Default Ground bar

Am I correct in stating that the wire should not be in contact with the side of the panel.

ground-bar-img_0170.jpg






Performing Home Inspections in Council Bluffs, Missouri Valley, Glenwood, and surrounding areas

Active Rain Member
Reply With Quote
Need a home inspection in Wisconsin? Check out InterNACHI's listing of Wisconsin certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/30/11, 7:50 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Ground bar

Quote:
Originally Posted by jharrison View Post
Am I correct in stating that the wire should not be in contact with the side of the panel.

Attachment 44396
Makes no difference as that bus is tied to the case anyway.

A bit sloppy, yes.

A problem, no.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 4/30/11, 9:00 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Ground bar

Like Michael said, it's already in contact via bonding strap. Is there another bus?



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #4  
Old 4/30/11, 9:39 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: Ground bar

Is the main disconnect in this panel?



Comprehensive Building Consultants
Naples Home Inspection, Naples Mold Inspection, Naples Radon Inspection, Bonita Springs Home Inspection, Bonita Springs Mold Inspection, Bonita Springs Radon Inspection.



Donate here:

or send checks to the
Fl Home and Insurance Inspector Chapter
1103 W Hibiscus Blvd Ste 311
Melbourne, Fl 32901
Reply With Quote
  #5  
Old 4/30/11, 10:28 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ground bar

I agree sloppy but not a problem. The black conductor with the white tape is an issue though.
Reply With Quote
  #6  
Old 4/30/11, 11:21 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: Ground bar

Quote:
Originally Posted by jharrison View Post
Am I correct in stating that the wire should not be in contact with the side of the panel.

Attachment 44396
The white tape on the black conductor is a no-go. Also, is that rust in the lower left corner of the picture? I'd be a little concerned about that if it is.



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
  #7  
Old 5/1/11, 11:10 AM
John Harrison's Avatar
John Harrison John Harrison is offline
InterNACHI Member
 
Join Date: May 2005
Location: Council Bluffs, Iowa
Posts: 940
Default Re: Ground bar

Quote:
The white tape on the black conductor is a no-go.
That one is installed backwards.

Quote:
Is the main disconnect in this panel?
Yes it is.

Quote:
Like Michael said, it's already in contact via bonding strap. Is there another bus?
No there is not






Performing Home Inspections in Council Bluffs, Missouri Valley, Glenwood, and surrounding areas

Active Rain Member
Reply With Quote
  #8  
Old 5/1/11, 12:55 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ground bar

Quote:
Originally Posted by jharrison View Post
That one is installed backwards.

So the white is landed on the breaker?
Reply With Quote
  #9  
Old 5/1/11, 9:26 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Ground bar

Quote:
Originally Posted by gwells View Post
Also, is that rust in the lower left corner of the picture? I'd be a little concerned about that if it is.
Boy you would hate it here with all the outside panels we have. Hell a little rust on the breaker screws never hurt anything around here.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Hey Electricians... Can you help by proofing this new course? gromicko Electrical Inspections 69 10/15/08 6:14 AM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Harmonized Ground Fault Circuit Interrupters jtedesco1 Electrical Inspections 5 3/21/06 8:48 AM