What's the difference? I have a copper 4AWG wire connected to the bonding jumper (green screw) inside a 200-amp panelboard. The wire is connected to a grounding rod (acorn and 8 feet). Is the wire a GEC or an EGC?

Equipment grounded conductors refer only to the copper grounding wires of the branch circuit wires?



BEN GROMICKO
InterNACHI Director of Education
"
Now That You've Had a Home Inspection" Book

Last edited by bgromicko; 2/4/08 at 11:58 AM..
Reply With Quote
  #2  
Old 2/4/08, 12:11 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: GEC and EGC

Ben,

It's actually quite easy to figure out.

A GEC is a grounding electrode conductor. It's that sole conductor between the ground rod or metal water pipe in direct contact with the earth serving as the required grounding electrode source to serve the building if in direct contact with the earth.

An EGC is an equipment grounding conductor which comes from the inside of a panel and is installed with a feeder or branch circuit.
Reply With Quote
  #3  
Old 2/4/08, 5:38 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: GEC and EGC

Ben,

To expand on Davids comments...remember this...the GEC is a function of connection to a grounding electrode(ie: Ground Rod,Ufer,Water Pipe,Ground Ring..etc.)......EGC should really be considered a bonding conductor.......

Typically if you see a 4 AWG in the panel...chances are it is for Water Pipe Electrode, Ufer possibly but remember Ground Rods usually are 6 AWG...and in some cases 8 AWG for a 100A service......but while a 4 AWG indeed can be used to a rod if they want....likely not.

Just remember if new construction chances are you will have plastic water lines coming in...so if you do and see a 4 AWG.....look for a Ufer then move down the list.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 9:58 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts