One more time please. When and under what circumstances is an additional ground rod required on a separate building such as a detached garage with sub-panel.
|
|
#2
|
||||
|
||||
|
Simple version = Each building requires its own GEC if it has an electrical panel. 250.32(A)
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
|||
|
|||
|
Jeff, thanks for the quick reply. Are you saying that anytime you have a separate building with an electrical panel that a ground rod is required irregardless whether its a three or four wire feed.
|
|
#4
|
||||
|
||||
|
Basically, yes.
Here is the code reference. . . Quote:
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
|||
|
|||
|
Thanks Jeff, thats what I needed.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Stupid ASHI legislatin in Washington DEAD. | gromicko | Legislation, Licensing & Legal Issues for Inspectors | 20 | 1/29/08 9:05 AM |
| Article on Commercial and Residential Inspections and Assessment | mcyr | Commercial Inspections | 2 | 8/6/07 1:26 AM |
| PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. | gromicko | Miscellaneous Discussion for Inspectors | 53 | 8/30/06 5:58 PM |