I just absolutely hate being wrong but occasionally it can happen.
My question concerns proper grounding of two updated panels one being the main on an exterior wall near the meter and has a earth ground in place. The second panel located on an interior wall within 3 feet of the exterior panel. The earth ground was not extended to the interior panel other than the neutral wire. Am I right or wrong should the earth ground have been extended to the interior panel.
Reply With Quote
  #2  
Old 12/5/06, 10:31 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding question

Charley,

To better answer your question......answer this...

1.) Is that interior panel fed from the outside panel or directly into the meter itself?

2.) How many wires are run to the inside panel?

Edit- opps...i said Interior Meter...lol...had to FIX that...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 12/5/06 at 10:44 AM..
Reply With Quote
  #3  
Old 12/5/06, 10:48 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Grounding question

Quote:
Originally Posted by pabernathy
Charley,

To better answer your question......answer this...

1.) Is that interior meter fed from the outside panel or directly into the meter itself?

2.) How many wires are run to the inside panel?
Paul The meter is outside and the main panel is located near the meter it is a standard 220 volt and a neutral 3 wires. The exterior panel has the earth ground to the rod. Both panels have the neutral connected to each other and in essence are connected to the ground rod. My question is should an additional ground have been connected between the two panels.
Reply With Quote
  #4  
Old 12/5/06, 10:52 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding question

Charley,

You did not answer my question........is the interior panel FED from the exterior panel..........or does the interior panel feed directly into the outside meter itself......just like the exteroir panel does.

Trust me...I am going somewhere with this........



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #5  
Old 12/5/06, 11:02 AM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Grounding question

Quote:
Originally Posted by pabernathy
Charley,

You did not answer my question........is the interior panel FED from the exterior panel..........or does the interior panel feed directly into the outside meter itself......just like the exteroir panel does.

Trust me...I am going somewhere with this........
Sorry you thru me with the meter.
The interior panel is fed directely from the exterior panel not the meter.
Reply With Quote
  #6  
Old 12/5/06, 11:13 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding question

Ahhh....then you should have a 4 wire set up going from the exterior panel to the interior panel......and no need to have the GEC go from the outside panel to the inside panel.....the Grounding takes place at the outside point...

The 4th wire that should be going to the inside panel is the EGC and fulfils the application fine.

if it is NOT a 4 wire setup...then it is wrong and should be called out and defered.

Sorry to drag you on and on with this....but wanted to make sure we are clear on it.....as both methods could have issued so I wanted to make sure we address your question directly.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #7  
Old 12/5/06, 11:35 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding question

Hope that explained it for you Charley...if not as always my phone is on and open for your questions.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #8  
Old 12/5/06, 1:46 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 3,875
Default Re: Grounding question

Quote:
Originally Posted by pabernathy
Ahhh....then you should have a 4 wire set up going from the exterior panel to the interior panel......and no need to have the GEC go from the outside panel to the inside panel.....the Grounding takes place at the outside point...

The 4th wire that should be going to the inside panel is the EGC and fulfils the application fine.

if it is NOT a 4 wire setup...then it is wrong and should be called out and defered.

Sorry to drag you on and on with this....but wanted to make sure we are clear on it.....as both methods could have issued so I wanted to make sure we address your question directly.
Thanks Paul the reason I asked this question I inspect in two different towns and the one that I do the most inspections in and am use to seeing a non-protected ground between the panels going to the neutral bars. The inspection that I was making reference to was being sold by a little old lady and her son installed the electrical panels and is suppose to be the city electrical inspector and he stated the the installation was up to city code.

I disagreed in my report stating that the indoor panel did not appear to be grounded properly and boy did I stir the stink.
Reply With Quote
  #9  
Old 12/5/06, 4:27 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding question

Charley,

It would only be wrongly done IF the guy did not run a 4 ( four ) wire cable to the interior panel....then his installation is incorrect.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Demystify Grounding & Bonding Class pabernathy Inspection Education & Training 5 12/24/06 2:10 AM
Grounding Question cbarrows Electrical Inspections 10 8/16/06 8:16 PM


All times are GMT -4. The time now is 9:50 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts