Can you have a neutral, grounding conductor and a grounded conductor on the same lug? I know that there shouldn't be two or more neutrals together, but what about one grounded conductor and one neutral?
Attachment 20958 Thanks "I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison www.newbeginningshomeinspection.com Last edited by nbhi; 7/8/08 at 8:41 AM.. |
|
#2
|
||||
|
||||
|
Each grounded conductor(neutral) needs to terminate under it's own screw.
From Mike Holt's site: Illustrated Changes to the NEC® Article 408 (384 in 1999 NEC) Switchboards and Panelboards All Content Copyright ©2008 Mike Holt Enterprises, Inc. 3604 Parkway Blvd Suite 3 Leesburg, FL 34748 Phone: 352 360 2620 [ M-F 8:30AM to 5:30PM EST ]
You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#3
|
|||
|
|||
|
Please Note:
jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
It is generally way wrong to have grounds and neutrals on the same bus, let alone the same screw. Do you want grounds to be energized with the neutrals when you use the circuit?
|
|
#4
|
||||
|
||||
|
I love when people spout out stuff.
When you drive a ground rod, and connect it back to the electrical panel, which bar would it be connected to? The Neutral bar, or the Ground Bar(if installed)? |
|
#5
|
||||
|
||||
|
It is generally way wrong to have grounds and neutrals on the same bus
Only when the panel is downstream from the main panel (the neutral bar should be separate and floating) or if the neutral and ground are bonded at the meter. |
|
#6
|
|||
|
|||
|
Please Note:
jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#7
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I can only assume it is this way in Canada as well. |
|
#8
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Yes, the neutral or ground bar. |
|
#9
|
||||
|
||||
|
Quote:
thx for playing along. |
|
#10
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
The bottom line is in the main panel the neutral bar gets bonded. Typically it is via a green screw. Any add-on bars mounted to the panel back box are ground bars ONLY. |
|
#11
|
|||
|
|||
|
Please Note:
jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
OK, Gary's picture appears to show the branch circuit neutral bus i believe with what appear to be grounding conductors double tapped with the neutral wires. Because this is a confusing subject, it may help if someone with authority could clarify that this is simply wrong?
|
|
#12
|
||||
|
||||
|
Quote:
Richard W. Washington, owner RW Home Inspections, Inc. www.RWHOMEINSPECTIONS.com Texas Real Estate Commission (TREC) Professional Inspector License #7238 Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter InterNACHI member since 2004 Based in Katy, serving Houston and all surrounding communities |
|
#13
|
||||
|
||||
|
Quote:
You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#14
|
||||
|
||||
|
What might be confusing on that picture to some people are the colors being used. On the ground bar, they are using a green wire and a bare copper wire. Those may be doubled up.
Green (Grounding conductor or Ground) Copper (Grounding conductor or Ground) White (Grounded conductor or neutral) |
|
#15
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
You can add grey to the "Grounded conductor or neutral" category. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| What do you think? Can this work for you? | jtedesco1 | Electrical Inspections | 21 | 2/26/11 2:00 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 9:24 AM |