Default Ground and neutral on same bar?

Sorry this is my weakest subject. In question is the bottom left 220 breaker. Red and black are hooked to the breaker(pic1). The white wire is connected to the same bar as the bare copper wire(pic 2&3). The ground and neutral bar are connected by a copper bar(pic4). This wire was brought in with no clamps telling me it may be a homeowner installation. I could not determine what was powered by this wire to see connections on other end. Any help is appreciated, Thank you, Karl
Attached Thumbnails
ground-and-neutral-same-bar-panel-1.jpg   ground-and-neutral-same-bar-panel-2.jpg   ground-and-neutral-same-bar-panel-3.jpg   ground-and-neutral-same-bar-panel-4.jpg  
Reply With Quote
  #2  
Old 6/15/07, 5:08 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,542
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ground and neutral on same bar?

Its linking the two neutral / ground bars. I see no problem with it.
Reply With Quote
  #3  
Old 6/15/07, 6:07 PM
Karl E. Gerhauser's Avatar
Karl E. Gerhauser Karl E. Gerhauser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Coos Bay, OR
Posts: 438
Default Re: Ground and neutral on same bar?

To my knowlege all that is needed for 220 is 2 hots and a ground, why the extra heavy neutal hooked to the ground bar?
Reply With Quote
  #4  
Old 6/15/07, 6:12 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,468
Default Re: Ground and neutral on same bar?

Quote:
Originally Posted by kgerhauser
To my knowlege all that is needed for 220 is 2 hots and a ground, why the extra heavy neutal hooked to the ground bar?
It may be feeding a remote panel.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #5  
Old 6/15/07, 6:16 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,103
Default Re: Ground and neutral on same bar?

The cable they used just had the extra white wire. The other end may have a 120V device that uses that neutral. Did they have a hot tub outside?



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #6  
Old 6/15/07, 6:23 PM
Karl E. Gerhauser's Avatar
Karl E. Gerhauser Karl E. Gerhauser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Coos Bay, OR
Posts: 438
Default Re: Ground and neutral on same bar?

There is no remote panel. The only external item is a Solar hot water panel which is also plumbed with PB 2110.
Reply With Quote
  #7  
Old 6/15/07, 6:25 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ground and neutral on same bar?

40 amp breaker, from the looks of it. Popular size for an electric range or a small packaged spa.
Reply With Quote
  #8  
Old 6/15/07, 8:07 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,468
Default Re: Ground and neutral on same bar?

Quote:
Originally Posted by kgerhauser
There is no remote panel. The only external item is a Solar hot water panel which is also plumbed with PB 2110.
Well, Karl, I know that you know what to report about that.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #9  
Old 6/15/07, 8:58 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Ground and neutral on same bar?

Looks like a common service-equipment install to me.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 6/17/07, 12:27 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Ground and neutral on same bar?

Karl,

Many situations could be presented to explain why their is a "grounded" conductor run...as marc says it could be for the range or it could be to something that has 240V but also has a timer on it that needs the 120V so thus a neutral is needed.....you may ask why does a Range need it...well the timers and many parts of the functions that control the range work on 120V and not 240V so that is why in many cases a "Grounded" conductor is run....so unless you can determine what that double pole is powering....I would not concern myself over the neutral's size.....but I would make a good case for WHY panels should be labeled properly and note that as such....if you can't tell what it is...chances are your client wont be able to either.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #11  
Old 6/17/07, 2:29 AM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Ground and neutral on same bar?

Based on the pictures you posted, I would not write up anything...provided this is the service equipment.

I would write up a missing clamp, and I would verbally inform my clients that I suspect a non-electrician installed the circuit.
Reply With Quote
  #12  
Old 6/17/07, 11:58 PM
Karl E. Gerhauser's Avatar
Karl E. Gerhauser Karl E. Gerhauser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Coos Bay, OR
Posts: 438
Default Re: Ground and neutral on same bar?

Thank you all, off of what you stated I realized this may be the 90+ furnace that looks new(it has a condensate pump system). The home had no GFCI, so I already called for eval. by an electrician and added for him to look at the amateur installation and lack of labeling. Defer, Defer, Defer. I was trying to understand it for my own edification. Everyone has been a great help, Thanks again. Larry, I know that you know, that I know. Karl.
Reply With Quote
  #13  
Old 1/20/08, 5:28 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ground and neutral on same bar?

Looks like the MBJ on the left side was missing, and did you question the black tape at phase A and B terminations, and the tape covering the Hex Head on the left? What size were those SEC's?

See NEC Article 250 for Grounding and Bonding requirements.

I plan on taking the advice of many and will begin adding the NEC references for information only, so that everyone knows that there are rules that cover the situations you encounter.

Last edited by jtedesco1; 1/22/08 at 8:12 AM..
Reply With Quote
  #14  
Old 1/20/08, 5:58 AM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 4,363
Default Re: Ground and neutral on same bar?

Quote:
Originally Posted by jtedesco1
Looks like the MBJ on the left side was missing, and did you question the black tape at phase A and B terminations, and the tape covering the Hex Head on the left? What size were those SEC's?

See NEC Article 250 for Grounding and Bonding requirements.

I plan on taking the advice of many and will begin adding the NEC references for information only, so that everyone knows that there are rules that cover the situations you encounter.
Joe,
Thank you for pointing that out.
I also noticed the "black tape" at the terminations and the tape covering the hex nut and I was going to say something but....I wanted to look up the NEC and I have just returned to the BB and I see that there are a lot of "threads" that I want to read before I respond to anything.

I have found that if I do a "Cut & Paste" of the pertinent sections of the IBC, IR, NEC etcetera it helps out a lot and cuts down on the non member lack of knowledge / contradictions.

Keep up the good work. It is GREATLY appreciated!



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
New Hampshire License #0096
Reply With Quote
  #15  
Old 1/20/08, 6:21 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ground and neutral on same bar?

Frank, you are welcomed and from now on everyone gets to see the National Electrical Code rules for references and for learning.

Mike go for it Code, is what they need.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
THE "GROUNDING "TRUTH- Article To Read pabernathy Electrical Inspections 1 1/1/07 2:14 PM
Bare wire on old dryer or stove circuit: neutral or ground? fbartlo Electrical Inspections 9 8/28/06 2:08 AM
Ground wire in neutral bar, neutral to breaker, hot to ground? rmc3inspection Electrical Inspections 4 8/1/06 10:44 AM