Is it acceptable to use the main gas line to use as a main ground?

The house is a 2002 built.

The home has plastic supply lines.

As you can see there was a ground at the main water line.

I personnaly would think you would have a better ground at the water line since it is 6feet instead of 3 feet for the gas.

Also home has no AFCI at the main box. Home was probably built before the 2002 code came out. Would you recommend as an improvement to add to the box?

One more question. What year was the code for the waterproof exterior covers. This one is missing and I would recommend installing.

Thanks

Last edited by dmacy; 4/25/08 at 10:41 AM..
Reply With Quote
  #2  
Old 3/13/06, 10:52 AM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding the gas line

David,
the Gas line is "bonded" to the water pipe "grounding" system----in addition there may have been ground rods as well.
Reply With Quote
  #3  
Old 3/13/06, 11:00 AM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: Grounding the gas line

There is the ground for the exterior ground rod. The gas ground is not for bonding. They are using for the water line ground.

Dave
Reply With Quote
  #4  
Old 3/13/06, 11:07 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Grounding the gas line

Quote:
Originally Posted by dmacy
Is it acceptable to use the main gas line to use as a main ground?
Absolutely not. But as Mr. Buell stated, it should be bonded.

Quote:
Originally Posted by dmacy
What year was the code for the waterproof exterior covers. This one is missing and I would recommend installing.
Weatherproof.

2005 NEC requires the "bubble" type cover at exterior receps. The type in your picture is the norm for many years previous.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 3/13/06 at 11:12 AM..
Reply With Quote
  #5  
Old 3/13/06, 11:08 AM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding the gas line

What do you mean the gas line ground is not for bonding?
Reply With Quote
  #6  
Old 3/13/06, 11:10 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding the gas line

NO, the Gas Piping should never be used as a Grounding Electrode. The requirement to connect to the gas piping comes into effect within the dwelling to areas likely to become energized....and in most cases this is taken care of by the equipment ground of the gas appliance but in most all areas the gas piping inside should be bonded to the system.....But most certainly NOT as the grounding electrode.

In this case I would suggest the owner drive an additional ground rod 6' from the first one and bond them together and complete their system if they are concerned.

As for the AFCI, It is something most certainly that can be suggested as it will save lives but is not something required for them to do....and i will let jeff finish on the other items.



Paul W. Abernathy

Last edited by pabernathy; 3/13/06 at 11:14 AM..
Reply With Quote
  #7  
Old 3/13/06, 11:27 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding the gas line

Here is a REFRESHER for you all....

http://www.nachi.org/forum/f19/bonding-piping-101-good-know-2272/



Paul W. Abernathy
Reply With Quote
  #8  
Old 3/13/06, 11:36 AM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: Grounding the gas line

I didnt think the ground at the main gas was right. Can the wire be removed from the gas and attached to the one by the meter?

There is about 8 feet to connect the two. Or does the wire need to be continuos?

About the bonding. Since the house has all plastic pipes. What is the best way to bond the gas pipe?

There was no bonding across the water tank. Being the plastic lineswould a bond still be required across the tank?

Thanks for all the responses.

Any tips to give to a new electrician. I am inspecting his house this afternoon. I better watch ans know what I say with the electrical.

Dave
Reply With Quote
  #9  
Old 3/13/06, 1:33 PM
lewens's Avatar
lewens lewens is offline
Active Poster
 
Join Date: Feb 2005
Location: Brantford, On
Posts: 774
Send a message via AIM to lewens
Please Note: lewens is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding the gas line

Jeff
Please explain to me how the bonding of the gas line to the plumbing is effective as most times a jumper from one side of the meter to the other is not present. Without the jumper the gas line is bonded to nothing. ????????
Larry
Reply With Quote
  #10  
Old 3/13/06, 3:29 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding the gas line

Larry the bonding of the gas piping is required "house side" of the meter because the pipe from the meter to the street is typically plastic. The gas piping isn't a grounding system it is a metallic "system" within the home that needs to be bonded to the grounding system.
Dave, the wire at the underground pipe at the meter is a tracer wire so that the utility can locate the plastic pipe if they need to and is not a ground wire (if that is what you mean by "the one at the meter")
Reply With Quote
  #11  
Old 3/13/06, 3:31 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding the gas line

Please...Please......guys the answers to those questions can really be obtained by reading the link I made above. Also the link I provided can explain it all about the gas piping system.



Paul W. Abernathy
Reply With Quote
  #12  
Old 3/13/06, 7:48 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Grounding the gas line

Quote:
Originally Posted by lewens
Please explain to me how the bonding of the gas line to the plumbing is effective as most times a jumper from one side of the meter to the other is not present. Without the jumper the gas line is bonded to nothing.
Quote:
Other Metal Piping Systems- Metal piping systems , such as gas or air piping which may become energized, SHALL BE bonded to the service equipment enclosure.
It's not bonded to the utility, it's bonded to the systems of the home.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 3/13/06, 8:10 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Grounding the gas line

Jeff, which side of the water meter would one bond the gas line to? Also, aren't all equipment using gas already bonded back thru the main panel ,if the are using elec.?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
  #14  
Old 3/13/06, 8:23 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,058
Default Re: Grounding the gas line

Bonding should be on the "house" side of all meters. I think you're confusing bonding with grounding. . .

http://www.nachi.org/forum/f19/bonding-2302/



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #15  
Old 3/13/06, 8:36 PM
nbhi's Avatar
nbhi nbhi is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Hamilton, OH
Posts: 715
Default Re: Grounding the gas line

Is this bonding of gas, heat ducks, etc., required? Should we be making our clients aware of this?



"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison

www.newbeginningshomeinspection.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Demystify Grounding & Bonding Class pabernathy Inspection Education & Training 5 12/24/06 1:10 AM
Metal Rigid or PVC Rigid what is code bpotts Electrical Inspections 5 12/4/06 2:40 PM


All times are GMT -4. The time now is 10:00 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts