Question Ground Wires Inside a Panel

Inspected a main service panel where whoever wired the panel had "saved space" by pigtailing three branch circuit ground wires together inside the panel so each pigtailed bunch could be connected to the neutral/ground bar via one ground wire. The result was that several ground wires were connected under a single screw (okay), but each of those single wires was connected to a bundle of at least three other ground wires inside the panel. This bundling of ground wires appeared to have been done so there would be enough connector screws -- every screw on the neutral/ground bar was occupied, either by a single neutral wire or multiple ground wires.

Is it okay to pigtail branch circuit ground wires inside a panel so multiple circuits are grounded to the neutral/ground bar by a single wire?
Reply With Quote
  #2  
Old 10/27/06, 12:27 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ground Wires Inside a Panel

How were they spliced?
Reply With Quote
  #3  
Old 10/27/06, 12:51 PM
Mike J. Veitenhans Mike J. Veitenhans is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Seattle, WA
Posts: 3
Default Re: Ground Wires Inside a Panel

One group of 3 pigtailed wires had a wire nut, another a barrel crimp.
Reply With Quote
  #4  
Old 10/27/06, 1:58 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Ground Wires Inside a Panel

Ok, not a code enforcement officier, so bare with me.

2005 NEC 250.122 (C) - Size of EGC's in Multiple Circuits.

Paraphrase: Allowed for raceway or cable, as long as the ECG is sized to the largest over current conductor.

Back To Your post: Was any groupings of mixed sized conductors, and was the final conductor the largest one, and sized for those circuits largest OCP?

In general, all electrical work must follow the manufactures instructions (2006 NEC 110.3(B), and must be a quality of work in that is neat and professional (2006 NEC 2006).

So for the $64k question, did it appear unsafe, and messy?

tom
Reply With Quote
  #5  
Old 10/27/06, 11:11 PM
Mike J. Veitenhans Mike J. Veitenhans is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Seattle, WA
Posts: 3
Default Re: Ground Wires Inside a Panel

Everything was 12 gauge wire and very neat.
Reply With Quote
  #6  
Old 10/27/06, 11:35 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Ground Wires Inside a Panel

I run into it a lot, "ECG abuse". Rather than installing a larger ground bar, some electricians install a large lug and cram like 5 ecg's under it. I've asked why, but I get "grey area" lingo, and it will pass the AHJ, so I stop asking.

Nice to see it's happening on the west coast as well.


later,

tom
Reply With Quote
  #7  
Old 10/27/06, 11:44 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ground Wires Inside a Panel

As long as the pigtail is as large as the largest grounding conductor in the bunch, there can be as many as the splicing device is listed for.
Reply With Quote
  #8  
Old 10/27/06, 11:50 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Ground Wires Inside a Panel

In the interest of a small error correction and clarity in posting.

EGC=Equipment Grounding conductor

ECG=ElectroCardioGram
Reply With Quote
  #9  
Old 10/27/06, 11:57 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Ground Wires Inside a Panel

Quote:
Originally Posted by mlarson
In the interest of a small error correction and clarity in posting.

EGC=Equipment Grounding conductor

ECG=ElectroCardioGram
Ha Ha, two posts, and I spell it two different ways. Good catch!

tom
Reply With Quote
  #10  
Old 10/28/06, 12:09 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Ground Wires Inside a Panel

Quote:
Originally Posted by tdietrich1
Ha Ha, two posts, and I spell it two different ways. Good catch!
tom
In a previous life I used to repair ECG equipment so it knda stuck out like a sore thumb for me.
Reply With Quote
  #11  
Old 10/28/06, 12:54 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Ground Wires Inside a Panel

Quote:
Originally Posted by tdietrich1
I run into it a lot, "ECG abuse". Rather than installing a larger ground bar, some electricians install a large lug and cram like 5 ecg's under it. I've asked why, but I get "grey area" lingo, and it will pass the AHJ, so I stop asking.

Nice to see it's happening on the west coast as well.


later,

tom
Tom,

Ok I am one of the Electricians out their that do not like the idea of EC's putting multiple EGC's under a single wirenut and running a single EGC to the lug.....in my mind ( without respect to CODE ) it is poor workmanship in my opinion.

I would prefer to see multiple wirenuts and splices within the panel with each individual EGC going to the terminal buss........regardless of what others will say....to me just POOR installations....WHY????

Because most all panels allow multiple EGC's under the same lug to the max allowed by the enclosure....in a normal 200A panel i have NEVER run out of space to do it properly......so.......some will say..but PAUL we are looking at old panels......SO......WHAT.....

NO EXCUSE for poor workmanship........WHY....are we SURE the old installation grouped these EGC's together and the 'pigtail" is sized correctly as previously listed.....we can't guarantee ANYTHING as people do the darndest things....so LOOK for it.......KEEP an eye on it.......

When i see bundling of the EGC's.....I see #10AWG's and #12 AWG's together....usually ecceeding the allowance of the wirenut anyway.......but then the pigtail is a # 14 AWG...........that would be an incorrect installation and worthy of MY REPORT.......

When it comes to electrical inspections....do not fall in to a laxed mode......while it seems some electricians around the country get upset when an HI puts some things in a report like Double Tapping........BUT as an electrician...I get paid to fix it.......it is simple but the HI is doing their JOB......

so NOT be swayed because you feel you will upset a local EC.....they can GET over it guys.......maintain the COURSE !

P.S....Tom cramming them into that LUG would increase the allowance of that LUG probably....as if the lug is allowing multiple wires....it will SAY SO......if it is old...do not assume it will.........if the HAIR on your neck sticks up...write it.....then defer it and let the EC field the question.......

Edit-Spelling......lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 10/28/06 at 5:24 PM..
Reply With Quote
  #12  
Old 10/28/06, 1:50 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Ground Wires Inside a Panel

Quote:
Originally Posted by pabernathy
if the HAIR on your neck sticks up...write it.....then defer it and let the EC field the question.......
Agreed.

tom
Reply With Quote
  #13  
Old 10/28/06, 7:54 PM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Ground Wires Inside a Panel

Hey Paul, as a EC, I love Home Inspectors, I get a lot of gravy work from them. Straightening out a DIY's mess pays real well.
Reply With Quote
  #14  
Old 10/29/06, 12:39 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Ground Wires Inside a Panel

Steve,

we are of like minds then.....great minds think alike....but I am sure you have heard the stories of electricians having fits with HI's.....i think it is just due to a lack of understanding is all.

When a house is built the electrician may go in their one time.....YET a HI will probably ( we hope ) go in many times through its sales life....those additional eyes are sooooooo valuable......



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 10:02 PM
Two ground wires jlybolt Electrical Inspections 8 8/10/06 3:06 PM
4 ground wires into 1 in main panel psiposs Electrical Inspections 13 5/18/06 2:27 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 2:01 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts