Default Ground rod at separate building?

One more time please. When and under what circumstances is an additional ground rod required on a separate building such as a detached garage with sub-panel.
Reply With Quote
  #2  
Old 1/23/06, 10:51 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Ground rod at separate building?

Simple version = Each building requires its own GEC if it has an electrical panel. 250.32(A)



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 1/23/06, 10:55 AM
Mike Pettitt Mike Pettitt is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Crystal River, FL
Posts: 75
Default Re: Ground rod at separate building?

Jeff, thanks for the quick reply. Are you saying that anytime you have a separate building with an electrical panel that a ground rod is required irregardless whether its a three or four wire feed.
Reply With Quote
  #4  
Old 1/23/06, 11:24 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Ground rod at separate building?

Basically, yes.

Here is the code reference. . .

Quote:
Where two or more buildings or structures are supplied from a common ac service by a feeder(s) or branch circuit(s), the grounding electrode(s) required in Part III of this article at each building or structure shall be connected in the manner specified in 250.32(B) or (C). Where there are no existing grounding electrodes, the grounding electrode(s) required in Part III of this article shall be installed.
Quote:
Exception: A grounding electrode at a separate building or structure shall not be required where only one branch circuit supplies the building or structure and the branch circuit includes an equipment grounding conductor for grounding the conductive non-current-carrying parts of all equipment.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 1/23/06, 11:28 AM
Mike Pettitt Mike Pettitt is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Crystal River, FL
Posts: 75
Default Re: Ground rod at separate building?

Thanks Jeff, thats what I needed.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Stupid ASHI legislatin in Washington DEAD. gromicko Legislation, Licensing & Legal Issues for Inspectors 20 1/29/08 9:05 AM
Article on Commercial and Residential Inspections and Assessment mcyr Commercial Inspections 2 8/6/07 1:26 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM


All times are GMT -4. The time now is 3:08 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts