Default GEC question

Two service panels for each with its own meter. The gec comes into the panel on the left and lands on a bus bar. A second gec is tapped off of that bar and continues to the second panel. I've never seen this before - is it ok?
Attached Thumbnails
grounding-electrode-conductor-question-gec.jpg  



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #2  
Old 6/2/07, 11:19 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: GEC question

Edited.....I called ya.....I hope you are straight now...if you need anything else feel free to give me a call.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 6/2/07 at 11:34 AM..
Reply With Quote
  #3  
Old 6/2/07, 11:38 AM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,008
Default Re: GEC question

Thanks Paul - you are the best. I appreciate you taking the time to call and explain it.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #4  
Old 6/2/07, 12:14 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,842
Cool Re: GEC question

Quote:
Originally Posted by bsmith
Thanks Paul - you are the best. I appreciate you taking the time to call and explain it.
if you'd be so kind please explain to the rest of us



ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes accept the good
Reply With Quote
  #5  
Old 6/2/07, 12:17 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GEC question

Quote:
Originally Posted by badair
if you'd be so kind please explain to the rest of us
Barry... are you feeling left out that nobody will call you?

Answer your friggin phone, will ya?

This is super-secret electrician stuff, and we can't just go blurting it out for everyone.
Reply With Quote
  #6  
Old 6/2/07, 2:58 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GEC question

In my opinion that jumper should be removed. It is a parallel neutral path.
You only need to ground a service once, anywhere between the service point and the service disconnect.
Reply With Quote
  #7  
Old 6/2/07, 4:47 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: GEC question

Marc.....I choose to call him and explain the options and so on.

Edited...I just wont go there....

Anyway......just easier this morning to call as I was heading out.....plus you got 3 other electricians here who can explain it.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 6/2/07 at 4:52 PM..
Reply With Quote
  #8  
Old 6/2/07, 5:01 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GEC question

Quote:
Originally Posted by pabernathy
Marc.....I choose to call him and explain the options and so on.
Probably the best option in this case, because as you say, there are options. There is also some missing necessary information in the first post. It would have involved a long, drawn-out series of posts, with much code thrown in. That would have gotten ugly quickly from the people who want the quick easy answers and who also don't tolerate the technical content very kindly.
Reply With Quote
  #9  
Old 6/2/07, 5:10 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: GEC question

Anyway this issue is cleared up in the newer revision but what Greg is saying is correct....however, this is how it has been done for many years and it seems that many AHJ's still allow the practice.....thinking more in terms of bonding the enclosures together as opposed to it being an actual GEC...and then many say the TAP conditions onder the GEC requirements are then not in play.......

I think in the original question it was asked about the GEC and the allowance of the applications for the GEC to each disconnection means is growing with the 2008 revision...but here is a picture of a common way to do a tap on the GEC....

Electricians have been argueing over this very thing for many cycles....it was just easier to call bill.....than to do a long and drug out thing here...sorry as it was my choice and I made it......
Attached Thumbnails
grounding-electrode-conductor-question-dsc01722.jpg  



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #10  
Old 6/2/07, 5:49 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: GEC question

The more I got into this...why re-create the wheel......Barry...read this article and it will become crystal clear.....

http://ecmweb.com/mag/electric_grounding_vs_bonding_7/



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #11  
Old 6/2/07, 6:02 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: GEC question

I would not worry as much about that Parallel issue.....while the application is wrong you are going to have parallels in the water piping system as well if bonded properly and so on....anyway being in place in my opinion is better than not being there at all...or with the lack of a proper TAP method..

Check out the debate on it over at the HOLT site...you will see what I mean..

http://forums.mikeholt.com/archive/i...p/t-56612.html

Kinda a Lessor of TWO evils approach really....but in the end...just plain sloppy....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #12  
Old 6/2/07, 11:00 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GEC question

The code has softened it's stand on parallel paths on the line side of the main bonding jumper so this is really just a redundant connection. The point really is, you only have to ground a service once.
Reply With Quote
  #13  
Old 6/3/07, 11:09 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: GEC question

I remember the first time I went to put in a double meter-base on a two family house(one service drop). I drew it out to figure the least amount of copper and time. I had a spider web of copper planned. Then the master elec showed me something. The double meter base had a teeny-tiny lug on it, for 6awg on the 'neutral' bar. Life has simpler ever since.
Reply With Quote
  #14  
Old 6/3/07, 5:05 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: GEC question

Quote:
Originally Posted by Greg Fretwell
The code has softened it's stand on parallel paths on the line side of the main bonding jumper so this is really just a redundant connection. The point really is, you only have to ground a service once.
But the NEC continues to demand the methods for tapping the GEC in regards to multiple disconnection locations....Why soften it and then get redundant on the method and location of the connections Greg.

The nec is very clear on what methods are allowed to make that connection, if it is done at a gutter or at the meter can I can see no problem with a single grounding point...but if it is done at the panels inside we have to look at how the connections are made and if proper bonding is taking place....parallel paths on grounding and so on is being brushed aside for a better chance of clearing faults in making sure enclosures are tied together in more than a single location out at the meter or a gutter location..dont you think?



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #15  
Old 6/3/07, 11:01 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: GEC question

I really do not see a problem with multiple paths on the line side of the main bonding jumper.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sump Pit/Pump Question Joey D'Adamo Plumbing Inspections 4 11/26/08 2:04 PM
Interesting Question? jmckenna1 Miscellaneous Discussion for Inspectors 9 11/25/07 2:13 PM
WA State Legislative update hmiller Legislation, Licensing & Legal Issues for Inspectors 153 5/5/07 12:55 AM
Rule of Thumb A/C sizing question from Practice Exam gliebig Inspecting HVAC Systems 9 5/25/06 2:38 AM


All times are GMT -4. The time now is 5:03 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts