Default Grounding ( neutral) Conductor Terminals

Intent: This new section should ensure that grounded (neutral) conductors terminate within the panelboard to an individual terminal. This has been a UL requirement (UL Std. 67 – Panelboard Standard) for some time, and the addition to the NEC is intended to bring this information to the installers. Technically, this is covered by 110.3(B), which requires all equipment to be installed in accordance with the manufacturer's installation instructions and markings, but nobody knew it existed. UL Std. 67 (Panelboard Standard) permits up to three 10 AWG equipment grounding conductors to terminate on a single terminal, if the terminal is marked for this purpose.

The intent of this requirement is to ensure that the grounded (neutral) conductor of a multiwire branch circuit is not momentarily disconnected, which could result in the destruction of electrical equipment and fires from overvoltage.

My Comments - As we have talked many times regarding this and have posted things as well, it is always important to know exactly where the reason for reporting it comes from. This is posted courtesy of Mike Holt Enterprises



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #2  
Old 4/15/06, 10:37 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding ( neutral) Conductor Terminals

nice post Paul. good to know. what if this info is not availible in the panel, or on the cover door. do we assume it's o.k. or not o.k.?? when in dought, call it out?
Reply With Quote
  #3  
Old 4/15/06, 10:44 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Grounding ( neutral) Conductor Terminals

Jay,

it is never ok for Neutrals to be double lugged regardless of the panel ledger. As for the grounds it is a common practice to place (2) grounds of the same AWG per terminal.

Keep an eye out for someone placing (2) grounds under a terminal that are different size AWG's which is most certainly a thing to call out.

The main issue here really is the doubling up of the neutrals or mixing the neutrals with a EGC at the same terminal, Most every one calls this out anyway I just wanted to post a image to help seal it in the memory as well as giving a reference to better understand it.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #4  
Old 4/15/06, 11:03 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding ( neutral) Conductor Terminals

awesome....thanx Paul.
Reply With Quote
  #5  
Old 4/18/06, 1:49 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Grounding ( neutral) Conductor Terminals

No problem my brother.......my own brother who is a TOP NOTCH electrical contractor about 60 miles from my electrical contracting business.....has been putting Neutrals and Grounds under the same lug for years...and the local AHJ never called it out.

So when I came over to speak at their local Apprentice program and the local AHJ happen to sit in on it....guess what......ALOT of panels were turned down in the coming weeks after...lol.....now my brother does it the right way...lol....

With everything electrical contractors have to learn and keep up with, things in the UL can be laxed on....thankfully we have people like Joe T who are spreading the word on it more and more because even I don't carry around a UL White Book....may start to however...thehehhe.......anyway I am glad the NEC 2002 addressed it.

I just wanted to give it to ya in Laymans Terms to better understand it....Mike Holt's books do a good job at breaking it down for you.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #6  
Old 4/19/06, 11:47 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding ( neutral) Conductor Terminals

I'm sure i speak for many of us when i say, we realy appreciate you, Jeff, Joe, and ALL the other electricians who help us out with the most difficult, and "ruly" systems in a home. i've learned more from you folks than any of the 3 HI corrispondences i've done, any of my residential or military training in this feild. Thanx again...........Jay.
Reply With Quote
  #7  
Old 4/20/06, 11:55 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Grounding ( neutral) Conductor Terminals

Quote:
Originally Posted by Jay Moge
I'm sure i speak for many of us when i say, we realy appreciate you, Jeff, Joe, and ALL the other electricians


Hey, I'm learning here too. I am a full time HI. No sparky in me at all.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #8  
Old 4/20/06, 12:02 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,078
Default Re: Grounding ( neutral) Conductor Terminals

Quote:
Originally Posted by jpope


Hey, I'm learning here too. I am a full time HI. No sparky in me at all.
Maybe, but you're also a wellspring of NEC and general code knowledge.
My added thanks to Paul and You...



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #9  
Old 4/20/06, 11:06 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding ( neutral) Conductor Terminals

Quote:
Originally Posted by jpope


Hey, I'm learning here too. I am a full time HI. No sparky in me at all.
i thought for sure you USED to be one. sorry if i offended you or the electricians.
Reply With Quote
  #10  
Old 4/20/06, 11:38 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 664
Default Re: Grounding ( neutral) Conductor Terminals

Thanks Paul for another great post.

Thanks Jeff and Brian for your help earlier.

This board is an education in itself.




"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #11  
Old 5/24/06, 11:19 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Grounding ( neutral) Conductor Terminals

Bump...Again for the Newbies......



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #12  
Old 5/24/06, 4:25 PM
Mike Parks's Avatar
Mike Parks Mike Parks is offline
Active Poster
 
Join Date: Oct 2003
Location: Columbus Ohio
Posts: 150
Please Note: Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding ( neutral) Conductor Terminals

Not a problem for me, but it is not 'code' compliant.

I like the egc and the grounded conductor (NOT ALLOWED) together because it makes it easier to disconnect a circuit.

I never would like to see two grounded conductors under the same lug.

I cannot remember when it was code but remember it being enforced in the mid 90's.

Be careful with this one, this is a code issue, not necessarily a safety one.
Reply With Quote
  #13  
Old 5/24/06, 5:52 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Grounding ( neutral) Conductor Terminals

Mike,

In nature it is a Safety Issue as well......while the standard has been around for many years....in my opinion their is a safety aspect here as well that should be addressed.

Many electricians did this for years as much of a point to twist them together under the same terminal...however it has been a violation of Standard 67 for quite some time.

Twisting together MAY remove the grounded and Equipment Grounding Conductor....BUT does not mean the Non-Grounded conductor is not present and ON and their is a possible other issues......which could be a issue if removed even together.

I personally just dont like to see grounded conductors DOUBLED up on anything.....I also find that the terminals get LOOSE faster in that manner as well versus individual terminations.

Just my opinion...for what its worth...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #14  
Old 7/7/06, 12:06 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Grounding ( neutral) Conductor Terminals

great stuff....Bump it again



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #15  
Old 1/29/07, 9:26 PM
Peter W. Bennett Peter W. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Little Silver, NJ
Posts: 373
Default Re: Grounding ( neutral) Conductor Terminals

[quote=pabernathy]Jay,

it is never ok for Neutrals to be double lugged regardless of the panel ledger. As for the grounds it is a common practice to place (2) grounds of the same AWG per terminal.

Keep an eye out for someone placing (2) grounds under a terminal that are different size AWG's which is most certainly a thing to call out.

The main issue here really is the doubling up of the neutrals or mixing the neutrals with a EGC at the same terminal, Most every one calls this out anyway I just wanted to post a image to help seal it in the memory as well as giving a reference to better understand it.

Paul, thanks for the clarification. Based on your comment "The main issue here really is the doubling up of the neutrals or mixing the neutrals with a EGC at the same terminal", here's a photo of a mix.
Attached Thumbnails
grounding-neutral-conductor-terminals-lugged.jpg  
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Demystify Grounding & Bonding Class pabernathy Education 5 12/24/06 2:10 AM
Metal Rigid or PVC Rigid what is code bpotts Electrical 5 12/4/06 3:40 PM


All times are GMT -4. The time now is 2:16 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147