Default Grounding....this could make you mad

My home orginally had some 2 prong receptacles, and BX cable running throughout. I replaced the 2 prong receptacles with 3-prong receptacles on the assumption that they will be self-grounding (through the metal BX cover). Ground testing confirmed this.

Am I OK?
Reply With Quote
  #2  
Old 1/31/07, 3:02 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding....this could make you mad

No you are not OK...if you are truly talking about BX cable which was made by GE. It is not intended for use as a EGC .

And since we are talking about a house that DID only have (2) prong plugs in it I would venture to say you ARE talking about BX and again it was not intended for this purpose.

Sure it will read Cont. through it and make a tester show it is grounded but it is not a low impedance path nor does it have a reliable spiral connection without the bonding strip...as it has a tendency to NOT be really consistent in it's connection points.

I have been into basements ( I explain this story at my seminars ) about a basement that had this and the COIL of the BX through the rafters had gotten to the point it burnt into the holes and was one step from burning the house down....

Note: The bondings strip is NOT the EGC in AC cable....just want to make sure you are clear on that.....once it leaves the cable it serves no purpose.



Paul W. Abernathy

Last edited by pabernathy; 1/31/07 at 6:59 PM..
Reply With Quote
  #3  
Old 1/31/07, 3:13 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding....this could make you mad

Ian,

In my opinion you are better off going and buying some GFCI receptacles and replace the FIRST one in each circuit and label the others as required and then you can leave them (3) prong plugs.

Another solution is simply to buy GFCI breakers IF you have breakers and do it that way...but probably cheaper with the price of GFCI receptacles today to just replace the first one in each circuit and protect yourself that way.

Some may say...well Paul a little protection on that spiral BX is better than none.....NOT if it wont clear the fault or the resistance is so high it heats up or you get objectionable current on it with high resistance and becomes a potential problem down the road.



Paul W. Abernathy
Reply With Quote
  #4  
Old 1/31/07, 3:45 PM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,060
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding....this could make you mad

I have had local electricians use that exact fix in my area after calling out 2 prongers....seems to be the consensus.
Reply With Quote
  #5  
Old 1/31/07, 4:16 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding....this could make you mad

Which fix tony...the BX as a EGC or the GFCI replacement option?



Paul W. Abernathy
Reply With Quote
  #6  
Old 1/31/07, 5:11 PM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,060
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding....this could make you mad

Sorry..your fix of course
Reply With Quote
  #7  
Old 1/31/07, 5:22 PM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 199
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Grounding....this could make you mad

I have no idea what I am talking about, but to stimulate debate:

Concerning the replacement of 2-prong with 3-prong receptacles see the following link. Has NEC code references too (Note the table has 2002 NEC references, but the discussion below that table has 1999 NEC references). And it talks about upgrading a 2-prong outlet with the old style AC cable (BX trademark from GE, which does not have the currently required bonding wire/strip per 2002 NEC 320.100). 2002 NEC 250.146(B) does permit "self grounding" outlets without the wire ... I know it's not considered good practice by most sparkies ... but you are looking from an HI point of view here.

http://www.codecheck.com/250_50_commentary.html

Now, you're going to hit me.
Reply With Quote
  #8  
Old 1/31/07, 5:39 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding....this could make you mad

Ian,

Again I don't believe Code Check was written by Electricians...to be honest with you. I can only give you my opinion on what I know and BX casing is not a good choice for a EGC in my view.

Now Code check can say what it wants but where is their reference, just saying BX is ok does not make it OK. Personally I question many things I see sometimes written by Non-Electricians.

Would never hit ya fella......you may get an electrician or two to agree with you or even say...its the lessor of two evils as well...but I don't like the practice......every wonder WHY AC cable today as the bonding strip within it?????

I would venture to say the BX you are speaking of does not have a internal bonding strip...without it you have a higher inductive reactance in the spiral outer case.

AC cable in itself meets the EGC requirement IF the strip is inside the cable as 250.118 allows AC cable IF done in that manner as a EGC.



Paul W. Abernathy
Reply With Quote
  #9  
Old 1/31/07, 6:22 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,055
Default Re: Grounding....this could make you mad

Paul you need to come back out to Seattle for another road show. I missed the last one. Plus we can go egg Stephen Stanczyk's house while your out here, LOL.

If that dosnt get you back out here,.. I dont know what will,... Mexican food? =)



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681

Last edited by pdoane; 1/31/07 at 6:25 PM..
Reply With Quote
  #10  
Old 1/31/07, 6:27 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding....this could make you mad

Peter...I would LOVE to.....not sure if it will happen but would LOVE it



Paul W. Abernathy
Reply With Quote
  #11  
Old 1/31/07, 6:40 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Grounding....this could make you mad

Ian, don't guess. Verify you have BX(which I hate how it's an over used term), or actually AC.

If you can't tell the diff, you shouldn't be working with electricity, for your and your's safety.

tom
Reply With Quote
  #12  
Old 1/31/07, 6:42 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding....this could make you mad

Quote:
Originally Posted by pdoane
Paul you need to come back out to Seattle for another road show. I missed the last one. Plus we can go egg Stephen Stanczyk's house while your out here, LOL.

If that dosnt get you back out here,.. I dont know what will,... Mexican food? =)
lol...no the RiskWithoutReward policy is probably what will not get me back out their...lol

BUT I loved that Mexican Place right beside the hotel.....was AWESOME.....simply Awesome except Stephen promised BURGERS on the next trip...someday...



Paul W. Abernathy
Reply With Quote
  #13  
Old 1/31/07, 10:37 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding....this could make you mad

I agree Tom, real BX might be a collector's item. It has become a generic term for anything with spiral armor. BTW if you tested this with your SureTest I would be a lot more confident that it had a <1ohm grounding path which is the standard. The 3 neon tester ... not so much.
Reply With Quote
  #14  
Old 1/31/07, 11:00 PM
apolillo's Avatar
apolillo apolillo is offline
Active Poster
 
Join Date: Nov 2004
Location: Baltimore, Md
Posts: 191
Please Note: apolillo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding....this could make you mad

Paul,
What would cause the spiral cable to heat to the point of scorching?
Anatol
Reply With Quote
  #15  
Old 2/1/07, 8:51 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding....this could make you mad

ANATOL,

Could be current running on the spiral case due to a improper Neutral to Case connection, could be a fault running on the case that simply will not clear a fault. The metal material used in the making of BX (tradename for GE product) was simply not made for the use.

I don't even like the suggestion that it be used for an effective fault path with regards to BX cable of that time or period.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


LinkBacks (?)
LinkBack to this Thread: http://www.nachi.org/forum/f19/grounding-could-make-you-mad-12920/
Posted By For Type Date
Making a safer circuit i am told anyone of these do - Terry Love's Plumbing & Remodel DIY advice forum This thread Refback 10/12/08 1:15 AM

Similar Threads
Thread Thread Starter Forum Replies Last Post
Grounding Wire help.... gbrasseur Electrical Inspections 3 2/27/07 10:31 PM
Demystify Grounding & Bonding Class pabernathy Inspection Education & Training 5 12/24/06 1:10 AM
Soares Grounding And Bonding Seminar For Nachi Members jtedesco1 Electrical Inspections 7 10/19/06 2:58 PM


All times are GMT -4. The time now is 9:58 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts