Default grounding with plastic plumbing

Is there anything special to look out for if you suspect the home has plastic pipes for plumbing. The main box did not have a label stating that and the ground wires were attached to the water and gas pipes. Just looking for any advice to give the homeowner should the home be plastic and not copper.
Reply With Quote
  #2  
Old 3/26/07, 10:53 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,037
Default Re: grounding with plastic plumbing

Repipe or original?

If it's a repipe, check to make sure there's a ground rod or Ufer.

If it's original, it's likely there's already a Ufer ground. There are no bonding requirements for non metallic piping (non metallic piping cannot be bonded).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 3/26/07, 11:00 PM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 211
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: grounding with plastic plumbing

Home built in 2005. If there is plastic, it's original. There is a ground rod taped to the side of the water pipe. How far down is goes, I have no idea....gotta be 10 feet i think. Gonna recommend that the homeowner determine the type of plumbing and if plastic, ensure the the electrical grounding is proper.
Reply With Quote
  #4  
Old 3/26/07, 11:04 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,037
Default Re: grounding with plastic plumbing

If there's a ground rod, it's proper (assuming the GEC is attached to the rod and service panel).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 3/26/07, 11:07 PM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 211
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: grounding with plastic plumbing

the GEC is attached by clamp to the water pipe to which the ground rod is taped. Isn't there a specific depth the ground rod has to go if the home is plumbed with plastic?
Reply With Quote
  #6  
Old 3/26/07, 11:16 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: grounding with plastic plumbing

8' but you probably need 2 ground rods 6 feet or farther apart if there are no other electrodes. Without a certified ground rod test most AHJs will not automatically agree it is less than 25 ohms.
Reply With Quote
  #7  
Old 3/27/07, 12:48 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,037
Default Re: grounding with plastic plumbing

Quote:
Originally Posted by Scott Schultz
to which the ground rod is taped.
Do you mean like, with electrical tape? Or do you mean tapped, like with a conductor?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #8  
Old 3/27/07, 1:06 AM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 211
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: grounding with plastic plumbing

I mean taped, like with what i wish was electrical tape but felt more like paper. It was painted and very loose, not a good job at all. I made the homeowner aware of it and told him if he does indeed have plastic pipes to make sure that grounding rod is properly attached.
Reply With Quote
  #9  
Old 3/27/07, 2:17 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,037
Default Re: grounding with plastic plumbing

Well then, the grounding electrode should be verified.

The ground rod is useless in that case. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #10  
Old 4/1/07, 8:37 PM
Mark A. Timpani's Avatar
Mark A. Timpani Mark A. Timpani is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 1,613
Default Re: grounding with plastic plumbing

Any good ufer pics or documentation?




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #11  
Old 4/1/07, 10:08 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: grounding with plastic plumbing

This is how we do a Ufer in Florida. It will end up being under a blank S/S cover in the stucco

http://members.aol.com/gfretwell/ufer.jpg
Reply With Quote
  #12  
Old 4/2/07, 12:10 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: grounding with plastic plumbing

Quote:
Originally Posted by mtimpani
Any good ufer pics or documentation?



Reply With Quote
  #13  
Old 4/2/07, 6:50 PM
Jeff S. Vogan's Avatar
Jeff S. Vogan Jeff S. Vogan is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Bevier, MO
Posts: 516
Default Re: grounding with plastic plumbing

Either way, the electric service can't be grounded to a gas pipe, can it?
Reply With Quote
  #14  
Old 4/3/07, 10:21 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,022
Default Re: grounding with plastic plumbing

Quote:
Originally Posted by jvogan
Either way, the electric service can't be grounded to a gas pipe, can it?
309.1 Grounding. Gas piping shall not be used as a grounding electrode.

309.2 Connections. Electrical connections between equipment and the building wiring, including the ground ing of the equipment, shall conform to the ICC Electrical Code.

SECTION 310 (IFGS)ELECTRICAL BONDING

310.1 Gas pipe bonding. Each above-ground portion of a gas piping system that is likely to become energized shall be electrically continuous and bonded to an effective ground-fault current path. Gas piping shall be considered to be bonded where it is connected to gas utilization equipment that is connected to the equipment grounding conductor of the circuit supplying that equipment.
Reply With Quote
  #15  
Old 4/3/07, 10:30 AM
Mark A. Timpani's Avatar
Mark A. Timpani Mark A. Timpani is offline
InterNACHI Member
 
Join Date: May 2004
Location: Tucson, AZ
Posts: 1,613
Default Re: grounding with plastic plumbing

Thanks for the pics Dave. Are the post tension cables ok for the ground/bond ?




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help - Polybutylene Pipes Rick G Plumbing 39 2/12/09 9:16 AM
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Demystify Grounding & Bonding Class pabernathy Education 5 12/24/06 2:10 AM


All times are GMT -4. The time now is 11:23 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts