Default Ground rod clamp

This ground rod clamp does not look right to me. It looks like the lower portion is backwards. What do you guys think?
Attached Images
File Type: jpg HPIM4836.jpga.jpg (185.0 KB, 98 views)
Reply With Quote
  #2  
Old 11/11/08, 8:07 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,891
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ground rod clamp

Actually, it's the upper clamp that's backwards. You flip it the way the topmost clamp is for pipes over a certain diameter, and you flip the way the bottom clamp is for rods and rebar. That top clamp doesn't look like it bottomed out, so it's probably tight and okay anyhow.
Reply With Quote
  #3  
Old 11/11/08, 8:27 PM
Kenneth R. Malone Kenneth R. Malone is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Sycamore, IL
Posts: 54
Kenneth R. Malone has had a little positive feedback
Default Re: Ground rod clamp

This has two ground rods. The other one the screw was not fastened and both of them are loose. Thanks for the info about the clamps. Ken
Reply With Quote
  #4  
Old 11/11/08, 8:47 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 4,191
Larry D. Kage .
Default Re: Ground rod clamp

Is that in conduit? Is there a reason for that?



"An Education, not just an Inspection"


Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525



Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #5  
Old 11/11/08, 10:39 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,891
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ground rod clamp

Quote:
Originally Posted by lkage View Post
Is that in conduit? Is there a reason for that?
Yes, to fulfill a code requirement. The code says that #4 copper is the smallest you can run when subject to physical damage. If the installer runs #6 in a place like that (all the bigger you're required to a rod), he needs to add some form of mechanical protection. In this case, he chose EMT. Note the use of a special ground rod clamp to receive the EMT connector, which also fulfills a code requirement that any metallic conduit used to protect a grounded electrode by "shorted" to the ground wire at each end. This trick connector meets that requirement at the rod end.

I just run #4 and forget about all that conduit mess.
Reply With Quote
  #6  
Old 11/12/08, 2:00 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 4,191
Larry D. Kage .
Default Re: Ground rod clamp

Quote:
Originally Posted by Marc D. Shunk View Post
Yes, to fulfill a code requirement. The code says that #4 copper is the smallest you can run when subject to physical damage. If the installer runs #6 in a place like that (all the bigger you're required to a rod), he needs to add some form of mechanical protection. In this case, he chose EMT. Note the use of a special ground rod clamp to receive the EMT connector, which also fulfills a code requirement that any metallic conduit used to protect a grounded electrode by "shorted" to the ground wire at each end. This trick connector meets that requirement at the rod end.

I just run #4 and forget about all that conduit mess.
Thanks Marc. I appreciate the lesson.



"An Education, not just an Inspection"


Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525



Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #7  
Old 11/12/08, 8:03 PM
Jim Port Jim Port is offline
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 131
Jim Port has had a little positive feedback
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ground rod clamp

Unless that rod is longer than 8 foot it does not satisfy the reuirement for 8 foot to be in direct contact with the earth. This would reuire the top to be driven flush or below the surface if an 8 foot rod is used.
Reply With Quote
  #8  
Old 11/12/08, 9:14 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,891
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ground rod clamp

Quote:
Originally Posted by Jim Port View Post
Unless that rod is longer than 8 foot it does not satisfy the reuirement for 8 foot to be in direct contact with the earth. This would reuire the top to be driven flush or below the surface if an 8 foot rod is used.
You're right, but while this is a technical code requirement, most people are smart enough to know that if it's 7' 10" or 8' in the ground, functionally it's probably just about the same. I'd sure never get into a pissing match over a few inches of rod.
Reply With Quote
  #9  
Old 11/12/08, 11:12 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is online now
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 2,886
Joe Farsetta has a reputation beyond repute Joe Farsetta has a reputation beyond repute Joe Farsetta has a reputation beyond repute Joe Farsetta has a reputation beyond repute Joe Farsetta has a reputation beyond repute Joe Farsetta has a reputation beyond repute Joe Farsetta has a reputation beyond repute Joe Farsetta has a reputation beyond repute Joe Farsetta has a reputation beyond repute Joe Farsetta has a reputation beyond repute Joe Farsetta has a reputation beyond repute
Default Re: Ground rod clamp

With new construction in my area, many electricians throw the ground rod into the footing trench prior to foundation backfill. I never get to see tha actual mechanical bond or ground rod.
Reply With Quote
  #10  
Old 11/12/08, 11:41 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,932
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Ground rod clamp

(B) Securing and Protection Against Physical Damage.
Where exposed, a grounding electrode conductor or its enclosure
shall be securely fastened to the surface on which it is
carried. A 4 AWG or larger copper or aluminum grounding
electrode conductor shall be protected where exposed to
physical damage. A 6 AWG grounding electrode conductor
that is free from exposure to physical damage shall be permitted
to be run along the surface of the building construction
without metal covering or protection where it is securely fastened
to the construction; otherwise, it shall be in rigid metal
conduit, intermediate metal conduit, rigid nonmetallic conduit,
electrical metallic tubing, or cable armor. Grounding electrode
conductors smaller than 6 AWG shall be in rigid metal conduit,
intermediate metal conduit, rigid nonmetallic conduit,
electrical metallic tubing, or cable armor.

Note: Is that AL coming out of that conduit? and that clamp is not designed to be installed the way the lower clamp is actually installed. I am not talking about the attachment to the Rod...marc is 100% correct but I dont think the connection from the end of conduit clamp to the clamp itself is actually designed to be done that way...but I could be wrong as I have never used one that way.



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.

Last edited by pabernathy; 11/12/08 at 11:47 PM.
Reply With Quote
  #11  
Old 11/12/08, 11:42 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,932
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Ground rod clamp

Quote:
Originally Posted by Marc D. Shunk View Post
I'd sure never get into a pissing match over a few inches of rod.
No Comment !



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Hey Electricians... Can you help by proofing this new course? gromicko Electrical 69 10/15/08 7:14 AM
Does the ground wire need a clamp? jkogel Electrical 7 10/9/08 6:30 AM
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
What's this video worth? jtedesco1 Education 5 4/18/08 10:24 AM
Harmonized Ground Fault Circuit Interrupters jtedesco1 Electrical 5 3/21/06 9:48 AM


All times are GMT -4. The time now is 8:08 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics