Default Grounding Myths Quiz

Hey Guys,

Take this little QUIZ and reply and I will tell you who got the MOST right. Just number your answers TRUE or FALSE in numeric order.

Myths of Grounding
  1. Electricity always takes the path of least resistance.
    True or False

  2. In current flow, electrons leaving a grounded power supply are trying to get to back to earth ground.
    True or False

  3. A 15-ampere breaker will ultimately trip if an energized 120-volt conductor is directly attached to an isolated ground rod that has a measured ground resistance of 25 ohms.
    True or False

  4. A ground rod at a metal light pole with no equipment ground (green wire) serves to reduce the touch potential and makes the installation safer.
    True or False

  5. The grounding electrode for a 480 x 120/208 volt transformer (separately derived service) is intended to help remove dangerous voltage (touch potential) that can be imposed on the metal parts of the electrical system from a line-to-ground fault.
    True or False

  6. Ground rods are not required at a separate building supplied by a 60 ampere 4 wire feeder (120/240 V -, 2 hots, neutral and ground, with the neutral floated at the separate building disconnect).
    True or False

  7. The connection to the earth (ground) is important for proper operation of Transient Voltage Surge Suppressors (TVSSs)?
    True or False

  8. The connection to the earth (ground) creates a new zero reference. And the lower the ground, the lower the zero reference.
    True or False

  9. Grounding (earth connection) metal parts to the earth helps reduce stray voltage.
    True or False

  10. Grounding at service equipment helps in protecting interior wiring from transient voltage caused by lightning.
    True or False



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #2  
Old 1/22/07, 7:03 PM
waksell waksell is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Orlando, FL
Posts: 199
Default Re: Grounding Myths Quiz

1.True
2.False
3.False
4.False
5.True
6.True
7.True
8.True
9.True
10.False
How bad did I do?
Reply With Quote
  #3  
Old 1/22/07, 7:07 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,739
Default Re: Grounding Myths Quiz

11. Coffee grounds are postively charged.
True or False



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #4  
Old 1/22/07, 7:09 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Grounding Myths Quiz

lol.....I think Brian is ON TO ME with this little QUIZ...lol



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #5  
Old 1/22/07, 7:10 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Grounding Myths Quiz

Quote:
Originally Posted by waksell
1.True
2.False
3.False
4.False
5.True
6.True
7.True
8.True
9.True
10.False
How bad did I do?
Wesley- I will let you know at the end...lol



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #6  
Old 1/22/07, 7:11 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,739
Default Re: Grounding Myths Quiz

I like the quiz Paul, but I have to look up most of the answers.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #7  
Old 1/22/07, 7:18 PM
waksell waksell is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Orlando, FL
Posts: 199
Default Re: Grounding Myths Quiz

I am not an electrical expert.
I'll admit that I am not sure about my answers.
The questions are kind of like the ones on the drivers license test, kinda tricky.
Reply With Quote
  #8  
Old 1/22/07, 7:19 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Grounding Myths Quiz

Quote:
Originally Posted by bkelly2
11. Coffee grounds are postively charged.
True or False
Ah...YES I believe they POSTIVELY charge me UP in the morning...because without it I am one Negative SOB through the day.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #9  
Old 1/22/07, 10:19 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding Myths Quiz

The last 4 are true

... if you add the word impedance to #8.
Reply With Quote
  #10  
Old 1/22/07, 10:28 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Grounding Myths Quiz

Greg...please provide me with your take on WHY the last 4 are true statments. I am quite interested in it if you don't mind.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #11  
Old 1/22/07, 10:57 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding Myths Quiz

The things you reference in the last 4 are all referring to common mode transients. They are all going to find another path to ground if you don't give them one. #8 is poorly worded so it is hard to figure out what they are really asking but if you are saying the lower the "... impedance to ground..." I say it is true. The difference in potential between the EGC and the dirt will be lower. (zero?)
Reply With Quote
  #12  
Old 1/23/07, 12:12 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Grounding Myths Quiz

lol....these are not mine greg as I got them from Mike Holts site, he says they are all FALSE on his site and I wanted to get others opinions on them.
  1. Electricity always takes the path of least resistance.
    False- A 250 ­ resistor will experience a current of 40 mA, while the 800 ­ resistor will experience a current
    of 12.5 mA.

    False. In parallel paths, current divides and .ows through each individual parallel path in accordance with Kirchoff’s current law. So, when given multiple conductive paths on which to .ow, current will take all of the available paths. Yes, it’s true that more current will flow through the lower resistive path, as compared to a higher resistive path in a parallel circuit, but that’s not the question.
  2. In current flow, electrons leaving a grounded power supply are trying to get to back to earth ground.
    False- We know they are trying to get BACK to the source.
  3. A 15-ampere breaker will ultimately trip if an energized 120-volt conductor is directly attached to an isolated ground rod that has a measured ground resistance of 25 ohms.
    False- We know that OHMS laws says 120 divided into 25 ohms is only 4.8 Amps, not enough to TRIP a 15 A Breaker.

