#1
|
|||
|
|||
|
Are gounding wires from the service panel to in ground rod to be continuous or can they be spliced?
Inspected a home last night and the ground wire above the panel to the outside had a splice about 6" above the box, and I remember reading somewhere that all grounding wires were to be continuous with no splices. Todd |
|
#2
|
|||
|
|||
|
Please Note:
jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
There are exceptions. The one that seems to apply in the situation as you describe it is:
The grounding electrode conductor, which runs to any convenient grounding electrode [250.64(F)], must not be spliced, except as permitted in (1) through (3):
Jimmy B. |
|
#3
|
||||
|
||||
|
The GEC should be continuous (no splice or joint), however, I have seen where they have been "accepted" if they are spliced using an irreversible connector or weld.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net Last edited by jpope; 3/15/07 at 3:26 PM.. |
|
#4
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Pictorial example of an irreversible compression splice of grounding electrode conductors:
|
|
#5
|
|||
|
|||
|
Please Note:
bandag is a non-member guest and is in no way affiliated with InterNACHI or its members.
Pic is kinda big, what is that clear material on the cable?
|
|
#6
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Quote:
|
|
#7
|
|||
|
|||
|
Please Note:
bandag is a non-member guest and is in no way affiliated with InterNACHI or its members.
On the right where the two copper wires are. what is that clear/silver stuff? Is that the irreversible connection you are talking about?
|
|
#8
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#9
|
|||
|
|||
|
Please Note:
jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Marc likes lots of detail.
|
|
#10
|
||||
|
||||
|
Try it like this next time, Marc.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#11
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#12
|
||||
|
||||
|
Quote:
and just for clarification, that's a picture of a "tap" rather than a "splice." It appears as if the common GEC is still continuos, as it should be. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#13
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#14
|
||||
|
||||
|
Quote:
Well, I guess I can't argue with that IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#15
|
|||
|
|||
|
Thank you all for your help! I knew I was right, but I just had to proof to teh "father" that I was.
Todd |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Branch circuit grounding wires in panel | Michael Martin | Electrical Inspections | 4 | 5/31/07 9:44 AM |
| Demystify Grounding & Bonding Class | pabernathy | Inspection Education & Training | 5 | 12/24/06 1:10 AM |