Default Handle ties on circuit breakers

Just need some clarification. Are handle ties required on these circuit breakers? For example, on the bottom left, first 3 breakers. Are these considered 2 ckt's to receps on same yoke? Just need some insight is all.
Attached Thumbnails
handle-ties-circuit-breakers-img_0012.jpeg  
Reply With Quote
  #2  
Old 11/16/06, 4:51 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Handle ties on circuit breakers

Hi Charles,

No handle ties are not required, those breakers are commonly called "mini twins" and each handle is controling a seperate circuit. You would only need ties if they were controlling one appliance as you sometimes see with 2 seperate breakers running each leg of a 240 volt circuit (AC, stoves etc)

I hope this helps

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 11/16/06, 4:52 PM
Charles Hellickson Charles Hellickson is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Colorado Springs, CO
Posts: 98
Default Re: Handle ties on circuit breakers

Thanks Gary,

This is what I thought...just needed some clarification...thank again
Chuck
Reply With Quote
  #4  
Old 11/16/06, 6:42 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Handle ties on circuit breakers

You may want to mention the recalled AFCI breakers in that panel. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 11/16/06, 7:02 PM
Charles Hellickson Charles Hellickson is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Colorado Springs, CO
Posts: 98
Default Re: Handle ties on circuit breakers

Yep, I remember that post on the recalls...Thanks for the heads up Jeff

Chuck
Reply With Quote
  #6  
Old 11/16/06, 7:04 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,657
Default Re: Handle ties on circuit breakers

http://www.cpsc.gov/cpscpub/prerel/prhtml05/05035.htmlour

Nice catch Jeff. I can tell that you are not an alarmast from your comment on the AFCI.
Reply With Quote
  #7  
Old 11/16/06, 7:05 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Handle ties on circuit breakers

Quote:
Originally Posted by dmacy
I can tell that you are not an alarmast from your comment on the AFCI.
I try not to be. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 11/16/06, 8:59 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 3,417
Send a message via ICQ to kshepard
Default Re: Handle ties on circuit breakers

Quote:
Originally Posted by jpope
You may want to mention the recalled AFCI breakers in that panel. . .
Jeff, that was a recall notice issued over 2 years ago. Do you memorize recall items or compare the breakers you see with a list?

With all the different things we have to bear in mind, how do you remember an item on a recall list from 2 years ago?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
InterNACHI Director of International Development
Director of Green Building

EXPERT WITNESS SERVICE
Conventional and Log homes

(303) 717-8940
Reply With Quote
  #9  
Old 11/16/06, 9:19 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Handle ties on circuit breakers

Quote:
Originally Posted by kshepard
With all the different things we have to bear in mind, how do you remember an item on a recall list from 2 years ago?
I have been dealing with these since their recall. These were installed in thousands of homes in my area, and most of them have not been changed out. That is, except for those homes where I have called them out.

Recently, one builder finally took the high road and replaced the AFCI breakers in over 750 homes, in a tract where I called it out on more than 20 homes.

The replacement breakers have a green test button.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 11/16/06, 11:08 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Handle ties on circuit breakers

How have the replacements been going. Is SqD living up to the promise to cover the labor?
Reply With Quote
  #11  
Old 11/16/06, 11:23 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Handle ties on circuit breakers

I was under the impression not all "Blue Button" SQ-D AFCI's are in the recall, I would have to search for the list I saved that Paul posted though.

Are they?
Reply With Quote
  #12  
Old 11/16/06, 11:25 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Handle ties on circuit breakers

Quote:
Originally Posted by Greg Fretwell
How have the replacements been going. Is SqD living up to the promise to cover the labor?
That, I cannot answer. I really don't know.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 11/17/06, 5:18 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Handle ties on circuit breakers

Whew..Back from Atlanta......figured I would chime in...

Be aware that on those tandoms in the panel shown...that none of them go to a multiwire circuit and share a neutral ( grounded ) conductor.....as in doing so would put BOTH loads on the same LINE in the panel and compounding the load on the grounded conductor of that circuit.

The only reason I bring this up is your statement on (2) circuits on the same YOKE............would generally constitute someone trying to do a Multiwire circuit in most cases....and tandoms should NOT be used for this application.



Paul W. Abernathy
Reply With Quote
  #14  
Old 5/4/07, 6:41 AM
Timothy J. Gardner Timothy J. Gardner is offline
InterNACHI Member
 
Join Date: Sep 2003
Location: Moneta, VA
Posts: 272
Default Re: Handle ties on circuit breakers

Paul,

Good info - I just saw one of the exact situations you mention .

handle-ties-circuit-breakers-improper-tandem-use.jpg

This unlabeled tandem circuit breaker feeds a three wire w/ground romex cable. Either it is an improper multi-wire circuit or improper 240 v circuit. Don't know which - don't care - it needs attention by a licensed electrician.

tg
Reply With Quote
  #15  
Old 5/4/07, 10:13 PM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Handle ties on circuit breakers

What is all the dirt/dust on the circuit breakers at the left side of the panel all about?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Can an AFCI offer GFCI protection gbeaumont Electrical Inspections 19 7/6/06 11:45 PM


All times are GMT -4. The time now is 3:11 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts