Saw this one today - fairly new service panel, several egc's were bundled, then pigtailed to a bus. The bundle seems wrong and the size of the pigtail definitely seems wrong (too small -16awg). The local Electrical Inspector passed it so I'm not going to shovel sand against the tide. Just wondering what you think.
http://www.SmithHomeInspection.com SmithHomeInspection@yahoo.com NY State Lic. # 16000008304 631-434-5200 |
I'm sorta stumped on this one. I wouldn't do that myself, but I think it's legal as well. If I ran 10 circuits into a junction box, for instance, I only need one ground that is rated for the single biggest circuit in that box. If this was a bundle of all 16 ga. reduced grounds, one pigtail to the bar is probably legal. I forget if the QO ground bars are rated for a conductor that small, though. I don't have one handy here at home to look at, but I'm thinking they're only rated for a #14 as the smallest conductor.
I don't use Greenies myself, but I just happened to think I should look up their capacity:
#14 thru #10 AWG Min. 2 #14 Max. 3 #12 w/ 1#14 They're not even rated for however many #16's they're holding in that picture. The second picture appears to show another big azz bundle in one ground bar hole. If that's the case, that's improper also. |
Thanks Marc-
The ground bundle in the second pic is actually the ground from the sec. "A man cannot be truly grateful and remain unhappy"
I write up all twisted/capped grounds. That's simply a lazy way out of installing the proper bar for a secure connection of all grounds.
I do to David. The pigtail had me stumped though.
There was a similar question on one of the BBs I watch about bundled neutrals on an isolated bus bar in a J box for a panel swap. The cludge was fed by a white insulated wire sized to 250.66 for the panel and nobody could really point to the exact violation (if there was one).
The grounds were done the same way with only the phases extended to the panel. |
( as it stands now ) as long as the connection ( wirenut in this case ) is designed to handle the number of EGC's being terminated ( which I dont think this one is... ) it can connect the EGC's....you would need to run the bonding jumper to the buss bar sized to cover the largest EGC in the splice.
The problem here is that it is a 110.3(B) violation with this wirenut, it risks improper installation, pulling off and the poor connection of an effective fault current path to the source.......which is why we properly terminate in the first place. Paul W. Abernathy |
I appreciate the clarification Paul. Thanks -