Any problem with a hard wired dryer. The ground is obvious.
Thanks, Scott Falvey Clear View Home Inspections, LLC Newbury, NH NACHI#05051292 www.clearviewhomeinspectionsllc.com |
|
#2
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Well, that's only #12, and you need #10 for any domestic clothes dryer that I've ever seen. It can be legal to hard wire a clothes dryer, but it needs a disconnecting means within sight of the appliance.
You've pointed out the goofy way the ground is terminated, but that 3/4" romex connector is probably not rated for the 12-3 that's running through it. |
|
#3
|
|||
|
|||
|
Thanks Mark, that is a good find. This house is full of things like this. Check out other posts at the plumbing section.
Thanks, Scott Falvey Clear View Home Inspections, LLC Newbury, NH NACHI#05051292 www.clearviewhomeinspectionsllc.com |
|
#4
|
|||
|
|||
|
If one chooses to hard wire the dryer, I believe it should be in conduit.
|
|
#5
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
The violation is the lack of a disconnect, and in your case the undersized wire and the use of Romex (that gets debated from time to time).
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Dryer sheets potential hazard | badair | Miscellaneous Discussion for Inspectors | 15 | 7/9/11 2:39 PM |
| Flex vs. hard gas hookup to dryer | Nathan W. Swilling | Plumbing Inspections | 18 | 4/2/08 10:54 AM |
| What is a 'condenser' dryer ?? | rcooke | Canadian Inspectors | 9 | 9/9/07 7:02 PM |
| direct wired dryer | msaxton | Electrical Inspections | 5 | 4/3/06 11:34 PM |