Default Gotta Blast Today!

During an inspection today I was down in the basement bathroom, went to plug my tester in the outlet and it blew clean out of my hand and into the sink. Didn't even trip the breaker (FPE Panel). Charred the ends of the tester.gotta-blast-today-tester.jpg



Bobby Hamilton
Bloodhound Home Inspection Services
Youngstown Home Inspection
Austintown Ohio Home Inspection


Providing home inspections, state licensed termite inspections and radon testing in Youngstown, Boardman, Canfield, Poland, Howland, Warren and surrounding Northeast Ohio areas.
Reply With Quote
Need a home inspection in Arizona? Check out InterNACHI's listing of Arizona certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/7/10, 9:55 PM
Ed Bancroft Ed Bancroft is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Brooksville, FL
Posts: 748
Default Re: Gotta Blast Today!

Good reminder to keep your distance when plugging in!
Reply With Quote
  #3  
Old 6/7/10, 11:59 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Gotta Blast Today!

Glad you're OK Bobby. Any pics of the FPE Panel?



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #4  
Old 6/8/10, 12:31 AM
Bobby Hamilton's Avatar
Bobby Hamilton Bobby Hamilton is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Austintown, OH
Posts: 1,246
Default Re: Gotta Blast Today!

Quote:
Originally Posted by ccurrins View Post
Glad you're OK Bobby. Any pics of the FPE Panel?
Thanks Chris. Here's one, should've guessed there would be dbl taps all over the place by just looking at the telephone wire connections to the left of the panel.
gotta-blast-today-img_0091.jpg



Bobby Hamilton
Bloodhound Home Inspection Services
Youngstown Home Inspection
Austintown Ohio Home Inspection


Providing home inspections, state licensed termite inspections and radon testing in Youngstown, Boardman, Canfield, Poland, Howland, Warren and surrounding Northeast Ohio areas.
Reply With Quote
  #5  
Old 6/8/10, 12:56 AM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Gotta Blast Today!

Quote:
Originally Posted by bhamilton View Post
Thanks Chris. Here's one, should've guessed there would be dbl taps all over the place by just looking at the telephone wire connections to the left of the panel.
Attachment 37374
Why bother adding breakers. I like the bare grounding conductor terminating at breaker at left side.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #6  
Old 6/8/10, 1:29 AM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Gotta Blast Today!

Quote:
Originally Posted by bhamilton View Post
During an inspection today I was down in the basement bathroom, went to plug my tester in the outlet and it blew clean out of my hand and into the sink. Didn't even trip the breaker (FPE Panel). Charred the ends of the tester.Attachment 37373
Glad you're OK Bobby------!!

FPE--
Reply With Quote
  #7  
Old 6/8/10, 5:00 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Gotta Blast Today!

Quote:
Originally Posted by ccurrins View Post
I like the bare grounding conductor terminating at breaker at left side.
Are you saying that a bare equipment grounding conductor is terminating on a CB on the left side of the panel? At first glance it appeared that way to me too, on the 9th CB, but at second look it appears that the insulation is just a lighter shade of black.

What was wrong with the receptacle to cause the tester problem?
Reply With Quote
  #8  
Old 6/8/10, 8:52 AM
John E. Mullarkey John E. Mullarkey is offline
InterNACHI Member
 
Join Date: Oct 2009
Location: Sarasota, Fl
Posts: 349
Default Re: Gotta Blast Today!

You are a lucky guy Bobby. If the panel is FPE or Zinsco I do not pull them, waaaaay too dangerous.
Reply With Quote
  #9  
Old 6/8/10, 8:55 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Gotta Blast Today!

Quote:
Originally Posted by jmullarkey View Post
You are a lucky guy Bobby. If the panel is FPE or Zinsco I do not pull them, waaaaay too dangerous.
Especially if your incident occured before you opened the panel. That could have been your "warning shot".
Reply With Quote
  #10  
Old 6/8/10, 9:17 AM
Bobby Hamilton's Avatar
Bobby Hamilton Bobby Hamilton is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Austintown, OH
Posts: 1,246
Default Re: Gotta Blast Today!

Quote:
Originally Posted by jjonas View Post
Especially if your incident occured before you opened the panel. That could have been your "warning shot".
Where's your sense of excitement? All you need is a pair of shades and surgeon hands. Fingers grow back, don't they?



Bobby Hamilton
Bloodhound Home Inspection Services
Youngstown Home Inspection
Austintown Ohio Home Inspection


Providing home inspections, state licensed termite inspections and radon testing in Youngstown, Boardman, Canfield, Poland, Howland, Warren and surrounding Northeast Ohio areas.
Reply With Quote
  #11  
Old 6/8/10, 10:12 AM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Gotta Blast Today!

Yeah, the FPE panel is a hazard, but that was not the cause of the incident. Any idea what it was? It seems wierd, by the picture, the ground pin has a char mark on it.


Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #12  
Old 6/8/10, 10:45 AM
Steven C. Waskewicz's Avatar
Steven C. Waskewicz Steven C. Waskewicz is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Colorado Springs, CO
Posts: 1,948
Default Re: Gotta Blast Today!

If that had happened to me on an inspection, I'd be quickly calling for an electrician to check out the house wiring.
.
Imagine if this happened when plugging in some type of appliance?




Steven Waskewicz

Professional Building Analyst, BPI
Colorado Springs, Colorado
719-510-7703
Rest Assured Inspection Services, LLC.
719-510-7703 mobile all the time





Reply With Quote
  #13  
Old 6/11/10, 12:33 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Gotta Blast Today!

Quote:
Originally Posted by jmullarkey View Post
You are a lucky guy Bobby. If the panel is FPE or Zinsco I do not pull them, waaaaay too dangerous.

And your reference to the client would be based on what? Just so I am clear.

The issues with Zinsco was more so over the aluminum buss that came into effect at the onset of a copper shortage in the late 60's...otherwise please explain your concerns..and not just want you read on some websites.

As for FPE....other than a CRAPPY wiring job...their is space in that panel and so on....looks very clean. So while you would defer it and possible the client could have the breakers replaced with proper UL listed aftermarket breakers like "challenger"....whats the reason you would recomment full replacement....?

We read WAY to many things on the internet that lead us to make statements that mislead people. Yes, FPE was part of a class action suit in New Jersey and yes they did lie about their UL listings...but remember they are still used in canada under federal pioneer without the same issues....but still have the stab design. The CPSC did a test and did not recommend a full recall...so yes, defer them simply because the breakers dont function...but you might suggest to them if they do nothing to atleast look into replacing the breakers with aftermarket UL listed ones that do meet UL standards.....

Just a thought.....versus blanket statements.....



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
GutterStuff on the Today show - Link to segment tmcnamara Ancillary Inspection Services & Additional Topics 0 10/9/08 6:48 AM
GutterStuff on the Today show - Link to segment tmcnamara Exterior Inspections 0 10/9/08 6:47 AM
GutterStuff on the Today show - Link to segment attached tmcnamara Miscellaneous Discussion for Inspectors 0 10/9/08 6:41 AM


All times are GMT -4. The time now is 9:56 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts