Default Ground not bonded to neutral in main panel?

First pic shows main panel (CH 125 amp). BTW, the electrical panels were recently updated and both were very neat, proper, and professionally done (the garage distribution panel was even wired correctly!). The second pic shows the bonding strap which is not connected to the ground bus bar. The third pic shows the bonded neutral bus bar with the strap/green screw. Now my question, am I missing something obvious here? The ground needs to be connected/bonded to the neutral, no?
It just seems to me, the way these were both professionally done recently, that this seems to be too obvious (it even appears that the strap was "pulled away" from the grounded bus bar a bit). Additionally, don't these panels come connected (neutals & grounds strapped), and then installer adds bonding screw at time of install?

Any help/insight is always appreciated!
Attached Thumbnails
ground-not-bonded-neutral-main-panel-903-north-lane-defiance-064.jpg   ground-not-bonded-neutral-main-panel-903-north-lane-defiance-061.jpg   ground-not-bonded-neutral-main-panel-903-north-lane-defiance-063.jpg  
Reply With Quote
Find an InterNACHI certified Colorado Home Inspector (and anywhere else in North America)
  #2  
Old 10/6/09, 9:21 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Ground not bonded to neutral in main panel?

Yes. The grounding terminal-bus needs to be bonded to the enclosure by attaching it to the bonding strap.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 10/11/09, 10:49 PM
tmcsweeney tmcsweeney is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Buffalo, NY
Posts: 28
Default Re: Ground not bonded to neutral in main panel?

main panel should have the grounding bar bonded to the panel. Both ground and neutral wires maybe connected to this bar. On a sub panel the neutral wire bar should be insulated from the panel.
Reply With Quote
  #4  
Old 10/12/09, 12:39 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Ground not bonded to neutral in main panel?

Quote:
Originally Posted by tmcsweeney View Post
main panel should have the grounding bar bonded to the panel.
All panels must have the grounding bus bonded to the enclosure. In the service equipment, the neutrals must be bonded as well.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 10/12/09, 6:46 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Ground not bonded to neutral in main panel?

What he said ! This appears to be one of the most difficult for H.Is to grasp.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Twisted ground wires in main panel kmalone Electrical Inspections 10 12/8/08 9:06 PM
new ground bar kit Mike Kasper Electrical Inspections 12 12/1/08 11:12 PM
Electricians Check List pabernathy Electrical Inspections 74 12/5/07 7:39 PM
Main Panel Ground dnasser Electrical Inspections 10 12/2/07 5:31 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 5:33 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts