I found a grounding conductor clamped downstream of an isolation valve and pressure reducing valve on a copper plumbing supply. The plumbing supply continued outside to an exterior hose bib. I traced the grounding conductor and it went through the crawlspace foundation to a grounding electrode burried outside the front door of the house. I am assuming there is a splice to the service panel bond with the neutral in the wall. Any idea why this grounding conductor would be attached downstream on a copper supply plumbing? Why is it leading into the direction of a ground electrode buried in the dirt outside?
Last edited by mnicholet; 5/4/08 at 8:48 PM.. |
|
#2
|
||||
|
||||
|
Please Note:
rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Maybe the isolation valve and/or pressure reducing valve was breaking the electrical continuity of the pipe and somebody wanted to make sure the pipe was solidly bonded to ground.
|
|
#3
|
||||
|
||||
|
Maybe the dwelling has plastic water supplies to the dwelling and they are simply bonding the water line in compliance with 250.104 and has nothing to do with the grounding electrode system at all.
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#4
|
||||
|
||||
|
Please Note:
mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#5
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I see, and do, this every day. Only a small portion of the homes around here are on town water will metallic feed piping. |
|
#6
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#7
|
|||
|
|||
|
Please Note:
gmortensen is a non-member guest and is in no way affiliated with InterNACHI or its members.
This might be a better resource for you in BC:
http://www.csa-intl.org/onlinestore/...00000002418031 |
|
#8
|
||||
|
||||
|
250.104(A)(1) - ENJOY (A) Metal Water Piping. The metal water piping system shall be bonded as required in (A)(1), (A)(2), or (A)(3) of this section. The bonding jumper(s) shall be installed in accordance with 250.64(A), (B), and (E). The points of attachment of the bonding jumper(s) shall be accessible. (1) General. Metal water piping system(s) installed in or attached
to a building or structure shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or to the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with Table 250.66 except as permitted in 250.104(A)(2) and (A)(3). Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#9
|
|||
|
|||
|
I had a electrician call me the other day over an inspection I did recently. Seems as if the supply from the street was plastic and the plumbing was mixed plastic, copper, galvanized. He asked me if I expected that he should ground each piece of metal piping. The meterbase had a ground rod by the way. I welcome comments
|
|
#10
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
IMO a few short sections of copper pipe do NOT a "system" make. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 4:56 PM |
| What do you think? Can this work for you? | jtedesco1 | Electrical Inspections | 21 | 2/26/11 3:00 PM |
| What's this video worth? | jtedesco1 | Inspection Education & Training | 5 | 4/18/08 10:24 AM |
| Where is it written.... | bgromicko | General Inspection Discussion | 18 | 1/19/08 10:02 PM |