Are gounding wires from the service panel to in ground rod to be continuous or can they be spliced?

Inspected a home last night and the ground wire above the panel to the outside had a splice about 6" above the box, and I remember reading somewhere that all grounding wires were to be continuous with no splices.

Todd
Reply With Quote
  #2  
Old 3/15/07, 4:20 PM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 621
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: grounding wires

There are exceptions. The one that seems to apply in the situation as you describe it is:


The grounding electrode conductor, which runs to any convenient grounding electrode [250.64(F)], must not be spliced, except as permitted in (1) through (3):
  1. Splicing is permitted by irreversible compression-type connectors listed for grounding or by exothermic welding.
Also, if the GEC is exposed, and smaller than 8AWG, it must be protected by installing in rigid or intermediate metal conduit, rigid non-metallic, or EMT...just in case that's what you have.

Jimmy B.
Reply With Quote
  #3  
Old 3/15/07, 4:22 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: grounding wires

The GEC should be continuous (no splice or joint), however, I have seen where they have been "accepted" if they are spliced using an irreversible connector or weld.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net

Last edited by jpope; 3/15/07 at 4:26 PM..
Reply With Quote
  #4  
Old 3/15/07, 5:39 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: grounding wires

Pictorial example of an irreversible compression splice of grounding electrode conductors:

Reply With Quote
  #5  
Old 3/15/07, 6:19 PM
bandag bandag is offline
Active Poster
 
Join Date: Sep 2006
Posts: 137
Please Note: bandag is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: grounding wires

Pic is kinda big, what is that clear material on the cable?
Reply With Quote
  #6  
Old 3/15/07, 6:55 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: grounding wires

Quote:
Originally Posted by bandag
Pic is kinda big,...
But I posted it completely for free and out of willingness to be helpful, so quit your crying.

Quote:
Originally Posted by bandag
what is that clear material on the cable?
I have no idea what you're talking about. That's bare copper. Copper oxide?
Reply With Quote
  #7  
Old 3/15/07, 7:06 PM
bandag bandag is offline
Active Poster
 
Join Date: Sep 2006
Posts: 137
Please Note: bandag is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: grounding wires

On the right where the two copper wires are. what is that clear/silver stuff? Is that the irreversible connection you are talking about?
Reply With Quote
  #8  
Old 3/15/07, 7:24 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: grounding wires

Quote:
Originally Posted by bandag
On the right where the two copper wires are. what is that clear/silver stuff? Is that the irreversible connection you are talking about?
Indeed.
Reply With Quote
  #9  
Old 3/15/07, 7:35 PM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 621
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: grounding wires

Marc likes lots of detail.
Reply With Quote
  #10  
Old 3/15/07, 8:43 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: grounding wires

Try it like this next time, Marc.
Attached Thumbnails
grounding-wires-hpim0640a.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #11  
Old 3/15/07, 8:51 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: grounding wires

Quote:
Originally Posted by jpope
Try it like this next time, Marc.
As a non-member guest, the site will not permit me to attach a thumbnail.
Reply With Quote
  #12  
Old 3/15/07, 9:27 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: grounding wires

Quote:
Originally Posted by Marc D. Shunk
As a non-member guest, the site will not permit me to attach a thumbnail.
Well that's just wrong. ..

and just for clarification, that's a picture of a "tap" rather than a "splice." It appears as if the common GEC is still continuos, as it should be.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #13  
Old 3/15/07, 9:47 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: grounding wires

Quote:
Originally Posted by jpope
and just for clarification, that's a picture of a "tap" rather than a "splice." It appears as if the common GEC is still continuos, as it should be.
It's a tap and a splice, both. I made it myself.
Reply With Quote
  #14  
Old 3/16/07, 1:42 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: grounding wires

Quote:
Originally Posted by Marc D. Shunk
It's a tap and a splice, both. I made it myself.

Well, I guess I can't argue with that



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #15  
Old 3/16/07, 8:24 AM
Todd M. van Vranken Todd M. van Vranken is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Louisville, OH
Posts: 22
Default Re: grounding wires

Thank you all for your help! I knew I was right, but I just had to proof to teh "father" that I was.

Todd
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical 6 9/15/08 8:57 AM
Branch circuit grounding wires in panel Michael Martin Electrical 4 5/31/07 10:44 AM
Demystify Grounding & Bonding Class pabernathy Education 5 12/24/06 2:10 AM


All times are GMT -4. The time now is 3:37 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts