#1
|
||||
|
||||
|
Again, in todays inspection we found where the grounds and neutrals are sharing the same termination point. Why is this a no no? In my thinking they are sharing the same bus anyway?
Attachment 2637 "I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison www.newbeginningshomeinspection.com Last edited by nbhi; 4/11/06 at 8:45 PM.. |
|
#2
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
In the main panel they can be on the same busbar but not under the same screw. Keep the neutrals one per lug. The grounds can be up to 3, depending on the label.
|
|
#3
|
||||
|
||||
|
Greg, why not under the same lug? There are sharing the same bus. I know the neutrals have potential current.
"I have not failed, I have just found a 1000's way's that didn't work" Thomas Edison www.newbeginningshomeinspection.com |
|
#4
|
||||
|
||||
|
If two neutrals get loose that are from different legs you can get 240v across them. Remember that a light bulb will pass the voltage even when it is not on if the neutral is not connected. If your body gets in series with the loose neutral and ground the light will glow as you are being elecrocuted.
B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent 704 301-3207 |
|
#5
|
||||
|
||||
|
The best explanation I've ever seen of this is on TIJ (The Inspector's Journal) forum.
http://inspectorsjournal.com/forum/t...?TOPIC_ID=2762 See the downloadable document from Jim Katen in his reply (2nd from top). -- Erby Crofutt B4U Close Home Inspections Georgetown, Kentucky KY Lic# HI-2041 www.b4uclose.com http://www.kentuckyradon.com Kentucky Home Inspections Kentucky Home Inspectors NACHI02090301 Read my Active Rain Blog here: Erby, The Central Kentucky Home Inspector Join Active Rain HERE and I'll get some points for your participation. Please! I did ask nice! |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical | 6 | 9/15/08 8:57 AM |
| Stray Voltage can kill | rcooke | Electrical | 24 | 10/26/07 12:40 PM |
| Neutrals and Grounds | ekartal6 | Electrical | 9 | 10/8/07 12:42 PM |
| Electrician signs off 'ganged neutrals'...now what? | mgault | Electrical | 16 | 6/3/07 12:09 AM |
| Multiple grounds | gmathias | Electrical | 11 | 4/30/07 2:49 PM |