Default Grounding & Grounded conductors together

Saw this panel the other day in house with the EGC and Grounding conductors under same lug. Had a friend there ( electrician ) and told him I was going to point that out in report. He said why? that's a very common practice he said. House was built in 2005, went home and pulled my panel cover off and my wires were also combined under one lug. I thought they had to be seperate and only EGC could be combined on Service Panel. My house was built in 1996, did codes change or is my panel wrong also. I'm confused ( again ) just looking for some feedback on the subject. Mark T
Attached Thumbnails
grounding-and-grounded-conductors-together-img_2838.jpg   grounding-and-grounded-conductors-together-img_2841.jpg  
Reply With Quote
Need a home inspection in Ohio? Check out InterNACHI's listing of Ohio certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/13/10, 12:51 AM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Grounding & Grounded conductors together

Article 408 (384 in 1999 NEC)
Switchboards and Panelboards
408.21 Grounded Conductor Terminations
Each grounded (neutral) conductor must terminate within the panelboard in an individual terminal that is not used for another conductor. Figure 408-2



408.21 Grounded Conductor Terminations Figure 408-3



408.21 Grounded Conductor Terminations Figure 408-4



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #3  
Old 2/14/10, 11:10 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding & Grounded conductors together

While this was commonly done it was incorrect. Before being adding to the NEC as a direct prohibition it was in the listing a labeling instructions of the panel. To prevent this confusion it was added to the Articles posted above by CC.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What do you think? Can this work for you? jtedesco1 Electrical Inspections 21 2/26/11 2:00 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Where is it written.... bgromicko General Inspection Discussion 21 1/19/08 9:02 PM


All times are GMT -4. The time now is 9:58 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts