#1
|
||||
|
||||
Intent: This new section should ensure that grounded (neutral) conductors terminate within the panelboard to an individual terminal. This has been a UL requirement (UL Std. 67 Panelboard Standard) for some time, and the addition to the NEC is intended to bring this information to the installers. Technically, this is covered by 110.3(B), which requires all equipment to be installed in accordance with the manufacturer's installation instructions and markings, but nobody knew it existed. UL Std. 67 (Panelboard Standard) permits up to three 10 AWG equipment grounding conductors to terminate on a single terminal, if the terminal is marked for this purpose. The intent of this requirement is to ensure that the grounded (neutral) conductor of a multiwire branch circuit is not momentarily disconnected, which could result in the destruction of electrical equipment and fires from overvoltage. My Comments - As we have talked many times regarding this and have posted things as well, it is always important to know exactly where the reason for reporting it comes from. This is posted courtesy of Mike Holt Enterprises Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#2
|
||||
|
||||
|
Please Note:
Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
nice post Paul. good to know. what if this info is not availible in the panel, or on the cover door. do we assume it's o.k. or not o.k.?? when in dought, call it out?
|
|
#3
|
||||
|
||||
|
Jay,
it is never ok for Neutrals to be double lugged regardless of the panel ledger. As for the grounds it is a common practice to place (2) grounds of the same AWG per terminal. Keep an eye out for someone placing (2) grounds under a terminal that are different size AWG's which is most certainly a thing to call out. The main issue here really is the doubling up of the neutrals or mixing the neutrals with a EGC at the same terminal, Most every one calls this out anyway I just wanted to post a image to help seal it in the memory as well as giving a reference to better understand it. Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#4
|
||||
|
||||
|
Please Note:
Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
awesome....thanx Paul.
|
|
#5
|
||||
|
||||
|
No problem my brother.......my own brother who is a TOP NOTCH electrical contractor about 60 miles from my electrical contracting business.....has been putting Neutrals and Grounds under the same lug for years...and the local AHJ never called it out.
So when I came over to speak at their local Apprentice program and the local AHJ happen to sit in on it....guess what......ALOT of panels were turned down in the coming weeks after...lol.....now my brother does it the right way...lol.... With everything electrical contractors have to learn and keep up with, things in the UL can be laxed on....thankfully we have people like Joe T who are spreading the word on it more and more because even I don't carry around a UL White Book....may start to however...thehehhe.......anyway I am glad the NEC 2002 addressed it. I just wanted to give it to ya in Laymans Terms to better understand it....Mike Holt's books do a good job at breaking it down for you. Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#6
|
||||
|
||||
|
Please Note:
Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
I'm sure i speak for many of us when i say, we realy appreciate you, Jeff, Joe, and ALL the other electricians who help us out with the most difficult, and "ruly" systems in a home. i've learned more from you folks than any of the 3 HI corrispondences i've done, any of my residential or military training in this feild. Thanx again...........Jay.
|
|
#7
|
||||
|
||||
|
Quote:
Hey, I'm learning here too. I am a full time HI. No sparky in me at all. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#8
|
||||
|
||||
|
Quote:
My added thanks to Paul and You... - Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector |
|
#9
|
||||
|
||||
|
Please Note:
Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#10
|
||||
|
||||
|
Thanks Paul for another great post.
Thanks Jeff and Brian for your help earlier. This board is an education in itself.
"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com SmithHomeInspection@yahoo.com NY State Lic. # 16000008304 631-434-5200 |
|
#11
|
||||
|
||||
|
Bump...Again for the Newbies......
Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#12
|
||||
|
||||
|
Please Note:
Mike Parks is a non-member guest and is in no way affiliated with InterNACHI or its members.
Not a problem for me, but it is not 'code' compliant.
I like the egc and the grounded conductor (NOT ALLOWED) together because it makes it easier to disconnect a circuit. I never would like to see two grounded conductors under the same lug. I cannot remember when it was code but remember it being enforced in the mid 90's. Be careful with this one, this is a code issue, not necessarily a safety one. |
|
#13
|
||||
|
||||
|
Mike,
In nature it is a Safety Issue as well......while the standard has been around for many years....in my opinion their is a safety aspect here as well that should be addressed. Many electricians did this for years as much of a point to twist them together under the same terminal...however it has been a violation of Standard 67 for quite some time. Twisting together MAY remove the grounded and Equipment Grounding Conductor....BUT does not mean the Non-Grounded conductor is not present and ON and their is a possible other issues......which could be a issue if removed even together. I personally just dont like to see grounded conductors DOUBLED up on anything.....I also find that the terminals get LOOSE faster in that manner as well versus individual terminations. Just my opinion...for what its worth... Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#14
|
||||
|
||||
|
great stuff....Bump it again
Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#15
|
|||
|
|||
|
[quote=pabernathy]Jay,
it is never ok for Neutrals to be double lugged regardless of the panel ledger. As for the grounds it is a common practice to place (2) grounds of the same AWG per terminal. Keep an eye out for someone placing (2) grounds under a terminal that are different size AWG's which is most certainly a thing to call out. The main issue here really is the doubling up of the neutrals or mixing the neutrals with a EGC at the same terminal, Most every one calls this out anyway I just wanted to post a image to help seal it in the memory as well as giving a reference to better understand it. Paul, thanks for the clarification. Based on your comment "The main issue here really is the doubling up of the neutrals or mixing the neutrals with a EGC at the same terminal", here's a photo of a mix. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical | 6 | 9/15/08 8:57 AM |
| Demystify Grounding & Bonding Class | pabernathy | Education | 5 | 12/24/06 2:10 AM |
| Metal Rigid or PVC Rigid what is code | bpotts | Electrical | 5 | 12/4/06 3:40 PM |