Default Green bonding screw

Doesn't the green bonding screw need to be attached to the panel. The bar is broken on this Cutler Hammer 125 amp 1/0 aluminum main panel.
Attached Thumbnails
green-bonding-screw-dsc00846.jpg  



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
Need a home inspection in New Jersey? Check out InterNACHI's listing of New Jersey certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/23/10, 7:55 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Green bonding screw

Sometimes those little bonding bars are shipped with their green screw tapped into the panel but not landed on the neutral bar. It appears that the screw has a small piece of copper that should have been entered into one of the holes in the neutral bar and tightened.
Reply With Quote
  #3  
Old 3/23/10, 8:19 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Green bonding screw

Is this a sub panel? I see no grounds.

In a sub panel the neutral bar is NOT connected to the panel.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #4  
Old 3/23/10, 8:28 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Green bonding screw

Quote:
Originally Posted by ccurrins View Post
Is this a sub panel? I see no grounds.

In a sub panel the neutral bar is NOT connected to the panel.

I only see a three wire feed and it looks like it is coming from a meter base.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #5  
Old 3/23/10, 8:40 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Green bonding screw

I see a bonding strap/jumper that is not attached. Where's the broken "bar" you're referring to?

The three-wire feed is fine for service equipment, but I too wonder where all the egc's are. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 3/23/10, 9:07 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: Green bonding screw

Quote:
Originally Posted by jpope View Post
I see a bonding strap/jumper that is not attached. Where's the broken "bar" you're referring to?

The three-wire feed is fine for service equipment, but I too wonder where all the egc's are. . .
The broken strap not attached is the bar I'm referring to. The bar that the bonding screw is attached to it which is left of the neutral bus. I know my terminology is off so please set me straight.

The egc's are crammed down at the bottom left behind all the bundling.

This was a main panel as I mentioned in the first post.



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #7  
Old 3/23/10, 10:09 PM
Jeffrey Moore Jeffrey Moore is online now
InterNACHI Member
 
Join Date: Feb 2008
Location: Mesa, AZ
Posts: 282
Default Re: Green bonding screw

I cannot see where the egc's are attached anywhere. Are they just bundled together or are they attached somehow/somewhere?



Jeff Moore
www.quantumhomeinspections.com
Flir (ITC) Level II Thermographer
Mesa, AZ
Reply With Quote
  #8  
Old 3/23/10, 11:13 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Green bonding screw

Then you are correct, the bonding strap (the copper strap/jumper with the green screw) should be attached directly to the neutral terminal bar.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 3/25/10, 5:53 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: Green bonding screw

Quote:
Originally Posted by jpope View Post
Then you are correct, the bonding strap (the copper strap/jumper with the green screw) should be attached directly to the neutral terminal bar.
Great. Thanks for your help.

Any further wording that you would add. Here is what I put in the report. The photo is the same photo I posted.

The green bonding screw is not attached to the neutral bus bar via the copper pipe behind the dead front cover. PHOTOGRAPH "L"



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #10  
Old 3/25/10, 8:15 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Green bonding screw

It's possible (not likely, but possible) that the bond was established elsewhere.

The neutral conductors are required to be bonded to the enclosure at the service panel. A bonding connection was not visible and should be verified or established by a qualified electrician.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 3/25/10, 8:42 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Green bonding screw

Quote:
Originally Posted by jpope View Post
It's possible (not likely, but possible) that the bond was established elsewhere.

The neutral conductors are required to be bonded to the enclosure at the service panel. A bonding connection was not visible and should be verified or established by a qualified electrician.

Jeff,
Since this panel contains the service disconnect and has an offset nipple connecting it directly to the meter enclosure where else do you think that bond could be?
Reply With Quote
  #12  
Old 3/25/10, 9:15 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Green bonding screw

I've seen instances where bonding conductor was attached to the neutral terminal and to the grounding terminal - just a wire run between each terminal bar.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Siemens distribution panel bonding screw installation jfrederick Electrical Inspections 10 8/18/09 9:42 PM
Bonding Screw kmalone Electrical Inspections 25 4/6/08 6:16 PM
Neutral bus bar failed inspection Greg Moritz Electrical Inspections 18 1/19/08 1:53 PM
Subpanel Bonding Screw away Electrical Inspections 24 1/9/08 2:46 PM


All times are GMT -4. The time now is 9:56 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts