Default Ground Bundle Pigtail

Saw this one today - fairly new service panel, several egc's were bundled, then pigtailed to a bus. The bundle seems wrong and the size of the pigtail definitely seems wrong (too small -16awg). The local Electrical Inspector passed it so I'm not going to shovel sand against the tide. Just wondering what you think.
Attached Thumbnails
ground-bundle-pigtail-grnd-bundle.jpg   ground-bundle-pigtail-bundle-cond.jpg  



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #2  
Old 6/14/07, 6:02 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ground Bundle Pigtail

I'm sorta stumped on this one. I wouldn't do that myself, but I think it's legal as well. If I ran 10 circuits into a junction box, for instance, I only need one ground that is rated for the single biggest circuit in that box. If this was a bundle of all 16 ga. reduced grounds, one pigtail to the bar is probably legal. I forget if the QO ground bars are rated for a conductor that small, though. I don't have one handy here at home to look at, but I'm thinking they're only rated for a #14 as the smallest conductor.
Reply With Quote
  #3  
Old 6/14/07, 7:19 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ground Bundle Pigtail

I don't use Greenies myself, but I just happened to think I should look up their capacity:

#14 thru #10 AWG
Min. 2 #14
Max. 3 #12 w/ 1#14

They're not even rated for however many #16's they're holding in that picture. The second picture appears to show another big azz bundle in one ground bar hole. If that's the case, that's improper also.
Reply With Quote
  #4  
Old 6/15/07, 7:50 AM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,008
Default Re: Ground Bundle Pigtail

Thanks Marc-

The ground bundle in the second pic is actually the ground from the sec.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #5  
Old 6/15/07, 10:02 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Ground Bundle Pigtail

I write up all twisted/capped grounds. That's simply a lazy way out of installing the proper bar for a secure connection of all grounds.
Reply With Quote
  #6  
Old 6/15/07, 11:59 AM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,008
Default Re: Ground Bundle Pigtail

I do to David. The pigtail had me stumped though.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #7  
Old 6/17/07, 2:18 AM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Ground Bundle Pigtail

Quote:
Originally Posted by dvalley
I write up all twisted/capped grounds. That's simply a lazy way out of installing the proper bar for a secure connection of all grounds.
It does seem lazy, but is it wrong? I never see it in my area, but it sure seems like it could be done within the requirements of the NEC.
Reply With Quote
  #8  
Old 6/17/07, 4:48 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ground Bundle Pigtail

There was a similar question on one of the BBs I watch about bundled neutrals on an isolated bus bar in a J box for a panel swap. The cludge was fed by a white insulated wire sized to 250.66 for the panel and nobody could really point to the exact violation (if there was one).
The grounds were done the same way with only the phases extended to the panel.
Reply With Quote
  #9  
Old 6/18/07, 9:36 AM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,008
Default Re: Ground Bundle Pigtail

Quote:
It does seem lazy, but is it wrong? I never see it in my area, but it sure seems like it could be done within the requirements of the NEC.
EGCs in sub panels should be on their own bus (384-20) but I can't find anything about ground bundles in service panels.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #10  
Old 6/18/07, 10:35 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Ground Bundle Pigtail

( as it stands now ) as long as the connection ( wirenut in this case ) is designed to handle the number of EGC's being terminated ( which I dont think this one is... ) it can connect the EGC's....you would need to run the bonding jumper to the buss bar sized to cover the largest EGC in the splice.

The problem here is that it is a 110.3(B) violation with this wirenut, it risks improper installation, pulling off and the poor connection of an effective fault current path to the source.......which is why we properly terminate in the first place.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #11  
Old 6/18/07, 10:49 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: Ground Bundle Pigtail

Quote:
Originally Posted by pabernathy
( as it stands now ) as long as the connection ( wirenut in this case ) is designed to handle the number of EGC's being terminated ( which I dont think this one is... ) it can connect the EGC's....you would need to run the bonding jumper to the buss bar sized to cover the largest EGC in the splice.

The problem here is that it is a 110.3(B) violation with this wirenut, it risks improper installation, pulling off and the poor connection of an effective fault current path to the source.......which is why we properly terminate in the first place.
Thank you, Paul.
Reply With Quote
  #12  
Old 6/18/07, 5:04 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,008
Default Re: Ground Bundle Pigtail

I appreciate the clarification Paul. Thanks -



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 12:39 PM
Two ground wires jlybolt Electrical Inspections 8 8/10/06 3:06 PM
Harmonized Ground Fault Circuit Interrupters jtedesco1 Electrical Inspections 5 3/21/06 9:48 AM