Default Grounding or bonding??

The main disconnect is located in the basement. The distribution panel is on the second floor. Is the copper conductor that runs from the panel to the main disconnect a grounding conductor or a bonding jumper? Should it be #8 copper ? (like the GEC at the disconnect) or can is be smaller?



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #2  
Old 11/6/06, 1:07 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Grounding or bonding??

It sounds as if you are referring to the equipment grounding conductor (EGC) which would be sized according to the size of the OCPD or rated capacity of the remote panel.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 11/6/06, 1:21 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Grounding or bonding??

Thanks Jeff.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #4  
Old 11/6/06, 2:15 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding or bonding??

Table 250.122 in the NEC will assist in helping you size them correctly Bill......if you dont have a NEC.......always suggest them as a good investment...

Knowlegde is KING !







Paul W. Abernathy
Reply With Quote
  #5  
Old 11/6/06, 2:36 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Grounding or bonding??

Quote:
Knowlegde is KING !
and I am a peasant!!!!!



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Terminations of Grounding & Bonding Equipment pabernathy Electrical Inspections 24 12/6/07 5:56 PM
Demystify Grounding & Bonding Class pabernathy Inspection Education & Training 5 12/24/06 1:10 AM


All times are GMT -4. The time now is 3:09 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts