Default Grounding again

Can you have a neutral, grounding conductor and a grounded conductor on the same lug? I know that there shouldn't be two or more neutrals together, but what about one grounded conductor and one neutral?

Attachment 20958

Thanks



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com

Last edited by nbhi; 7/8/08 at 8:41 AM..
Reply With Quote
  #2  
Old 5/6/08, 5:33 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Grounding again

Each grounded conductor(neutral) needs to terminate under it's own screw.

From Mike Holt's site:

Illustrated Changes to the NEC®
Article 408 (384 in 1999 NEC) Switchboards and Panelboards
All Content Copyright ©2008 Mike Holt Enterprises, Inc.
3604 Parkway Blvd Suite 3 Leesburg, FL 34748
Phone: 352 360 2620 [ M-F 8:30AM to 5:30PM EST ]




You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #3  
Old 5/6/08, 6:04 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding again

It is generally way wrong to have grounds and neutrals on the same bus, let alone the same screw. Do you want grounds to be energized with the neutrals when you use the circuit?
Reply With Quote
  #4  
Old 5/6/08, 6:08 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Grounding again

I love when people spout out stuff.

When you drive a ground rod, and connect it back to the electrical panel, which bar would it be connected to? The Neutral bar, or the Ground Bar(if installed)?

Reply With Quote
  #5  
Old 5/6/08, 9:59 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Grounding again

It is generally way wrong to have grounds and neutrals on the same bus

Only when the panel is downstream from the main panel (the neutral bar should be separate and floating) or if the neutral and ground are bonded at the meter.
Reply With Quote
  #6  
Old 5/6/08, 11:15 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding again

Quote:
Originally Posted by jwicklander
It is generally way wrong to have grounds and neutrals on the same bus

Only when the panel is downstream from the main panel (the neutral bar should be separate and floating) or if the neutral and ground are bonded at the meter.
Yes, sorry about that, we were talking branch circuits, i think. Around here it's a given that the neutral is bonded to ground at the meter and kept separate for the branch circuits downstream from there.
Reply With Quote
  #7  
Old 5/7/08, 6:55 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding again

Quote:
Originally Posted by jkogel
Yes, sorry about that, we were talking branch circuits, i think. Around here it's a given that the neutral is bonded to ground at the meter and kept separate for the branch circuits downstream from there.
The neutral is always bonded in the meter as well as the main panel/disconnect.
I can only assume it is this way in Canada as well.
Reply With Quote
  #8  
Old 5/7/08, 6:56 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding again

Quote:
Originally Posted by tdietrich1
I love when people spout out stuff.

When you drive a ground rod, and connect it back to the electrical panel, which bar would it be connected to? The Neutral bar, or the Ground Bar(if installed)?

If it is in the main panel (as it must be) the easy answer to your question is YES.
Yes, the neutral or ground bar.
Reply With Quote
  #9  
Old 5/7/08, 12:50 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Grounding again

Quote:
Originally Posted by Speedy Petey
If it is in the main panel (as it must be) the easy answer to your question is YES.
Yes the topic was the main panel. So the neutral bar gets the GEC and a bonding jumping goes to the ground bar.

thx for playing along.
Reply With Quote
  #10  
Old 5/7/08, 1:45 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding again

Quote:
Originally Posted by tdietrich1
Yes the topic was the main panel. So the neutral bar gets the GEC and a bonding jumping goes to the ground bar.
Not necessarily. The bonding jumper could be a screw, or bar, or strap. You do not need a jumper from bar to bar.

The bottom line is in the main panel the neutral bar gets bonded. Typically it is via a green screw.
Any add-on bars mounted to the panel back box are ground bars ONLY.
Reply With Quote
  #11  
Old 5/7/08, 1:54 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding again

OK, Gary's picture appears to show the branch circuit neutral bus i believe with what appear to be grounding conductors double tapped with the neutral wires. Because this is a confusing subject, it may help if someone with authority could clarify that this is simply wrong?
Reply With Quote
  #12  
Old 5/7/08, 4:18 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: Grounding again

Quote:
Originally Posted by nbhi
Can you have a neutral, grounding conductor and a grounded conductor on the same lug? I know that there shouldn't be two or more neutrals together, but what about one grounded conductor and one neutral?

Attachment 20958

Thanks
PLease clarify--is it ok for the grounded conductor and neutral conductor to be on the same bus? From Michaels code reference then the grounded conductor can be doubled just not the neutral?



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #13  
Old 5/7/08, 4:37 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Grounding again

Quote:
Originally Posted by rwashington
PLease clarify--is it ok for the grounded conductor and neutral conductor to be on the same bus? From Michaels code reference then the grounded conductor can be doubled just not the neutral?
I think you may be confusing terms. The "grounded conductor" is the Neutral.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #14  
Old 5/7/08, 6:37 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Grounding again

What might be confusing on that picture to some people are the colors being used. On the ground bar, they are using a green wire and a bare copper wire. Those may be doubled up.

Green (Grounding conductor or Ground)
Copper (Grounding conductor or Ground)
White (Grounded conductor or neutral)
Reply With Quote
  #15  
Old 5/7/08, 8:23 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding again

Quote:
Originally Posted by jwicklander
Green (Grounding conductor or Ground)
Copper (Grounding conductor or Ground)
White (Grounded conductor or neutral)
Exactly.

You can add grey to the "Grounded conductor or neutral" category.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What do you think? Can this work for you? jtedesco1 Electrical Inspections 21 2/26/11 2:00 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM


All times are GMT -4. The time now is 3:09 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts