House is approx. 1997, has hard wired smokes, however when tested, they do not all sound if 1 is tested.
My understanding is they are all hard wired so they will sound togather throughout the house. Is this correct? They did all sound individually, one was not installed (removed) would this keep the others from sounding in sync.? Thanks, Scott Falvey Clear View Home Inspections, LLC Newbury, NH NACHI#05051292 www.clearviewhomeinspectionsllc.com |
|
#2
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Hard wiring them does not make them all sound at once. Interconnecting them does. If they are wired with 3 conductors and interconnected, they will all sound at once. If they are only wired with 2 conductors, they cannot be interconnected.
|
|
#3
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Given the age of the house they certainly should be interconnected.
|
|
#4
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Sounds to me like they were wired with "2-wire" and not interconnected. Why? Who knows??? |
![]() |