  4. A ground rod at a metal light pole with no equipment ground (green wire) serves to reduce the touch potential and makes the installation safer.
    False- because we know that the resistance of the earth is so great, very little current will return to the power source via earth if the earth is the only grounding path. The OCPD would not open much like in the example before.

  5. The grounding electrode for a 480 x 120/208 volt transformer (separately derived service) is intended to help remove dangerous voltage (touch potential) that can be imposed on the metal parts of the electrical system from a line-to-ground fault.
    False: Because all metal parts of electrical installations are required to be bonded to an effective ground-fault current path [250.4(A)(3)], there is no difference of potential between different separately derived systems.


  6. Ground rods are not required at a separate building supplied by a 60 ampere 4 wire feeder (120/240 V -, 2 hots, neutral and ground, with the neutral floated at the separate building disconnect).
    False- We know they are required at the separate building.

  7. The connection to the earth (ground) is important for proper operation of Transient Voltage Surge Suppressors (TVSSs)?
    False. The earth serves no purpose in the operation of a TVSS device. TVSS protection devices protect electrical equipment by shunting high-frequency impulse currents away from the load and back to the source via the circuit conductors, not via the earth.

  8. The connection to the earth (ground) creates a new zero reference. And the lower the ground, the lower the zero reference.
    False- Hmmm I find that zero reference is zero reference....not sure HOW low the ground is has anything to do with this reference point.

  9. Grounding (earth connection) metal parts to the earth helps reduce stray voltage.
    False: Grounding metal parts to the earth serves no purpose in reducing stray or NEV voltage.
    However,
    bonding metal parts together reduces the difference of potential between the metal parts, but the stray or NEV voltage, as measured between the metal parts and the earth, will not be reduced.
    Stray voltage or neutral-to-earth voltage can come from the electric utility’s distribution system, the building’s electric system, or both of these sources.


  10. Grounding at service equipment helps in protecting interior wiring from transient voltage caused by lightning.
    False. Grounding metal parts to the earth does not assist in protecting interior wiring or equipment from lightning.
    However,
    grounding the building disconnecting means to the earth does reduce the likelihood of a fire caused by elevated lightning voltage seeking a path to the earth by arcing across combustible materials.
    Interior wiring and equipment can be protected from lightning- induced voltage transients on the circuit conductors by the use of properly designed cascading TVSS protection devices: one at the service equipment, one at each downstream panelboard, and one at each point of use.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #13  
Old 1/23/07, 12:17 AM
waksell waksell is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Orlando, FL
Posts: 199
Default Re: Grounding Myths Quiz

I guess I'm only batting 400.

I heard 300 was a good batting average.
Reply With Quote
  #14  
Old 1/23/07, 12:48 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Grounding Myths Quiz

ahh...you are good Wesley....it was just a fun thing and to be honest with you..this is why I idol Mike Holt......I did not get them all right myself when I did it...he explains things very well.....

Oh to be Mike Holt....



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #15  
Old 1/23/07, 3:31 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding Myths Quiz

Perhaps Mike Holt has never really studied lightning.
IBM did a lot of studies on this in the lightning capital of the world and concluded it is very important to have a good grounding electrode and that it be used by all utilities. We went from blowing up 50 boxes a week to virtually zero. Our stuff works. The easy example is your modem. An ungrounded TVSS might do a great job of shunting the voltage on the supply side and preventing the circuitry from seeing a line/neutral surge but if the whole modem rises several hundred volts from ground that difference will be made up on the telephone side that has it's own grounding coinnection and it goes boom.

As for #8, if your EGC is bonded to the neutral and not well grounded the difference in potential between the case of your stove and the terazzo floor in your kitchen (on a slab) can be shocking. (a defect in this house when I moved in) My "zero" standing on the floor was not the same as the utility "zero". In the computer biz I have measured 35 volts between the ground of buildings 20 feet apart. "Local" ground is very important. It is why 250 says we drive a rod (or 2) at every building. In the computer biz we also bonded all of these together with a fat wire. If a data cable went somewhere we also ran a big bond.

All I can say about # 9 is to read Article 547 and the USDA articles about bonding grids and the ground rods you should have in a dairy barn. That is all to prevent stray current. The stray current is between "ground" where the power comes from and the dirt where you are using it.
They say, if you have a stock tank warmer, you should bury a ground ring around it and bond the tank. At the door of a barn you should be burying rods out in the dirt on the apron bonded to the steel in the floor.

Perhaps I misunderstood 10 since my thoughts were the same as the statement starting with "however..."

I think he interntionally made the wording vague on a few so he could make the case for "false". It was my first impression that he was going for all false but about #7 I saw he may be going astray.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Shane Boyd, here are IAC2's requirements: gromicko IAC2 Forum 1 11/12/06 9:05 PM
Can you guess what goofy inspection trade association requires all this?! gromicko Canadian Inspectors 4 8/26/06 4:11 PM


All times are GMT -4. The time now is 7:04 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts