Default Grounding strap to panel

This panel as far as I can see does not have a grounding strap to protect the panel enclosure, or did I miss it?
Thanks
Attached Thumbnails
grounding-strap-panel-306-16th-ave-ne-179-small-.jpg.jpg
Views:	185
Size:	37.5 KB
ID:	30313  
Reply With Quote
Find an InterNACHI certified Hawaii Home Inspector (and anywhere else in North America)
  #2  
Old 7/25/09, 10:06 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Grounding strap to panel

That is a Square D panel that uses a green bond screw, not a strap. I can not see the area near the main lugs enough to see if this has been installed. Perhaps you could post a closeup?
Reply With Quote
  #3  
Old 7/25/09, 11:04 PM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 333
Default Re: Grounding strap to panel

Jim, you are correct about it being a square D panel. Yes there was a green bond screw across the top buss tie but I couldn't see if it made contact anywhere to the enclosure. Are you saying that this screw if installed makes this connection?
Reply With Quote
  #4  
Old 7/26/09, 7:52 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Grounding strap to panel

Quote:
Originally Posted by gwilcox View Post
Jim, you are correct about it being a square D panel. Yes there was a green bond screw across the top buss tie but I couldn't see if it made contact anywhere to the enclosure. Are you saying that this screw if installed makes this connection?
Gerald,

If there is a green screw present, it makes contact to the panel. It penetrates the neutral bar and touches the panel on contact.
Reply With Quote
  #5  
Old 7/26/09, 8:00 AM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 333
Default Re: Grounding strap to panel

Thanks for the information guys, I appreciate it.
Reply With Quote
  #6  
Old 8/1/09, 10:36 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Grounding strap to panel

Yes, That "GREEN" screw makes the contact needed within that enclosure to meet the "main bonding" requirement. Just to clarify in your original question you said it was to protect the panel......it is not their to protect the panel, it is their to provide a return path to the source in the event the panel enclosure or downstream equipment, devices or panels obtain a fault. This creates a low impedance path back to the source to facilitate the operation of an OCPD ( Overcurrent Protective Device ) and reduce the ongoing shock hazard and potential fire by tripping out the OCPD and clearing the voltage from the metal parts as well. The EGC ( Equipment Grounding Conductors ) within the circuits down stream have a more equal potential to ground under normal conditions as well during this event.



Paul W. Abernathy
Reply With Quote
  #7  
Old 8/1/09, 10:49 AM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 333
Default Re: Grounding strap to panel

Well said, Thanks Paul.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 10:00 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts