How many mark up the ground in a panel if it just goes to the meter cabinet and not into the panel , I had a dissucion with a bulider yesterday when i called it out.
|
| Find an InterNACHI certified Kansas Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
Are you referring to the service neutral or the grounding electrode conductor?
In either case, there must be a bonding connection between the panel enclosure and the meter cabinet - assuming they're physically separate. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
||||
|
||||
|
It is the ground electrode . There was no ground wire coming from the meter base neutral or electrode to the main service panel in the garage. Just conduit between both. Not a bonded connection . Electrician was the builder and said it was not needed in this area. Wrote it up any .
Just asking this is about 5 in the same area i have found. Thanks Jeff |
|
#4
|
||||
|
||||
|
There should be three conductors connecting the meter base to the service panel - H+H+N. The neutral is used to bond the panels. The GEC will generally originate from the service panel.
Admittedly, most of what I see are combination-type panels, where the meter socket and service equipment are in a single cabinet, so I may be missing something here. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
||||
|
||||
|
|
|
#6
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Some areas allow the grounding to be accomplished in the meter socket. Others do not allow the grounding in the socket so it gets done in the panel or disconnect.
|
|
#7
|
||||
|
||||
|
That's exactly what I would expect to see.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#8
|
||||
|
||||
|
Quote:
Jim is correct - it depends on your jurisdiction. Most of CA rquires the GEC to originate from the service equipment. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#9
|
|||
|
|||
|
It is up to the PoCo practice in the area and that may have changed at some point over the years. As long as the neutral is bonded to the meter base enclosure and GEC (which we cannot see) electrically all should be ok.
Frank P. Newman Emerald City Inspections, LLC Dublin, GA |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 4:56 PM |
| Odd grounding question. | mnahrgang | Electrical Inspections | 2 | 8/25/09 3:04 PM |
| Question about metal Building grounding | sparksnmore | Electrical Inspections | 16 | 11/19/07 1:19 PM |
| Grounding question | cbottger | Electrical Inspections | 8 | 12/5/06 4:27 PM |