.

A GFI located next to the panel may provide protection to the downstream devices. If the kitchen and bath are on one circuit this could be possible.

It sounds like you are asking if the bath and kitchen can share a circuit, but I am not sure. Under recent code editions they could not share a receptacle circuit. I do not know when the current circuit requirements were added that require 2 20 amp small appliance and the 20 amp bathroom receptacle circuit.
Reply With Quote
  #4  
Old 12/9/09, 7:40 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFI's

Quote:
Originally Posted by staylor5 View Post
Why argue with her. Tell her she is wrong and move on. If this is for a home inspection you should be using a code book anyway.
If the house pre-dates the requirements for GFI protection could you please explain how she is wrong? Without more facts this could go either way.

Also it seems like many say that HIs are not code inspectors and codes should not be part of the inspection.
Reply With Quote
  #5  
Old 12/9/09, 8:41 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: GFI's

Quote:
Originally Posted by Jim Port View Post
Also it seems like many say that HIs are not code inspectors and codes should not be part of the inspection.
That is correct Jim. Even though we may use codes as a basic reference, we do not carry a code book around at an inspection.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #6  
Old 12/9/09, 9:04 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: GFI's

Lack of GFCI protection in required locations should be considered a defect, regardless of when the home was built and what code requirements were at the time. Same with smoke detectors, etc.

These are considered basic safety devices by current standards and are easily retrofitted. That said, it doesn't mean that the seller is automatically on the hook to implement them. Our job is to inform the client about the house not negotiate repairs and upgrades.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #7  
Old 12/9/09, 9:44 PM
Chuck Lambert Chuck Lambert is offline
Unmoderated Guest
 
Join Date: Jan 2008
Location: Southern California
Posts: 228
Please Note: Chuck Lambert is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFI's

Quote:
Originally Posted by cevans View Post
Lack of GFCI protection in required locations should be considered a defect, regardless of when the home was built and what code requirements were at the time. .
I disagree, lack of GFCI's in a 1965 built house is not a defect. They were NOT required when home was built. If an item was not required at time of construction how can it be a defect.

Your 1957 Chevy does not have a third brake light and no airbags...is it defective?

Recommend GFCI's be added as a SAFETY upgrade, that is all we can do.

Chuck
Reply With Quote
  #8  
Old 12/9/09, 11:21 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: GFI's

Quote:
Originally Posted by Chuck Lambert View Post
I disagree, lack of GFCI's in a 1965 built house is not a defect. They were NOT required when home was built.

Recommend GFCI's be added as a SAFETY upgrade, that is all we can do.

Chuck
Agreed. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 12/9/09, 11:39 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: GFI's

Quote:
Originally Posted by Chuck Lambert View Post
I disagree, lack of GFCI's in a 1965 built house is not a defect. They were NOT required when home was built. If an item was not required at time of construction how can it be a defect.

Your 1957 Chevy does not have a third brake light and no airbags...is it defective?

Recommend GFCI's be added as a SAFETY upgrade, that is all we can do.

Chuck

Seat belts didn't use to be required in cars either, but the analogy is totally irrelevant. Lack of GFCI or smoke detectors is still a defect in my opinion and you'd be negligent not to report it to your client, just as you would be negligent in not reporting lack of seatbelts in a car if someone had hired you to do a safety inspection.

If someone were electrocuted for lack of a GFCI that wasn't required when the house was built and you decided wasn't a deficiency worthy of reporting in a contemporary inspection, how do you think you would fare in a court defense against negligence? I think would be a pretty tough sell for you.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX

Last edited by cevans; 12/9/09 at 11:43 PM..
Reply With Quote
  #10  
Old 12/9/09, 11:39 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: GFI's

Unfortunately the state of Texas doesn't agree so Chuck E and I have to report lack of GFCI, AFCI and several other similar items as "Deficient" regardless of the age of the home to comply with our state SOP.



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
  #11  
Old 12/10/09, 12:25 AM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GFI's

Quote:
Originally Posted by mboyett View Post
Unfortunately the state of Texas doesn't agree so Chuck E and I have to report lack of GFCI, AFCI and several other similar items as "Deficient" regardless of the age of the home to comply with our state SOP.

I know some states require smoke detector upgrades any time a home is remodeled or sold. Does Texas required GFCI or AFCI upgrades upon sale?

www.MauiHomeInspections.com
Reply With Quote
  #12  
Old 12/10/09, 12:36 AM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: GFI's

Illinois SOP is a little vague on what is deficient and puts the burden on the inspector.

2) Report on those systems and components inspected that, in the
opinion of the inspector, are significantly deficient; and

A) A reason why the system or component is significantly
deficient.

I do report lack of GFI's and it depends on the age of the building how I report it.

Also, many municipalities in my area that have occupancy inspections before you can live in a home use either the 2002 or 2006 NEC code which requires a GFCI in many locations.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #13  
Old 12/10/09, 12:39 AM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: GFI's

Quote:
Originally Posted by Mark Thorman View Post
I know some states require smoke detector upgrades any time a home is remodeled or sold. Does Texas required GFCI or AFCI upgrades upon sale?

www.MauiHomeInspections.com
Not state wide, but some cities may. If any do, it would likely be Austin where Mike B is located. The state SOP, however clearly stipulates how home inspectors are supposed to report.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
Find an InterNACHI certified Michigan Home Inspector (and anywhere else in North America)
  #14  
Old 12/10/09, 1:13 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: GFI's

Quote:
Originally Posted by tdevine View Post
Is there any written rule and if there is where can i find it. I have a customer that claims that her GFI that is located next to her FEDERAL PACIFIC breaker panel is all she needs.

From my understanding a homeowner needs a Gfi in the kitchen and one in each bathroom. Unless they are all wired downstream.

I need to find info on this !!!

HELP
A code book might help, or perhaps some training on resedential electrical systems.
Reply With Quote
  #15  
Old 12/10/09, 5:45 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: GFI's

Quote:
Originally Posted by cevans View Post
If any do, it would likely be Austin where Mike B is located.
No, not for a sale but on a remodel...who knows what the AHJ might require? The door is opened on a permitted remodel to all sorts of requirements.



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Do lack of GFI's prevent funding? rwashington Electrical Inspections 5 2/18/07 6:16 PM


All times are GMT -4. The time now is 9:55 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts