This a re-bar ground inside. It should be copper, right? This house was built in 2008. There is a ground wire on the water line.
Thanks! |
| Find an InterNACHI certified California Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#3
|
||||
|
||||
|
Thanks! That is the first one have seen in the Kansas City area.
|
|
#4
|
|||
|
|||
|
Just to use this as an educational tool......which I am sure many of you are aware of but here it goes anyway.
Sometimes I get asked how come they dont see a "ground rod" in a home that has a water pipe ground? I explain to them that ( and lets use this image as an example ) the National Electrical Code says that you must ground the electrical system and in doing so the dwelling happens to have a metal water pipe underground 10' or more in length in contact with the soil so they connect it via a listed and labeled clamp a point within 5' of the point of entry into the structure.......ok.......so like in this image why no ground rod? Lets look at what 250.50 says : III. Grounding Electrode System and Grounding Electrode Conductor 250.50 Grounding Electrode System. All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system. Where none of these grounding electrodes exist, one or more of the grounding electrodes specified in 250.52(A)(4) through (A)[8] shall be installed and used. Exception: Concrete-encased electrodes of existing buildings or structures shall not be required to be part of the grounding electrode system where the steel reinforcing bars or rods are not accessible for use without disturbing the concrete. Now it says we can use one of the ones present in 250.52(A)(1) - (A)(7) right. so as we see from the original posters information that 250.52(A)(1) does exist as that is the water pipe ground and we happen to also see 250.52(A)(3) exists also which is the concrete encased electrode......so why no ground rod? Thats an easy one...lets look at what 250.53(D)(2) says.... (2) Supplemental Electrode Required. A metal underground water pipe shall be supplemented by an additional electrode of a type specified in 250.52(A)(2) through (A)[8]. Where the supplemental electrode is a rod, pipe, or plate type, it shall comply with 250.56. The supplemental electrode shall be permitted to be bonded to the grounding electrode conductor, the grounded service-entrance conductor, the nonflexible grounded service raceway, or any grounded service enclosure. Exception: The supplemental electrode shall be permitted to be bonded to the interior metal water piping at any convenient point as covered in 250.52(A)(1), Exception. OK..so you can see 250.52(A)(3) is indeed present and meets the supplilmental requirement of 250.53(D)(2) so no ground rods would be needed....... we can expand on this if anyone has any questions........... Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Hey Electricians... Can you help by proofing this new course? | gromicko | Electrical Inspections | 69 | 10/15/08 6:14 AM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |
| Ground Wires Inside a Panel | mveitenhans | Electrical Inspections | 13 | 10/29/06 11:39 AM |
| Harmonized Ground Fault Circuit Interrupters | jtedesco1 | Electrical Inspections | 5 | 3/21/06 8:48 AM |