I found a grounding conductor clamped downstream of an isolation valve and pressure reducing valve on a copper plumbing supply. The plumbing supply continued outside to an exterior hose bib. I traced the grounding conductor and it went through the crawlspace foundation to a grounding electrode burried outside the front door of the house. I am assuming there is a splice to the service panel bond with the neutral in the wall. Any idea why this grounding conductor would be attached downstream on a copper supply plumbing? Why is it leading into the direction of a ground electrode buried in the dirt outside?
Attached Thumbnails
grounding-conductor-dsc01832.jpg  

Last edited by mnicholet; 5/4/08 at 8:48 PM..
Reply With Quote
  #2  
Old 5/4/08, 8:50 PM
rbrady's Avatar
rbrady rbrady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding conductor

Maybe the isolation valve and/or pressure reducing valve was breaking the electrical continuity of the pipe and somebody wanted to make sure the pipe was solidly bonded to ground.
Reply With Quote
  #3  
Old 5/4/08, 8:55 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding conductor

Maybe the dwelling has plastic water supplies to the dwelling and they are simply bonding the water line in compliance with 250.104 and has nothing to do with the grounding electrode system at all.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #4  
Old 5/4/08, 9:03 PM
mnicholet's Avatar
mnicholet mnicholet is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 542
Please Note: mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding conductor

Quote:
Originally Posted by pabernathy
Maybe the dwelling has plastic water supplies to the dwelling and they are simply bonding the water line in compliance with 250.104 and has nothing to do with the grounding electrode system at all.
Yes, the service water supply is plastic. I am not familiar with bonding the water line in compliance with 250.104. Do you know where I can get some information about it? Thanks.
Reply With Quote
  #5  
Old 5/4/08, 9:39 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding conductor

Quote:
Originally Posted by pabernathy
Maybe the dwelling has plastic water supplies to the dwelling and they are simply bonding the water line in compliance with 250.104 and has nothing to do with the grounding electrode system at all.
That is what it seems to me.
I see, and do, this every day. Only a small portion of the homes around here are on town water will metallic feed piping.
Reply With Quote
  #6  
Old 5/4/08, 9:49 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding conductor

Quote:
Originally Posted by mnicholet
Yes, the service water supply is plastic. I am not familiar with bonding the water line in compliance with 250.104. Do you know where I can get some information about it? Thanks.
If the water line coming in is plastic, and the home's pipework is metallic, you can bond the metallic pipework anyplace that pleases you most. It must be bonded, however, and catching it on the way out to the rods was apparently the easiest thing to do in that particular case.
Reply With Quote
  #7  
Old 5/5/08, 4:35 AM
gmortensen gmortensen is offline
New User
 
Join Date: Aug 2007
Location: Cambridge, ON
Posts: 94
Please Note: gmortensen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding conductor

This might be a better resource for you in BC:
http://www.csa-intl.org/onlinestore/...00000002418031
Reply With Quote
  #8  
Old 5/5/08, 7:14 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding conductor

250.104(A)(1) - ENJOY

(A) Metal Water Piping.
The metal water piping system
shall be bonded as required in (A)(1), (A)(2), or (A)(3) of
this section. The bonding jumper(s) shall be installed in
accordance with 250.64(A), (B), and (E). The points of
attachment of the bonding jumper(s) shall be accessible.

(1) General.
Metal water piping system(s) installed in or attached
to a building or structure shall be bonded to the service
equipment enclosure, the grounded conductor at the service,
the grounding electrode conductor where of sufficient size, or
to the one or more grounding electrodes used. The bonding
jumper(s) shall be sized in accordance with Table 250.66 except
as permitted in 250.104(A)(2) and (A)(3).



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #9  
Old 5/7/08, 6:41 PM
Mike W. Cole Mike W. Cole is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Hickory, NC
Posts: 65
Default Re: Grounding conductor

I had a electrician call me the other day over an inspection I did recently. Seems as if the supply from the street was plastic and the plumbing was mixed plastic, copper, galvanized. He asked me if I expected that he should ground each piece of metal piping. The meterbase had a ground rod by the way. I welcome comments
Reply With Quote
  #10  
Old 5/7/08, 9:25 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding conductor

Quote:
Metal water piping system(s) installed in or attached
to a building or structure shall be bonded to the service
equipment enclosure, the grounded conductor at the service,
the grounding electrode conductor where of sufficient size, or
to the one or more grounding electrodes used.
It is our/your/their job to determine just exactly what a piping "system" is.
IMO a few short sections of copper pipe do NOT a "system" make.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
What do you think? Can this work for you? jtedesco1 Electrical Inspections 21 2/26/11 3:00 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 10:24 AM
Where is it written.... bgromicko General Inspection Discussion 18 1/19/08 10:02 PM


All times are GMT -4. The time now is 10:09 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts