There is a bar connecting the ground and nuetral busses. The busses should not be tied together at this particular (sub) panel. Does this bar come out or is there some other was to separate them?
Thanks in advance. ![]()
|
| Find an InterNACHI certified Kansas Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
The bar is removable.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
||||
|
||||
|
Please Note:
rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thank you Proffessor Pope!
I figured it was removeable. |
|
#4
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
You just need to loosen the buss screw and then the screw thru the jumper and into the enclosure. The jumper is slotted to allow its removal from the bar.
|
|
#5
|
|||
|
|||
|
I still see a technical code violation in the first image.....anyone know...
Check out 408.41 ( Easy Fix ) Paul W. Abernathy |
|
#6
|
|||
|
|||
|
Paul,
Is neutral and ground allowed to have more than 1 wire per lug ? |
|
#7
|
|||
|
|||
|
Quote:
408.41 Grounded Conductor Terminations. Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor. InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
|
#8
|
|||
|
|||
|
Please Note:
kluce is a non-member guest and is in no way affiliated with InterNACHI or its members.
No and Yes. The neutral wires need to be separated while 2 wires under one connection is allowed.
|
|
#9
|
|||
|
|||
|
Please Note:
kluce is a non-member guest and is in no way affiliated with InterNACHI or its members.
I did an inspection on a new construction yesterday and found the tie bar not removed in the Auxiliary panel. I took a look at some of the units that weren't done yet and seen the same thing. Ooops.
The plumber really screwed up by connecting the wrong water pipes to many of the fixtures. I seen hot water going into both toilets, Hot and cold reverse at many of the fixtures (kitchen and laundry tub was correct) and both showers producing nothing but hot water no matter where the handle was turned. He has some work ahead of him since this is a slab house and most of the pipes are in the cement floor. |
|
#10
|
||||
|
||||
|
You could always swap the lines at the water heater, and swich the lines at the sink. Problem solved!
Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#11
|
|||
|
|||
|
Quote:
Grounded " Neutral" Condutors - No and sometimes Yes....No in that under normal conditions like the one shown here NO. However, their is an exception which does not apply to this example but it does apply to some conditions. 408.41 Grounded Conductor Terminations. Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor. Exception: Grounded conductors of circuits with parallel conductors shall be permitted to terminate in a single terminal if the terminal is identified for connection of more than one conductor. Paul W. Abernathy |
![]() |