  #16  
Old 1/29/07, 10:10 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding ( neutral) Conductor Terminals

There is another similar violation people seem to ignore. In the main panel you have a neutral bus bar, connected to the grounded service conductor or connected to that bus bar with the factory strap but you can also have other auxillary bus bars screwed directly to the enclosure. Those bus bars are ONLY for the grounding conductors. If you connect a neutral to one of these it is a 250.6 violation since you are sending branch circuit current through the main bonding jumper. Even in the main panel where the service disconnect resides, all ground busses are not the same.
Reply With Quote
  #17  
Old 1/29/07, 10:13 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding ( neutral) Conductor Terminals

Which are you refering to greg.....the original post was a MIKE HOLT image...The picture in the previous post was new...have not even looked at it.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #18  
Old 1/30/07, 2:13 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding ( neutral) Conductor Terminals

I don't know of any pictures of this. If I get a minute I may take some.
Reply With Quote
  #19  
Old 1/30/07, 10:08 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding ( neutral) Conductor Terminals

Ahh....I thought you were talking about a specific image. yes, I agree it is VERY important to know how the busses are connected within the panel.

This would be MORE so a problem in a "Remote Distribution Panel" when done incorrectly.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #20  
Old 2/3/07, 6:38 PM
Peter W. Bennett Peter W. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Little Silver, NJ
Posts: 515
Default Re: Grounding ( neutral) Conductor Terminals

Any photos/diagrams available?
thanks, Peter
Reply With Quote
  #21  
Old 2/3/07, 7:06 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding ( neutral) Conductor Terminals

Peter,

I will see...but just think of it this way.....like a normal remote distribution panel with a seperate isolated " Grounded " neutral buss bar and then a jumper to the panel....all along you had a grounding buss bar already attached to the panel....kinda defeats the isolation of the grounded buss bar part...

Did anyone notice in my original post i used the title " grounding (Neutral ) conductor terminals"...so wrong..lol...I should have said " Grounded ( Neutral ) conductor terminals"

Amazed I was not caught on that....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #22  
Old 2/3/07, 7:08 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,557
Default Re: Grounding ( neutral) Conductor Terminals

Quote:
Originally Posted by pabernathy
Amazed I was not caught on that....
I guess no one wanted to challenge the GURU.
Reply With Quote
  #23  
Old 2/3/07, 7:13 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding ( neutral) Conductor Terminals

lol.......WOW...now you KNOW I dont demand that kinda respect...lol

Actually I noticed it a bit back but then it would not let me edit it so I said...Hell with it...lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #24  
Old 2/3/07, 7:36 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding ( neutral) Conductor Terminals

lol...I notice GREG is reading this post as we speak.....Be gentle on me FELLA...thehehe



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #25  
Old 2/4/07, 3:03 PM
aandrews aandrews is offline
New User
 
Join Date: Mar 2006
Location: New Castle, DE
Posts: 90
Please Note: aandrews is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding ( neutral) Conductor Terminals

Thanks Paul .

Just went down and looked at my Panel and found two spots were the ground and neutral are together on the buss bar. Should I remove and separate them ? I have installed a few breakers before.
Reply With Quote
  #26  
Old 2/4/07, 3:06 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding ( neutral) Conductor Terminals

Well.....You can but do this for me FIRST......CLICK off your MAIN breaker ( and understand the wires coming IN are still LIVE ) ahead of time just to be safe and GO FOR IT.....just make sure you have your torque wrench handy



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #27  
Old 2/4/07, 4:06 PM
aandrews aandrews is offline
New User
 
Join Date: Mar 2006
Location: New Castle, DE
Posts: 90
Please Note: aandrews is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding ( neutral) Conductor Terminals

Thanks Paul will do !
Reply With Quote
  #28  
Old 2/4/07, 4:47 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Grounding ( neutral) Conductor Terminals

Quote:
Originally Posted by pabernathy
Did anyone notice in my original post i used the title " grounding (Neutral ) conductor terminals"...so wrong..lol...I should have said " Grounded ( Neutral ) conductor terminals"

Amazed I was not caught on that....
I just read this post and that was flashing in neon so I was going to mention something but you've already cleaned up after yourself. I'll have to let the granddaughter know that, yes, we even have to clean up after ourselves on the message board. She'll like that.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #29  
Old 2/4/07, 6:31 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding ( neutral) Conductor Terminals

lol......it was posted like.......April of 2006, I noticed it at a point that it would not let me edit anymore...not sure what the time frame was on that...lol....yeah I never said I was perfect....it is only implied as such



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Demystify Grounding & Bonding Class pabernathy Inspection Education & Training 5 12/24/06 2:10 AM
Metal Rigid or PVC Rigid what is code bpotts Electrical Inspections 5 12/4/06 3:40 PM


All times are GMT -4. The time now is 10:58 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts