Default Grounding Electrode


With this in mind. . .

250.24(A)(1) General.
The connection shall be made at any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means.

Scenario. . .

400 amp service with a single switch (disconnect) located at the exterior of the home.

Approx. 30 feet of continuous, 3 inch, RMC to the first distribution panel (three wire feed plus RMC). This distribution panel fed four additional panels down stream, plus a portion of the homes branch circuits.

The grounding electrode (ground rod) was attached to the grounding bus of the first distribution panel via (approx) 15 feet of cable and LFMC, with no connection (other than the RMC) back to the service equipment.

This was a "no-brainer" because the grounding bus was not bonded to the distribution panel, therefore, not bonded to the service eq.

Question. . .

If the bonding had been there, would this have been acceptable under the GE requirements of 250.24?

Attached Thumbnails
grounding-electrode-hpim7442.jpg   grounding-electrode-hpim7448.jpg   grounding-electrode-hpim7449.jpg   grounding-electrode-hpim7451.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #2  
Old 7/13/06, 3:05 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 834
Send a message via Skype™ to pbolliger
Default Re: Grounding Electrode

I read this:

"any accessible point from the load end of the service drop or service lateral "

As not "any point" on the service equipment but location (House wise) in relation to the "Main" service panel near the service entry point.

What your describing / showing is any point along the service equipment installation. I see this as problem. The difference in potential at the service panel with respect to any point down stream of the service panel could be enough to kill someone. I equate this to two GEC's not bonded 30 feet away.. What is the difference in potential there? Three wire feeds...

Also looks as if you have 3 phase power from that one picture..



Sure RMC but are we sure it's a continuous electrical path with least resistance (impedance)?

What is the deal with the grounding rod...I have the impression it is not copper skin but a plated deal corrosion special...


Where are the sparkies?? tick tock tick tock...

Reply With Quote
  #3  
Old 7/13/06, 4:09 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Grounding Electrode

It was a 3-wire system (via 6 conductors) plus the RMC, which is okay if done properly.

I questioned the distance (and method) from the service to the electrode and was hammered by the EC.

As far as I could tell, the rod was just painted.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #4  
Old 7/13/06, 4:39 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 834
Send a message via Skype™ to pbolliger
Default Re: Grounding Electrode

Jeff,

Can't tell you if this is or isn't acceptable. Don't know
Local AHJ thing??
I can tell you from what I see here that the GEC (RMC and wire)for example in my house alone is over 25 feet in length BUT this is Chicago where A GEC system is a cold (old) Galvanized steel pipe into soil.

I have seen even longer runs ... There is an issue with resistivity and diameter of a wire / conductor and rod itself so perhaps Paul , Greg, Joe, can elaborate on that .

R=rho x length/A rho for copper is 10.37 based on CM (circular Mils) /Foot @ Temp of 20deg Centi (77 deg F) A.K.A room temp

For example:
If you have a 3/0 for the GEC.

A 3/0 is 167,810 Circular mils... "A"

So lets take a 3/0 and say 15 feet length and you have:
rho (0.0618 ohms per 1000 feet) that gives you .0000618 per foot. So
15 times .0000618 =.000927 ohms... Not much Resistance / Impedance.

It depends on the AWG used I would think and the run..

My NERD side..
Reply With Quote
  #5  
Old 7/13/06, 5:09 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding Electrode

The "switch" was the service disconnect. That is the last place the GEC could be connected and that is where the main bonding jumper should be.
Reply With Quote
  #6  
Old 7/13/06, 5:26 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Grounding Electrode

Thanks Greg (you too Pat ). That's pretty much what I thought.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Demystify Grounding & Bonding Class pabernathy Education 5 12/24/06 2:10 AM
Electrical Inspection Training for Home Inspectors jtedesco1 Education 6 4/27/06 11:43 PM


All times are GMT -4. The time now is 7:20 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts