Default Grouding at the main panel

Hello everyone... my first post ! The first pic is the exterior panel just below the meter. Isn't the GEC supposed to be connected to the neutral in this panel ?

The second pic is the interior sub-panel. Comments on my above question and any other issues are welcomed ! Other than the GEC issue, I don't see any other problems with these panels (correct me if I am wrong).

http://imageshack.us/photo/my-images/155/img1346c.jpg/

http://imageshack.us/photo/my-images/254/img1355k.jpg/
Reply With Quote
Need a home inspection in South Carolina? Check out InterNACHI's listing of South Carolina certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/10/11, 10:10 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Grouding at the main panel

The connection for the GEC should be visible in your first picture.

Additionally, there should be an equipment grounding conductor leaving the first panel and attached to the grounding terminal at the "sub" panel - it may be that the conduit is providing this bond, but it's not visible in your photos.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 11/10/11, 4:51 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grouding at the main panel

Is this equipment listed for use as service equipment?

Reply With Quote
  #4  
Old 11/10/11, 6:30 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grouding at the main panel

I wonder if the bond screw is just below the neutral lug near the top of the buss?

Perhaps the grounding is in the meter socket?
Reply With Quote
  #5  
Old 11/10/11, 6:31 PM
James L. Keilson's Avatar
James L. Keilson James L. Keilson is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Maryland, USA
Posts: 1,378
Send a message via ICQ to jkeilson
Default Re: Grouding at the main panel

Quote:
Originally Posted by Robert Meier View Post
Is this equipment listed for use as service equipment?


Not possible to tell from this picture. It could just be some home made fused disconnect from what is in the pic. Would need to see the entire enclosure and better yet the manufacturer label to answer your question.

Jim




Maryland Home Inspection Services Inc.

www.MarylandHomeInspectionServices.com

State of Maryland License# 31141
Virginia License#3380 000468

National Association Of Certified Home Inspectors ID: NACHI10101807
International Association of Certified Indoor Air Consultants (IAC2). Certification # IAC2-02-0919
Maryland Home Inspectors In Gaithersburg, Rockville, Germantown, Bethesda, Potomac, Also All of Northern Virginia and Washington, D.C.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sub panel main tripping? crichiii Electrical Inspections 6 12/28/06 10:08 AM
Main Panel location dmacy Electrical Inspections 5 12/6/06 6:32 PM
Main disconnect at meter instead of main panel. OK? kshepard Electrical Inspections 14 11/8/06 6:24 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 9:56 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts