Default grounding on plumbing

What is the intent behind the rule that a jumper be placed from one side of the water meter to the other when the cold water line is used as a ground connection? Is it because the meter could be removed and the ground lost? or due to some issue with conductivity through the meter? or something else? Thanks.
Reply With Quote
  #2  
Old 8/17/07, 9:36 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: grounding on plumbing

Is the water pipe being used as an electrode or is there 10 feet of metal water pipe in contact with earth?
Reply With Quote
  #3  
Old 8/17/07, 10:00 AM
gmathias gmathias is offline
New User
 
Join Date: Aug 2004
Location: Lewisburg, PA
Posts: 64
Please Note: gmathias is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: grounding on plumbing

I think that the ground contact is the main factor. I recommended that an additional grounding conductor be installed and clamped to a metal stake driven into the earth.
Reply With Quote
  #4  
Old 8/17/07, 10:26 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: grounding on plumbing

Quote:
Originally Posted by gmathias
What is the intent behind the rule that a jumper be placed from one side of the water meter to the other when the cold water line is used as a ground connection? Is it because the meter could be removed and the ground lost? or due to some issue with conductivity through the meter? or something else? Thanks.
Hi Greg the intent is to maintain a continuous grounding path should the meter be required to be removed for servicing.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #5  
Old 8/17/07, 11:11 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: grounding on plumbing

You answered your own question.

Regardless of there is 10 feet(being used as a gec) or not, if there is metal piping there should be a bonding jumper around removable components (water meter, heater, demineralizer, etc) and it should be properly bonded for a low impedance ground fault path.

tom
Reply With Quote
  #6  
Old 8/17/07, 12:07 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: grounding on plumbing

Quote:
Originally Posted by tdietrich1
You answered your own question.

Regardless of there is 10 feet(being used as a gec) or not, if there is metal piping there should be a bonding jumper around removable components (water meter, heater, demineralizer, etc) and it should be properly bonded for a low impedance ground fault path.

tom
Herein lays the confusion between bonding and grounding when it concerns a metal pipe.

There is no requirement to bond around anything and there is no requirement to make a metal pipe electrically continuous when we are bonding the pipe.

The requirement to bond around removable devices if found in 250.53(D)(1) so let’s take a short minute and look at this section of the code.

First this section is found in Part III which is “III. Grounding Electrode System and Grounding Electrode Conductor”
Part Three address two different aspects of grounding which comprises the Electrode and the Electrode Conductor.

Second 250.53 addresses the electrode system installation “250.53 Grounding Electrode System Installation.” 250.53 address nothing but that part of the metal pipe that is part of the electrode. In 250.52 we are told that only the first five feet can be used as the electrode. “Interior metal water piping located more than 1.52 m (5 ft) from the point of entrance to the building shall not be used as a part of the grounding electrode system or as a conductor to interconnect electrodes that are part of the grounding electrode system.”

Third subpart (D) of 250.53 address a metal pipe that is underground “(D) Metal Underground Water Pipe” This subpart addresses the metal pipe that is being used as part of the electrode system and has two subparts one of which a seems to cause a lot of confusion.

Forth is Sub Part (1) found in 250.53(D).
"(1) Continuity. Continuity of the grounding path or the bonding connection to interior piping shall not rely on water meters or filtering devices and similar equipment."
This part addresses the continuity of the first five feet that is part of the electrode and covers the requirement found in 250.104 which is the requirement to bond that part of the metal pipe that is on the interior of the building and not part of the electrode system.
Continuity is required to be maintained between the electrode and the interior part of the metal water pipe and this is accomplished through bonding around removable devices.

In This Slide the blue metal water pipe is the underground electrode and the green is the first five feet of the metal pipe that is on the interior of the building and is also part of the electrode. The red is the interior metal pipe and is required to be bonded by 250.104 and this is accomplished with the purple bonding jumper outlined in 250.53(D)(1).


In This Slide there is no metal pipe that is part of the electrode and the interior pipe is metal. Although there are removable devices in the metal pipe the only requirement is to bond the pipe as outlined in 250.104 and there is no requirement to bond around anything.
Reply With Quote
  #7  
Old 8/17/07, 12:53 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: grounding on plumbing

Quote:
Originally Posted by Mike Whitt
Herein lays the confusion between bonding and grounding when it concerns a metal pipe.
I was under the impression from previous posts, there was confusion about doing it.

"huh huh he said 'doing it' huh..." "yeah yeah, doing it!"


Quote:
Originally Posted by Mike Whitt
There is no requirement to bond around anything and there is no requirement to make a metal pipe electrically continuous when we are bonding the pipe.
Ok now I'm confused about your post.

Please no reply necessary.

tom
Reply With Quote
  #8  
Old 8/17/07, 3:22 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: grounding on plumbing

Quote:
Originally Posted by tdietrich1
Ok now I'm confused about your post.
Which part?

This confusion needs to be cleared up for all involved, don't you think?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Demystify Grounding & Bonding Class pabernathy Inspection Education & Training 5 12/24/06 2:10 AM
A few useful posts - I forget from whom jmichalski Plumbing Inspections 12 3/30/06 10:06 PM


All times are GMT -4. The time now is 10:04 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts