Default Ground Rod

This a re-bar ground inside. It should be copper, right? This house was built in 2008. There is a ground wire on the water line.


Thanks!
Attached Thumbnails
ground-rod-100_1903.jpg  
Reply With Quote
Find an InterNACHI certified Washington Home Inspector (and anywhere else in North America)
  #2  
Old 4/29/09, 7:34 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Ground Rod

Ufer Ground

http://www.aps.com/files/_files/pdf/ESPServices/700.pdf (see page 3)



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #3  
Old 4/29/09, 8:29 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,531
Default Re: Ground Rod

Thanks! That is the first one have seen in the Kansas City area.
Reply With Quote
  #4  
Old 5/3/09, 12:15 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Ground Rod

Just to use this as an educational tool......which I am sure many of you are aware of but here it goes anyway.

Sometimes I get asked how come they dont see a "ground rod" in a home that has a water pipe ground?

I explain to them that ( and lets use this image as an example ) the National Electrical Code says that you must ground the electrical system and in doing so the dwelling happens to have a metal water pipe underground 10' or more in length in contact with the soil so they connect it via a listed and labeled clamp a point within 5' of the point of entry into the structure.......ok.......so like in this image why no ground rod?

Lets look at what 250.50 says :

III. Grounding Electrode System and Grounding
Electrode Conductor
250.50 Grounding Electrode System. All grounding electrodes
as described in 250.52(A)(1) through (A)(7) that are
present at each building or structure served shall be bonded
together to form the grounding electrode system. Where
none of these grounding electrodes exist, one or more of
the grounding electrodes specified in 250.52(A)(4) through
(A)[8] shall be installed and used.

Exception: Concrete-encased electrodes of existing buildings
or structures shall not be required to be part of the grounding
electrode system where the steel reinforcing bars or rods are
not accessible for use without disturbing the concrete.

Now it says we can use one of the ones present in 250.52(A)(1) - (A)(7) right.
so as we see from the original posters information that 250.52(A)(1) does exist as
that is the water pipe ground and we happen to also see 250.52(A)(3) exists also
which is the concrete encased electrode......so why no ground rod?

Thats an easy one...lets look at what 250.53(D)(2) says....


(2) Supplemental Electrode Required.
A metal underground
water pipe shall be supplemented by an additional
electrode of a type specified in 250.52(A)(2) through
(A)[8]. Where the supplemental electrode is a rod, pipe, or
plate type, it shall comply with 250.56. The supplemental
electrode shall be permitted to be bonded to the grounding
electrode conductor, the grounded service-entrance conductor,
the nonflexible grounded service raceway, or any
grounded service enclosure.
Exception: The supplemental electrode shall be permitted
to be bonded to the interior metal water piping at any
convenient point as covered in 250.52(A)(1), Exception.

OK..so you can see 250.52(A)(3) is indeed present and meets the supplilmental
requirement of 250.53(D)(2) so no ground rods would be needed.......

we can expand on this if anyone has any questions...........




Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Hey Electricians... Can you help by proofing this new course? gromicko Electrical Inspections 69 10/15/08 7:14 AM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 10:24 AM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 12:39 PM
Harmonized Ground Fault Circuit Interrupters jtedesco1 Electrical Inspections 5 3/21/06 9:48 AM


All times are GMT -4. The time now is 2:09 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts