Default Grounding 101

Think the installer here passed this class? Ever took this class?
Attached Thumbnails
grounding-101-jacuzzi-ground.jpg  




Kevin Weiss

Professional Inspector
Level I Infrared
www.AbsoluteInspections.net
www.homeinspectorsplanotx.com
www.homeinspectorsmckinney.com
Absolute Inspections, LLC
972-463-0887
Reply With Quote
  #2  
Old 3/3/09, 9:49 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: Grounding 101

Looks like a hot tub or something like

If cover is in place not much wrong

Electrical box should be properly mounted

Hard to tell if ground in on a copper pipe or not

If it is -- what else is wrong??

rlb
Reply With Quote
  #3  
Old 3/3/09, 9:52 PM
kweiss's Avatar
kweiss kweiss is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Rowlett, TX
Posts: 1,060
Default Re: Grounding 101

Ground wire is neatly run to the copper fitting below the cold water valve. Very nice. Notice anything about the supply line to the cold water line?




Kevin Weiss

Professional Inspector
Level I Infrared
www.AbsoluteInspections.net
www.homeinspectorsplanotx.com
www.homeinspectorsmckinney.com
Absolute Inspections, LLC
972-463-0887
Reply With Quote
  #4  
Old 3/3/09, 10:20 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Grounding 101

The wire is not for grounding purposes, it's for bonding purposes.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 3/3/09, 10:25 PM
kweiss's Avatar
kweiss kweiss is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Rowlett, TX
Posts: 1,060
Default Re: Grounding 101

Last time I checked PEX doesn't conduct. So bonding or grounding it is not accomplishing much when the supply line is a plastic PEX pipe instead of copper.




Kevin Weiss

Professional Inspector
Level I Infrared
www.AbsoluteInspections.net
www.homeinspectorsplanotx.com
www.homeinspectorsmckinney.com
Absolute Inspections, LLC
972-463-0887
Reply With Quote
  #6  
Old 3/3/09, 10:31 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Grounding 101

They were bonding the copper fitting...does that go to a faucet? If so, I wouldn't write it up.



Excellence in Inspections
Mike Boyett, TREC #7290
mikeb@capcityinspections.com
Capital City Inspections
Austin, Texas
(512) 577-2579

Company blog is: www.capcityinspections.com/blog
Reply With Quote
  #7  
Old 3/3/09, 10:35 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Grounding 101

This appears to be the bond for the metal peices of the spout and/or valves. It appears they are following the "letter of the code."

Take a look at NEC 680.74



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 3/4/09, 8:46 AM
kweiss's Avatar
kweiss kweiss is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Rowlett, TX
Posts: 1,060
Default Re: Grounding 101

Well I guess I stand corrected. This is the first time I have seen it like this. Normally, I see this run to an actual copper supply line or outside to a rod in the ground. Thanks




Kevin Weiss

Professional Inspector
Level I Infrared
www.AbsoluteInspections.net
www.homeinspectorsplanotx.com
www.homeinspectorsmckinney.com
Absolute Inspections, LLC
972-463-0887
Reply With Quote
  #9  
Old 3/4/09, 4:03 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Grounding 101

I can't think of a reason why a pump like this would have its own grounding electrode. The purpose of the lug is to bond the pump to all other components of the system that have the potential to become energized. It is not a "grounding" mechanism.

In other words, it's not meant to "ground" the pump directly, even though (in most cases) it does bond the pump to the grounding electrode of the home's electrical system.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 3/5/09, 8:58 PM
David P. OKeefe's Avatar
David P. OKeefe David P. OKeefe is offline
InterNACHI Member
 
Join Date: May 2008
Location: Delmar,, NY
Posts: 974
Default Re: Grounding 101

Shouldn't that be under GFCI protection?



David

InterNACHI #08051301
NYS Lic. #16000038229
NYS DEC Cert # T4865884
518-505-8305
HouseAbout Home Inspections
HouseAbout on Facebook
NY Capital Region Chapter InterNACHI


Reply With Quote
  #11  
Old 3/5/09, 9:05 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Grounding 101

Absolutely. But the GFCI protection can be located anywhere on the circuit, prior to the motor. It does not necessarily have to be directly on the receptacle shown in the picture.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 3/5/09, 9:19 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding 101

Quote:
Originally Posted by kweiss View Post
Well I guess I stand corrected. This is the first time I have seen it like this. Normally, I see this run to an actual copper supply line or outside to a rod in the ground. Thanks

Kevin,
If you see a Jacuzzi tub or a spa with the bonding conductor run to a ground rod driven just for the tub it would be a sure sign the installer is clueless about grounding and bonding.
Reply With Quote
  #13  
Old 3/5/09, 10:38 PM
Terry Clayton Terry Clayton is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Arnold, MO
Posts: 246
Default Re: Grounding 101

Normally you would find the GFCI located outside of the unit, makes it more convenient to rest. Jeff is right on the bonding conductor bonds all metal parts something often missed during installs.
Reply With Quote
  #14  
Old 3/7/09, 10:08 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding 101

680.74 Bonding.
All metal piping systems and all

grounded metal parts in contact with the circulating water
shall be bonded together using a solid copper bonding
jumper, insulated, covered, or bare, not smaller than 8
AWG. The bonding jumper shall be connected to the terminal
on the circulating pump motor that is intended for
this purpose. The bonding jumper shall not be required to
be connected to a double insulated circulating pump motor.
The 8 AWG or larger solid copper bonding jumper is required
for equipotential bonding in the area of the hydromasage
bathtub and shall not be required to be extended or
attached to any remote panelboard, service equipment, or
any electrode. [ROP 17-166, 17-168]


( Note: this is the ROC..I dont have my 2008 NEC Handy )


(B) Permissive Rules.


Permissive rules of this Code are

those that identify actions that are allowed but not required,
are normally used to describe options or alternative methods,
and are characterized by the use of the terms shall be
permitted or shall not be required.



BTW..the small metal portion on most of the tub faucets is not part of the circulation water so it would not require bonding



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Where is it written.... bgromicko General Inspection Discussion 21 1/19/08 9:02 PM


All times are GMT -4. The time now is 9:57 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts