Old 10/2/09, 6:47 AM
Wayne B. Wilson's Avatar
Default Grounding Question
How many mark up the ground in a panel if it just goes to the meter cabinet and not into the panel , I had a dissucion with a bulider yesterday when i called it out.
Find an InterNACHI certified Florida Home Inspector (and anywhere else in North America)
Old 10/2/09, 11:08 AM
Jeffrey R. Pope's Avatar
Default Re: Grounding Question
Are you referring to the service neutral or the grounding electrode conductor?
In either case, there must be a bonding connection between the panel enclosure and the meter cabinet - assuming they're physically separate.
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Old 10/2/09, 11:18 AM
It is the ground electrode . There was no ground wire coming from the meter base neutral or electrode to the main service panel in the garage. Just conduit between both. Not a bonded connection . Electrician was the builder and said it was not needed in this area. Wrote it up any .
Just asking this is about 5 in the same area i have found. Thanks Jeff
Old 10/2/09, 11:37 AM
There should be three conductors connecting the meter base to the service panel - H+H+N. The neutral is used to bond the panels. The GEC will generally originate from the service panel.
Admittedly, most of what I see are combination-type panels, where the meter socket and service equipment are in a single cabinet, so I may be missing something here.
Jeff Pope
Santa Clarita CA
(661) 212-0738
Old 10/2/09, 11:49 AM
I wish i had taken a picture of the meter base entrance
Old 10/2/09, 12:21 PM
Jim Port Jim Port is offline
Unmoderated Guest
Some areas allow the grounding to be accomplished in the meter socket. Others do not allow the grounding in the socket so it gets done in the panel or disconnect.
Old 10/2/09, 12:33 PM
That's exactly what I would expect to see.
Jeff Pope
Santa Clarita CA
(661) 212-0738
Old 10/2/09, 3:25 PM
Ah, now I get it. I was misunderstanding the question.
Jim is correct - it depends on your jurisdiction. Most of CA rquires the GEC to originate from the service equipment.
Jeff Pope
Santa Clarita CA
(661) 212-0738
Old 10/2/09, 9:18 PM
It is up to the PoCo practice in the area and that may have changed at some point over the years. As long as the neutral is bonded to the meter base enclosure and GEC (which we cannot see) electrically all should be ok.
Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Odd grounding question. mnahrgang Electrical Inspections 2 8/25/09 2:04 PM
Question about metal Building grounding sparksnmore Electrical Inspections 16 11/19/07 12:19 PM
Grounding question cbottger Electrical Inspections 8 12/5/06 3:27 PM